VFD Output Current is More Than Input Current

11/10/2020 3:00 AM

Dear colleagues,

In our refinery, we have 04 nos of 30kW 415V motor for fan application driven through ABB VFD ACS800. As per process requirement, all 4 motors were running in 92 RPM approx. Current in display is 17.22A which is 33% of FLC!.torque was only 1.83% and Power is also 0.07% only. Whereas incomer side of VFD panel reads only 3A approx. when motor is in full speed 1500 rpm, it draws 25A, torque was 25%.

When we checked with ABB, they say that the motor is taking the magnetization current of the motor during no load condition. The magnetizing current is essentially constant, current consist motor magnetization part with stator inductor and drive circulating due to DTC mode, the magnetizing current can be as low as 20% to 40 % of the rated full load current of the motor . due to Voltage source inverter the output current will take from drive inverter side so it will not match until the full speed and load of the motor.

I wonder whether the motor draws this much current for magnetizing alone? Why the same is not appearing or adding to load current when motor is in full rated speed.

Please support

Cheers,

Vijay

__________________
You don't understand anything until you learn it more than one way.
Register to Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Guru

Join Date: Mar 2007
Location: by the beach in Florida
Posts: 33392
Good Answers: 1817
#1

Re: VFD output current is more than input current

11/10/2020 3:17 AM

At this slow speed you are running the motor in a very inefficient manner...

https://av8rdas.wordpress.com/2010/12/18/variable-frequence-drive-system-efficiency/

__________________
All living things seek to control their own destiny....this is the purpose of life
Register to Reply
Commentator

Join Date: Jan 2011
Location: India
Posts: 98
Good Answers: 2
#7
In reply to #1

Re: VFD output current is more than input current

11/10/2020 11:35 PM

I am concerned about the motor heating, not the efficiency sir.

__________________
You don't understand anything until you learn it more than one way.
Register to Reply
Guru

Join Date: Mar 2007
Location: by the beach in Florida
Posts: 33392
Good Answers: 1817
#8
In reply to #7

Re: VFD output current is more than input current

11/10/2020 11:50 PM

This is what leads to heating and motor failure...the motor is designed to run at minimum 50% load...Why do you run the motors at such a low speed? If this is all the ventilation you require, your motors are grossly oversized, or not designed for this type application...

__________________
All living things seek to control their own destiny....this is the purpose of life
Register to Reply
Commentator

Join Date: Jan 2011
Location: India
Posts: 98
Good Answers: 2
#11
In reply to #8

Re: VFD output current is more than input current

11/11/2020 6:25 AM

It is designed for running between 0-1500 rpm as per process requirement. We also have thermistor protection to cut off power supply from vfd to motor in case of winding temp is high

__________________
You don't understand anything until you learn it more than one way.
Register to Reply
Guru

Join Date: Mar 2007
Location: by the beach in Florida
Posts: 33392
Good Answers: 1817
#12
In reply to #11

Re: VFD output current is more than input current

11/11/2020 2:57 PM
__________________
All living things seek to control their own destiny....this is the purpose of life
Register to Reply
Guru

Join Date: Jul 2016
Posts: 1367
Good Answers: 105
#10
In reply to #7

Re: VFD output current is more than input current

11/11/2020 12:31 AM

If you have your ACS800 programmed properly, the motor will not overheat, nor will the life of the equipment be shortened. This is especially applicable to variable torque loads like your fans. The winding excitation is adjusted to the speed of the rotor, so you do not generate more heat than the motor was designed to tolerate. If you have some poorly built motors, perhaps operation below 10% rated speed might be moderately risky, especially if you operate right at the motor rated ambient temperature, usually 40C.

Register to Reply
Guru

Join Date: Jul 2007
Location: Commissariat de Police, Nouvions, occupied France, 1942.
Posts: 2599
Good Answers: 77
#13
In reply to #7

Re: VFD output current is more than input current

11/11/2020 3:16 PM

Your motor is heating partly because of the current flowing through the windings, which is less than the full load current anyway, and the fact that the fan is running slowly.

Why on earth you would want to do what you’re doing is a mystery to me, Mildred.

__________________
Good moaning!
Register to Reply
Guru
United Kingdom - Member - Indeterminate Engineering Fields - Control Engineering - New Member

Join Date: Jan 2007
Location: In the bothy, 7 chains down the line from Dodman's Lane level crossing, in the nation formerly known as Great Britain. Kettle's on.
Posts: 32175
Good Answers: 839
#2

Re: VFD output current is more than input current

11/10/2020 3:19 AM

The power drawn by a fan is proportional to something like the cube of the tip speed.

It appears from here that the inverter is doing a proper job. When a motor is taking little-to-no mechanical load it is effectively a coil of wire as far as the supply is concerned; one would expect a lot of current out-of-phase with the applied voltage in such circumstances, and out-of-phase doesn't appear on the motor shaft. When it is at full load a lot more current is drawn, this time in closer phase to the applied voltage.

__________________
"Did you get my e-mail?" - "The biggest problem in communication is the illusion that it has taken place" - George Bernard Shaw, 1856
Register to Reply Score 1 for Good Answer
Commentator

Join Date: Jan 2011
Location: India
Posts: 98
Good Answers: 2
#6
In reply to #2

Re: VFD output current is more than input current

11/10/2020 11:35 PM

Magnetizing current and no load current of induction motor is same? No load current is calculated at rated voltage and speed , i guess. In this case, current seems to be near no load current in low voltage, low speed.

__________________
You don't understand anything until you learn it more than one way.
Register to Reply
Guru

Join Date: Jul 2016
Posts: 1367
Good Answers: 105
#9
In reply to #6

Re: VFD output current is more than input current

11/11/2020 12:21 AM

No load current includes some real (mechanical) power components, bearing friction, I2R heat losses of the windings, windage of the rotor, and the motor cooling fan air movement power.

The bulk of the amperes observed will be due to the reactive power, the magnetizing current, when compared to total no load amperes.

Register to Reply
Guru

Join Date: Jul 2007
Location: Commissariat de Police, Nouvions, occupied France, 1942.
Posts: 2599
Good Answers: 77
#14
In reply to #6

Re: VFD output current is more than input current

11/11/2020 3:21 PM

That’s because at low speed the thing isn’t doing any work.

__________________
Good moaning!
Register to Reply
Guru
United Kingdom - Member - Indeterminate Engineering Fields - Control Engineering - New Member

Join Date: Jan 2007
Location: In the bothy, 7 chains down the line from Dodman's Lane level crossing, in the nation formerly known as Great Britain. Kettle's on.
Posts: 32175
Good Answers: 839
#3

Re: VFD Output Current is More Than Input Current

11/10/2020 9:38 AM

At <...92rpm...> the shaft would need only 6-10W to turn it. Try turning it by hand at this speed, obviously with the motor isolated from the supply first; it should go easily.

In any case, the motors are oversized for this job by a factor of between 2 and 3.

__________________
"Did you get my e-mail?" - "The biggest problem in communication is the illusion that it has taken place" - George Bernard Shaw, 1856
Register to Reply
Guru

Join Date: Jul 2016
Posts: 1367
Good Answers: 105
#4

Re: VFD Output Current is More Than Input Current

11/10/2020 11:28 PM

The actual real power required by the motor is very low, and the input power to the inverter will be very close to the real power, since many of these inverters present a 0.95 power factor to the supply.

The magnetizing current required by the motor can be supplied by the input capacitors in the inverter supply. The power factor of your lightly loaded motor is likely around 0.55, so you measure lots of amperes that, just like with power factor correction capacitors, can be sourced independent of the supply mains.

You could actually check the running power factor of the motor, assuming your input amperes are probably about 0.95.

I admit I’ve never actually checked the input amperes against output amperes, with some 70 or 80 PWM drives install & operate, so this was an illuminating discussion.

Register to Reply Score 1 for Good Answer
Power-User

Join Date: Feb 2020
Posts: 482
Good Answers: 7
#5

Re: VFD Output Current is More Than Input Current

11/10/2020 11:31 PM

Reconfigure the intake and output fan manifolds.....cycle one motor at a time at higher load. This also gives you longevity and redundancy.

__________________
Light is only half of what you think it is.
Register to Reply
Guru

Join Date: Jul 2007
Location: Commissariat de Police, Nouvions, occupied France, 1942.
Posts: 2599
Good Answers: 77
#15
In reply to #5

Re: VFD Output Current is More Than Input Current

11/11/2020 3:23 PM

That assumes that reverse flow through parallel fans can be prevented somehow.

__________________
Good moaning!
Register to Reply Score 1 for Good Answer
Guru

Join Date: Mar 2007
Location: by the beach in Florida
Posts: 33392
Good Answers: 1817
#16

Re: VFD Output Current is More Than Input Current

11/11/2020 11:09 PM

You must be getting some resonance that is inflating the voltage with ghost voltage...

__________________
All living things seek to control their own destiny....this is the purpose of life
Register to Reply
Guru
United Kingdom - Member - Indeterminate Engineering Fields - Control Engineering - New Member

Join Date: Jan 2007
Location: In the bothy, 7 chains down the line from Dodman's Lane level crossing, in the nation formerly known as Great Britain. Kettle's on.
Posts: 32175
Good Answers: 839
#17
In reply to #16

Re: VFD Output Current is More Than Input Current

11/12/2020 3:36 AM

__________________
"Did you get my e-mail?" - "The biggest problem in communication is the illusion that it has taken place" - George Bernard Shaw, 1856
Register to Reply Score 1 for Good Answer
Guru
Technical Fields - Technical Writing - New Member Engineering Fields - Piping Design Engineering - New Member

Join Date: May 2009
Location: Richland, WA, USA
Posts: 21017
Good Answers: 795
#18

Re: VFD Output Current is More Than Input Current

11/12/2020 4:31 AM

In many VFD apps, the output voltage is proportional to the output frequency. Thus lower frequency ==> lower voltage ==> higher current.

Has there been any problem with overheated motors?

__________________
In vino veritas; in cervisia carmen; in aqua E. coli.
Register to Reply
Guru
United Kingdom - Member - Indeterminate Engineering Fields - Control Engineering - New Member

Join Date: Jan 2007
Location: In the bothy, 7 chains down the line from Dodman's Lane level crossing, in the nation formerly known as Great Britain. Kettle's on.
Posts: 32175
Good Answers: 839
#19

Re: VFD Output Current is More Than Input Current

01/23/2024 9:59 AM

As well as modulating speed, the <...VFD [variable frequency drive]...> will modulate voltage. If at the running conditions the motor is drawing very little load, then the current in the supply cable to it could under some circumstances be higher than the current drawn by the <...VFD...>. It would appear that in this condition, the current is way out of phase with the voltage waveform, indicating magnetising current.

The <...fan application...> is lightly loaded. It might be worth turning it off.

__________________
"Did you get my e-mail?" - "The biggest problem in communication is the illusion that it has taken place" - George Bernard Shaw, 1856
Register to Reply
Guru
United States - Member - New Member Engineering Fields - Power Engineering - New Member

Join Date: Sep 2006
Location: California, USA, where the Godless live next door to God.
Posts: 4665
Good Answers: 804
#20

Re: VFD Output Current is More Than Input Current

01/29/2024 12:52 PM

Current on the motor side of the inverter is inclusive of the motor reactive current, i.e. the motor power factor is very low, probably as low as .2, so most of the current read by the drive output sensors is reactive. On the line side, the power factor remains at .95 irrespective of what is going on at the motor, so the current that you read is representative of the real power being consumed in by load and motor.

__________________
** All I every really wanted to be, was... A LUMBERJACK!.**
Register to Reply Score 1 for Good Answer
Register to Reply 20 comments

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Copy to Clipboard

Users who posted comments:

Crabtree (3); Haymaker (1); JRaef (1); PWSlack (4); rwilliams (3); SolarEagle (4); Tornado (1); vijaymail_electrical (3)

Previous in Forum: Motor Trip Class   Next in Forum: Insulation Monitoring Device for DC Fast Charging Station

Advertisement