how can i convert 10KA/1S to ??/3S
Re: short circuit current
08/19/2020 2:41 AM
Good Answers: 131
Re: Short Circuit Current
08/19/2020 8:06 AM
Is this for the short-time or peak withstand current for a HV switch? IEEE Std C37.30.1 (IEEE Standard Requirements for AC High-Voltage Air Switches Rated above 1000V) gives some info in its Tables, with a reference to "allowable I2t variations" in its section 8.3.5.1. You should take a look at that. So it may be that you can calculate an equivalent using I2t.
08/19/2020 9:22 AM
Here's a rough estimate: Power is proportional to current squared, and Energy is equal to power x time, E = I2Rt. For equal amount of energy, if time is multiplied by 3, I2 would be divided by 3, or I would be divided by sqrt(3).
Using this logic, 10KA/1S ~ 5.77KA/3S.
This assumes that the time is short enough that not much heat can escape.
Good Answers: 131
08/20/2020 9:33 AM
You did the math that I was leaving for the OP. That's what I was getting at. Thanks.
08/21/2020 1:34 AM
Thanks PeterT
08/21/2020 11:58 PM
thanks Rixter
08/21/2020 2:09 PM
Using basic arithmetic.
08/31/2020 7:47 AM
30kA