Bending Radius for uPVC 6" Cable Conduits

06/05/2020 8:49 AM

We are using uPVC 6" Conduits for all cable entries within multi-function buildings in our project. Request for advise for the minimum bending radius for this 6" size uPVC Cable Conduit as per reputed International Standard.

Is there any reputable international standard(s) for 6" which allows 0.91meter bending radius? (These conduits shall also be used for FOC Entry).

Register to Reply
Pathfinder Tags: Bending Radius
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.

Good Answers:

These comments received enough positive votes to make them "good answers".

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Guru

Join Date: Mar 2007
Location: by the beach in Florida
Posts: 33392
Good Answers: 1817
#1

Re: Bending Radius for uPVC 6" Cable Conduits

06/05/2020 12:12 PM
__________________
All living things seek to control their own destiny....this is the purpose of life
Register to Reply Score 1 for Good Answer
Associate

Join Date: Sep 2009
Location: United Arab Emirates, Abu Dhabi
Posts: 50
#2
In reply to #1

Re: Bending Radius for uPVC 6" Cable Conduits

06/05/2020 2:38 PM

much obliged for the gracious guidance, if i can request for uPVC rather than Rigid PVC, this would be wonderful please.

Register to Reply
Guru

Join Date: Mar 2007
Location: by the beach in Florida
Posts: 33392
Good Answers: 1817
#3
In reply to #2

Re: Bending Radius for uPVC 6" Cable Conduits

06/05/2020 2:53 PM
__________________
All living things seek to control their own destiny....this is the purpose of life
Register to Reply Score 1 for Good Answer
Guru

Join Date: May 2018
Location: Under the spreading Bunya Trees, South Burnett, Queensland, Australia
Posts: 807
Good Answers: 65
#4

Re: Bending Radius for uPVC 6" Cable Conduits

06/06/2020 3:58 AM

Are you using uPVC which here in Australia means drain pipe?

Is it allowable to use uPVC instead of electrical orange conduit in your country for buried in ground cable entries?

I have found for 150mm conduit it is far simpler to use preformed bends rather than try to make a bend in the conduit for it always wants to collapse unless it is over a form or packed with sand and heated and still the end result is no pleasing and if using a bending spring you will have a tough time trying to remove it.

There are preformed bends for uPVC which will make your job easier.

__________________
Hare today, goon tomorrow!
Register to Reply
Guru

Join Date: Oct 2006
Location: 44.56024"N 15.307971E
Posts: 8277
Good Answers: 270
#5
In reply to #4

Re: Bending Radius for uPVC 6" Cable Conduits

06/06/2020 6:18 AM

There are many companies that make benders for all varieties of PVC conduit and pipe.

Some use compressed air to maintain the internal diameter while bending and cooling.

5X the diameter of the conduit is a safe rule-of-thumb number to work with.

It is less for small conduit,but in the 6 inch diameter, 5X is pretty close.

Remember,the sharper the bend,the harder it is to pull wire through the conduit.

When pulling around multiple turns,these friction points really add up.

The maximum number of 90 degree bends is 4,If there are no other offsets or bends in the pipe.

Even 1 minor offset reduces the number to 3.

Total degrees of all angles,including offsets cannot exceed 360 degrees.

The pre-made Elbows come in both a standard,and long Ell version.

I always select the long Ell if possible.

These are cheaper for small jobs,but large jobs may justify buying a bender and training users.

Do not buy a cheap bender if you decide to buy one.

Do your home work,read reviews,and exercise due diligence when making your purchase.

The above dimension are referenced to the NEC handbook,used in most USA states.

International standards may differ.

Your local inspector or AHJ is your best point of contact on these matters.

Good luck.

__________________
"A man never stands so tall as when he stoops to help a child." "Never argue with a stupid person.They will drag you down to their level and beat you with experience" "To create an apple pie from scratch, first you must create a universe"
Register to Reply
Associate

Join Date: Sep 2009
Location: United Arab Emirates, Abu Dhabi
Posts: 50
#6
In reply to #5

Re: Bending Radius for uPVC 6" Cable Conduits

06/06/2020 7:55 AM

May i request your opinion as to why there is difference between TIA and NEC in Rigid PVC conduit bending radius [90 degree], as per guideline from TIA it seems it asks for 10 times the internal diameter whereas lets say for 6 inch size for NEC for Rigid PVC it requires 762 and 914.4mm.

is there any standard which is as same as NEC for the conduit bend (rigid PVC) from the following:

ITU-T

IEEE

IEC

BICSI

ETSI

NEMA

EIA

TIA

SEC (Security Directives for Industrial Facilities )

Register to Reply
Guru

Join Date: Mar 2007
Location: by the beach in Florida
Posts: 33392
Good Answers: 1817
#7
In reply to #6

Re: Bending Radius for uPVC 6" Cable Conduits

06/06/2020 9:57 AM

Well there might be a difference in the cable type...for a large heavy cable the bend would not likely be the minimum...The best thing is to acquire copies of all the relevant codes you will be dealing with, and read them all for the various applications you are using...There might also be variations for lubricated cable and non-lubricated pulls, temperature range, ground type, elevated or buried etc etc....

__________________
All living things seek to control their own destiny....this is the purpose of life
Register to Reply Score 1 for Good Answer
Guru

Join Date: Oct 2006
Location: 44.56024"N 15.307971E
Posts: 8277
Good Answers: 270
#8
In reply to #6

Re: Bending Radius for uPVC 6" Cable Conduits

06/06/2020 10:35 AM

I am only familiar with the NEC,but it would seem,in my opinion,the other codes favor a smoother bend to reduce pulling stress on the conductors and minimize deforming of the internal diameter of the bend.

When pulling certain signal wires,and fiber,NO bends are allowed.

Turns must be made within a junction box only and the dimensions of these boxes are specified to give adequate room for safe low stress turns.

Where are you located? Local codes can also differ from national codes.

ALWAYS check with the AHJ!

__________________
"A man never stands so tall as when he stoops to help a child." "Never argue with a stupid person.They will drag you down to their level and beat you with experience" "To create an apple pie from scratch, first you must create a universe"
Register to Reply Score 1 for Good Answer
2
Guru

Join Date: Dec 2009
Location: Land of Shining Waters
Posts: 916
Good Answers: 35
#9

Re: Bending Radius for uPVC 6" Cable Conduits

06/06/2020 10:42 AM

My small contribution: The Canadian Electrical Code (1994) Rule 12-922 states that the radius of the curve of the inner edge of the bends (for Rigid PVC) shall be at least 6 times the internal diameter (increased to 10 times when lead-sheathed cable is to be pulled). Field bends are permitted if equipment designed for the purpose is used.

__________________
It is easier to let the cat out of the bag than to put the cat back in the bag.
Register to Reply Good Answer (Score 2)
Associate

Join Date: Sep 2009
Location: United Arab Emirates, Abu Dhabi
Posts: 50
#10

Re: Bending Radius for uPVC 6" Cable Conduits

06/06/2020 3:17 PM

Can anyone advise if there is any guideline about Rigid PVC (UPVC) radius in BS EN 1401-1? Just want to compare the difference with NEC.

Our Project has currently selected 6 inch PVC-U conduit (internal dia 150mm) which has 12 sub-conduits (1inch each, external dia 31mm). So the fear is that the bending radius as per NEC would not be enough. The FOC might get damaged.

FOC Datasheets are as following:

Register to Reply
Guru

Join Date: Oct 2006
Location: 44.56024"N 15.307971E
Posts: 8277
Good Answers: 270
#11
In reply to #10

Re: Bending Radius for uPVC 6" Cable Conduits

06/06/2020 3:52 PM

I don't think you will find a universally accepted standard that is accepted by everyone.

That is because everyone has their opinion.

And you know what they say about opinions.

The ones that should matter to YOU,are the ones in the local area where you intend to do the work,and the cable manufacturers specification as it applies to bend radius,etc.

Put on your thinking cap,dig deep into the specifications,and derive an answer that fits your needs.

You have not told us where you are located or provided any other information that was requested.

You have been advised several times to consult with the AHJ,so that is my final answer in that regard.

I cannot help nor respect someone that will not help themselves.

__________________
"A man never stands so tall as when he stoops to help a child." "Never argue with a stupid person.They will drag you down to their level and beat you with experience" "To create an apple pie from scratch, first you must create a universe"
Register to Reply Score 1 for Off Topic
Guru
Popular Science - Weaponology - New Member Engineering Fields - Engineering Physics - New Member Engineering Fields - Nuclear Engineering - New Member

Join Date: Dec 2007
Location: No. VA, USA (No, it does NOTu mean "won't go"!)
Posts: 1796
Good Answers: 75
#12

Re: Bending Radius for uPVC 6" Cable Conduits

06/07/2020 7:32 AM

I think this falls in parallel with "we don't do college homework". I realize in the USA we may do things differently, but I was a project engineer for 41 years, and my boss would never have let me ask someone else to do the homework for me. I can ask questions, but it still came down to having to do local analysis, and then demonstrate that I had done that local analysis so that the questions asked by the US government, the US military, etc. Our primary customers) had cogent answers.

__________________
Been away a while. Miss all my old friends. Some of you I KNOW are still around. Where are the rest?
Register to Reply Off Topic (Score 5)
Associate

Join Date: Sep 2009
Location: United Arab Emirates, Abu Dhabi
Posts: 50
#13

Re: Bending Radius for uPVC 6" Cable Conduits

06/07/2020 9:12 PM

Gentlemen,

For those who are asking me to do local analysis and where is the project from etc etc, kindly note as following:

The project is a port project in Saudi Arabia and has some standards in current specification which flowed in from FEED. The standards are:

ITU-T

IEEE

IEC

BICSI

ETSI

NEMA

EIA

TIA

SEC (Security Directives for Industrial Facilities )

The only local code applicable here shall be SBC (Saudi Building Code) if any, that is not much helpful and the Client is advising to select one of the above standard.

I have shared the selected FOC Datasheet, i have also shared that detailed query that Our Project has currently selected 6 inch PVC-U conduit (internal dia 150mm) which has 12 sub-conduits (1inch each, external dia 31mm). So the fear is that the bending radius as per NEC would not be enough. The FOC might get damaged.

Due to design time / construction schedule issue, we do not want to change the 914mm radius of these conduits (90 degrees) which have already been selected and modeled, however we do not want a scenario where the FOC might get damaged as well.

so to sum up, will NEC bending radius be enough? is there any NEMA/TIA or any standard requested above allows the same bending radius for 6" UPVC conduit since NEMA/TIA as compared to NEC are on higher side (1.22-1.55).

Register to Reply
Guru
United Kingdom - Member - Indeterminate Engineering Fields - Control Engineering - New Member

Join Date: Jan 2007
Location: In the bothy, 7 chains down the line from Dodman's Lane level crossing, in the nation formerly known as Great Britain. Kettle's on.
Posts: 32175
Good Answers: 839
#14

Re: Bending Radius for uPVC 6" Cable Conduits

06/08/2020 2:06 AM

Is there some reason why this information cannot be had from the <...conduit...> supplier using the telephone?

__________________
"Did you get my e-mail?" - "The biggest problem in communication is the illusion that it has taken place" - George Bernard Shaw, 1856
Register to Reply
Associate

Join Date: Sep 2009
Location: United Arab Emirates, Abu Dhabi
Posts: 50
#15
In reply to #14

Re: Bending Radius for uPVC 6" Cable Conduits

06/08/2020 2:23 AM

We have approached the conduit suppliers but the reply i feel is bit shaky, vendor is mentioning Radius as per NEMA TC9 EB for 150mm conduit size, however i cannot find these radius in NEMA TC9:

The reply from supplier is as following:

  1. Since the size specified in your project is 150MM it is better to opt NEMA standards as there is no specific standard for this particular size in European-International standards unless the Drainage specification is used and I believe later on there will be confusion with standards.
  2. Accordingly, we recommend to use Size 6”/150MM DUCT PIPES manufactured according to NEMA TC8 EB-35 with minimum Modulus of Elasticity of 500,000 Psi. (35 stands for the stiffness of Pipes - 35 PSI)
  3. With regard to BENDS, we do have facility to fabricate BENDS from DUCTS with minimum Radius of 24”(610MM) to any RADIUS….30” (760MM), 36” (916MM) and so on. Larger Radius like 3 Mtr and above (mostly used in Communication Duct Banks) shall be fabricated in Segments.
  4. Regarding PEC DUCTS, since your required size in 150MM we cannot propose the same in PECD; currently we do produce PECD with built-in subducts of 110MM OD.

Register to Reply
Guru
United Kingdom - Member - Indeterminate Engineering Fields - Control Engineering - New Member

Join Date: Jan 2007
Location: In the bothy, 7 chains down the line from Dodman's Lane level crossing, in the nation formerly known as Great Britain. Kettle's on.
Posts: 32175
Good Answers: 839
#16

Re: Bending Radius for uPVC 6" Cable Conduits

06/09/2020 5:19 AM

There is a difference between the <...bending radius...> and the bend radius, which may be where some confusion lays.

  • The <...bending radius...> is that which is introduced by the Installer, by deforming the material out of straight, at site.
  • The bend radius is that produced by off-the shelf curved parts that fit the straight parts as part of the manufacturer's product range.

Both may be obtained by discussion with the manufacturer. A telephone discussion should sort it out.

<unsubscribes>

__________________
"Did you get my e-mail?" - "The biggest problem in communication is the illusion that it has taken place" - George Bernard Shaw, 1856
Register to Reply
Anonymous Poster #1
#17

Re: Bending Radius for uPVC 6" Cable Conduits

06/09/2020 5:21 AM
Register to Reply
Guru

Join Date: Oct 2006
Location: 44.56024"N 15.307971E
Posts: 8277
Good Answers: 270
#18

Re: Bending Radius for uPVC 6" Cable Conduits

06/09/2020 8:15 AM

Here is a good reference for your questions that compare EIS with NEC for conduit bend radius.

Everything you wanted to know but were reluctant to ask.

https://www.lanshack.com/DesigningConduitRuns.aspx#

__________________
"A man never stands so tall as when he stoops to help a child." "Never argue with a stupid person.They will drag you down to their level and beat you with experience" "To create an apple pie from scratch, first you must create a universe"
Register to Reply Score 1 for Good Answer
Associate

Join Date: Sep 2009
Location: United Arab Emirates, Abu Dhabi
Posts: 50
#19
In reply to #18

Re: Bending Radius for uPVC 6" Cable Conduits

06/09/2020 10:57 AM

Much obliged! This is a fantastic article and wonderful insight. Can I request, if you have it, any knowledge of an online calculator for Pulling Tension Calculation for the FOC? Our client wants this calculation to ensure FOC will survive during construction.

Register to Reply
Guru
United Kingdom - Member - Indeterminate Engineering Fields - Control Engineering - New Member

Join Date: Jan 2007
Location: In the bothy, 7 chains down the line from Dodman's Lane level crossing, in the nation formerly known as Great Britain. Kettle's on.
Posts: 32175
Good Answers: 839
#20
In reply to #19

Re: Bending Radius for uPVC 6" Cable Conduits

06/11/2020 5:12 AM

It's a bit overkill. The final testing, that of verifying are all signal paths operating correctly, ought to be sufficient.

Sounds like there is a Client with both a Gantt Chart and too much time on their hands...

__________________
"Did you get my e-mail?" - "The biggest problem in communication is the illusion that it has taken place" - George Bernard Shaw, 1856
Register to Reply
Guru

Join Date: Oct 2006
Location: 44.56024"N 15.307971E
Posts: 8277
Good Answers: 270
#24
In reply to #19

Re: Bending Radius for uPVC 6" Cable Conduits

06/25/2020 9:38 AM

The maximum allowable pulling tension on fiber cable can vary and is dependent on the cable construction. The maximum tension for a particular cable can be found on the cable spec sheet.

Here is a link to calculate pulling tension:https://www.econline.com/doc/calculating-cable-pulling-tensions-0001

Here is a guide for installing FO cable that may be useful:

https://www.thefoa.org/tech/ref/install/installcbl.html

Lots of information and guidance,caveats,etc.here

Good luck.(But remember, luck tends to favor the prepared mind)

__________________
"A man never stands so tall as when he stoops to help a child." "Never argue with a stupid person.They will drag you down to their level and beat you with experience" "To create an apple pie from scratch, first you must create a universe"
Register to Reply
Anonymous Poster #1
#21

Re: Bending Radius for uPVC 6" Cable Conduits

06/11/2020 7:25 AM
Register to Reply
Guru
Technical Fields - Technical Writing - New Member Engineering Fields - Piping Design Engineering - New Member

Join Date: May 2009
Location: Richland, WA, USA
Posts: 21017
Good Answers: 795
#22

Re: Bending Radius for uPVC 6" Cable Conduits

06/11/2020 10:56 PM

The bend radius of the outer 6" (150mm) conduit may not be of primary interest. Instead, the bend radius of the internal 1" (25mm) conduits will matter more.

Even with the minimum 24" radius (4D) bends for the 6" conduit, this will be 24D for the 1" conduits. This may be well more than ample.

Other things come into play as well, such as total degrees of bend in a run, total length of run, and orientation of parts of a run. For instance, a vertical run will have very little sidewall friction.

__________________
In vino veritas; in cervisia carmen; in aqua E. coli.
Register to Reply Score 1 for Good Answer
Associate

Join Date: Sep 2009
Location: United Arab Emirates, Abu Dhabi
Posts: 50
#23
In reply to #22

Re: Bending Radius for uPVC 6" Cable Conduits

06/25/2020 6:03 AM

Excellent point for the 1" conduit. Is there any software or calculation sheet for FOC where this can be checked?

Register to Reply
Anonymous Poster #1
#25

Re: Bending Radius for uPVC 6" Cable Conduits

07/08/2020 3:33 AM
Register to Reply
Anonymous Poster #2
#26

Re: Bending Radius for uPVC 6" Cable Conduits

09/12/2020 10:54 PM

Hi,

normally for pipe sleeve, we usually installed long bend to ease for pulling and also to comply the cable bending requirement..

Rgds,

Register to Reply Off Topic (Score 5)
Register to Reply 26 comments

Good Answers:

These comments received enough positive votes to make them "good answers".

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Copy to Clipboard

Users who posted comments:

Anonymous Poster (4); canadianslidewinder (1); HiTekRedNek (5); micahd02 (1); PWSlack (3); SolarEagle (3); Stef (1); Tornado (1); Usman Nazar Rathore (7)