Dear colleagues,
In our refinery, we have 04 nos of 30kW 415V motor for fan application driven through ABB VFD ACS800. As per process requirement, all 4 motors were running in 92 RPM approx. Current in display is 17.22A which is 33% of FLC!.torque was only 1.83% and Power is also 0.07% only. Whereas incomer side of VFD panel reads only 3A approx. when motor is in full speed 1500 rpm, it draws 25A, torque was 25%.
When we checked with ABB, they say that the motor is taking the magnetization current of the motor during no load condition. The magnetizing current is essentially constant, current consist motor magnetization part with stator inductor and drive circulating due to DTC mode, the magnetizing current can be as low as 20% to 40 % of the rated full load current of the motor . due to Voltage source inverter the output current will take from drive inverter side so it will not match until the full speed and load of the motor.
I wonder whether the motor draws this much current for magnetizing alone? Why the same is not appearing or adding to load current when motor is in full rated speed.
Please support
Cheers,
Vijay