Insulation Monitoring Device for DC Fast Charging Station

11/11/2020 5:11 AM

Can Anyone help me out here?

For DC Fast Charging Stations, is it Mandatory to Include a Insulation Monitoring Device on the Charge Scheme?

Is there any Mandatory Standards? or is it only for DC unearthed System?

Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.
Guru

Join Date: Mar 2007
Location: by the beach in Florida
Posts: 33392
Good Answers: 1817
#1

Re: Insulation Monitoring Device for DC Fast Charging Station

11/11/2020 5:48 AM

It seems like it's still pretty much the wild west out there as far as different standards go, what we need is one universal standard to simplify the process of slow charge vs different levels of fast charging protocols and design...so I would say you have to design to the standard being used in the geographic location you are selling in...I can tell you nothing will work that has a danger of electrocution attached....

https://greentransportation.info/ev-charging/range-confidence/chap8-tech/ev-dc-fast-charging-standards-chademo-ccs-sae-combo-tesla-supercharger-etc.html

https://en.wikipedia.org/wiki/IEC_62196

https://en.wikipedia.org/wiki/Charging_station

__________________
All living things seek to control their own destiny....this is the purpose of life
Reply
Guru

Join Date: Mar 2007
Location: by the beach in Florida
Posts: 33392
Good Answers: 1817
#2

Re: Insulation Monitoring Device for DC Fast Charging Station

11/11/2020 5:51 AM

http://www.sendyne.com/Company/Publications/Insulation%20Monitoring%20of%20Quick%20DC%20Charging%20Stations%20v0.1.pdf

"The number of electric vehicles is constantly increasing and will grow even faster in the future. This will also help to expand the charging station infrastructure, as DC charging stations are the first choice when electric vehicles need to be charged in the shortest possible time. Electrical safety must be ensured during the charging process. For this purpose, an unearthed DC power supply system (IT system) with insulation monitoring by an insulation monitoring device (IMD) is installed. The user must never be exposed to high voltages (up to 1000 V) at any time."

https://en.dold.com/company/press-center/insulation-monitoring-in-dc-charging-stations-rn-5897-020.html

"What are the requirements of the standard? n ISO6469-3:2011 Electrically propelled road vehicles – Safety specifications – Part 3: Protection of persons against electric shock "the minimum insulation resistance of the on-board network must be maintained throughout the service life and under all operating conditions"."

http://www.bender.ro/aplicatii/documentatie_aplicatii/Emobility_PROSP_en.pdf

__________________
All living things seek to control their own destiny....this is the purpose of life
Reply
Guru

Join Date: Oct 2006
Location: 44.56024"N 15.307971E
Posts: 8277
Good Answers: 270
#3

Re: Insulation Monitoring Device for DC Fast Charging Station

11/11/2020 7:27 AM

The common thread to all of the methods used are to prevent hazardous differential voltages from the person to the source,(or ground.)

The codes are usually created and reviewed by the underwriters(Insurance Companies) based on past experiences and claims.

There are many ways to tan a hide.

Each rule has it's particular design based on the locale and the engineers opinion o how to best comply,considering cost and effectiveness.

Codes are frequently revised due to differences on interpretation of the rules,and advances in technology.

Codes and rules are living documents,like languages that evolve over time.

__________________
"A man never stands so tall as when he stoops to help a child." "Never argue with a stupid person.They will drag you down to their level and beat you with experience" "To create an apple pie from scratch, first you must create a universe"
Reply
Guru

Join Date: Oct 2006
Location: 44.56024"N 15.307971E
Posts: 8277
Good Answers: 270
#4

Re: Insulation Monitoring Device for DC Fast Charging Station

11/11/2020 7:36 AM

IHMHO:

The bottleneck in the electric vehicle advancement is the availability of charging stations.

Imagine how many Gigawatt hours it will take to replace the fossil fuel vehicles of today?This infrastructure will require many changes and a long time to implement.

How much energy to replace a gallon of gasoline or diesel?

Charging stations must have a huge reservoir of energy available to handle demand,and they may be located close to solar grids for economy,or be connected to the grid with superconductors.

It will eventually happen,with advances in storage methods and batteries,capacitors,etc. but it will take a considerably long time I think.

__________________
"A man never stands so tall as when he stoops to help a child." "Never argue with a stupid person.They will drag you down to their level and beat you with experience" "To create an apple pie from scratch, first you must create a universe"
Reply Off Topic (Score 5)
Guru

Join Date: Jul 2007
Location: Commissariat de Police, Nouvions, occupied France, 1942.
Posts: 2599
Good Answers: 77
#5

Re: Insulation Monitoring Device for DC Fast Charging Station

11/11/2020 3:12 PM

British Standard 7671 covers it, Mildred.

__________________
Good moaning!
Reply
Guru

Join Date: Mar 2007
Location: by the beach in Florida
Posts: 33392
Good Answers: 1817
#6
In reply to #5

Re: Insulation Monitoring Device for DC Fast Charging Station

11/11/2020 3:31 PM

"The current version is BS 7671:2018 (the 18th Edition) issued in 2018 and came into effect from 1 January 2019. [3][3] Amendment 1 to the 18th Edition was published in February 2020 but the only changes were to section 722 (Electric Vehicle Charging Installations). These changes came into immediate effect upon publication release, unlike previous amendments where 6 months elapsed before changes became compliant. [4] BS 7671 is also used as a national standard by Mauritius, St Lucia, Saint Vincent and the Grenadines, Sierra Leone, Sri Lanka, Trinidad and Tobago, Uganda, Cyprus, and several other countries, which base their wiring regulations on BS 7671."

https://en.wikipedia.org/wiki/BS_7671

Changes to Section 722

Section 722 (electric vehicle charging installations) provides requirements for the supplies to electric vehicles.

There are a number of significant changes in Section 722 of the DPC: Protection against electric shock Regulation 722.411.4.1 concerning the use of protective multiple earthing (PME) supply has changed. The exception for a dwelling if none of (i), (ii), or (iii) is reasonably practicable has been deleted. This now means that PME cannot be used unless you meet (i), or (ii), or (iii) of 722.411.4.1.

As a reminder of those regulations:

 Regulation 722.411.4.1(i) refers to a situation where a connecting point is supplied from a 3-phase installation used to supply loads other than charging points and where the load is sufficiently well balanced.

 Regulation 722.411.4.1(ii) requires a very low resistance earth electrode to mitigate the effects of an open circuit PEN conductor fault on the supply.

 Regulation 722.411.4.1(iii) refers to protection by a voltage operated device. An important change is that the regulation now makes the point that this device could be included within the charging equipment. It is worth noting that this device will also require an earth electrode.

The touch voltage threshold of 70 V mentioned in 722.411.4.1(i), 722.411.4.1(ii) and 722.411.4.1(iii) is on the basis that Table 2c (Ventricular fibrillation for alternating current 50/60 Hz) of IEC 60479-5{ed1.0} gives a value of 71 V for both-hands-to-feet, in water-wet conditions with medium contact area (12.5 cm2 ).

https://electrical.theiet.org/media/1154/the-impact-of-the-18th-edition-sections-722-753-and-new-730.pdf

__________________
All living things seek to control their own destiny....this is the purpose of life
Reply
Guru

Join Date: Mar 2007
Location: by the beach in Florida
Posts: 33392
Good Answers: 1817
#7
In reply to #6

Re: Insulation Monitoring Device for DC Fast Charging Station

11/11/2020 4:10 PM

"RCD protection Regulation 722.531.2.101 has been redrafted concerning RCD protection. The regulation now contains further requirements for both Type A and Type B RCDs to take account of DC fault current. "

https://www.proactivetechnicaltraining.co.uk/rcds-different-types/#:~:text=Type%20AC.,currents%20and%20smooth%20d.c.%20currents.

__________________
All living things seek to control their own destiny....this is the purpose of life
Reply
Guru

Join Date: Jul 2007
Location: Commissariat de Police, Nouvions, occupied France, 1942.
Posts: 2599
Good Answers: 77
#8
In reply to #7

Re: Insulation Monitoring Device for DC Fast Charging Station

11/11/2020 4:28 PM

AP#1 could also have looked that up if arsed.

__________________
Good moaning!
Reply
Guru

Join Date: Mar 2007
Location: by the beach in Florida
Posts: 33392
Good Answers: 1817
#9
In reply to #8

Re: Insulation Monitoring Device for DC Fast Charging Station

11/11/2020 5:12 PM

Yeah but what good would that do the rest of us...?

__________________
All living things seek to control their own destiny....this is the purpose of life
Reply
Guru

Join Date: Oct 2006
Location: 44.56024"N 15.307971E
Posts: 8277
Good Answers: 270
#10
In reply to #7

Re: Insulation Monitoring Device for DC Fast Charging Station

11/12/2020 5:58 AM

Using inductive coupling could eliminate a lot of the concerns with shock hazards,but this would affect the cost and profit of the vehicle,which will not fly with manufacturers.

Better to pass the cost on down to the end user,which is where all profit originates anyway.

That helps the economy.

Money is like electrons,nearly useless unless they are moving.

__________________
"A man never stands so tall as when he stoops to help a child." "Never argue with a stupid person.They will drag you down to their level and beat you with experience" "To create an apple pie from scratch, first you must create a universe"
Reply
Guru
Popular Science - Cosmology - Let's keep knowledge expanding Engineering Fields - Retired Engineers / Mentors - Hobbies - HAM Radio - New Member

Join Date: Dec 2006
Location: North America, Earth
Posts: 4528
Good Answers: 106
#11

Re: Insulation Monitoring Device for DC Fast Charging Station

11/12/2020 10:39 AM

I don't mandate it. Who are you working for?

__________________
“I would rather have questions that can't be answered than answers that can't be questioned.” - Richard Feynman
Reply
Anonymous Poster #1
#13
In reply to #11

Re: Insulation Monitoring Device for DC Fast Charging Station

11/23/2020 5:06 AM

I appreciate all the answers provided here.

Thank you

Can you please tell me Is there a Particular logic for Mandating / Non Mandating.

Why such an expensive IMD needs to be used in the first case?

Reply
Guru

Join Date: Mar 2007
Location: by the beach in Florida
Posts: 33392
Good Answers: 1817
#14
In reply to #13

Re: Insulation Monitoring Device for DC Fast Charging Station

11/23/2020 5:17 AM
__________________
All living things seek to control their own destiny....this is the purpose of life
Reply
Guru
United Kingdom - Member - Indeterminate Engineering Fields - Control Engineering - New Member

Join Date: Jan 2007
Location: In the bothy, 7 chains down the line from Dodman's Lane level crossing, in the nation formerly known as Great Britain. Kettle's on.
Posts: 32175
Good Answers: 839
#12

Re: Insulation Monitoring Device for DC Fast Charging Station

11/16/2020 4:24 AM

No standard is <...Mandatory...>. However there are commercial, safety, insurance cover and possibly legal consequences for not following the applicable ones.

__________________
"Did you get my e-mail?" - "The biggest problem in communication is the illusion that it has taken place" - George Bernard Shaw, 1856
Reply
Anonymous Poster #1
#15

Re: Insulation Monitoring Device for DC Fast Charging Station

11/23/2020 7:20 AM

For an IT Earthing system is it mandatory to provide a Insulation monitoring Device (IMD)

What is the best earthing system for a DC fast charging Station

TN, TT, IT ?

Reply
Guru

Join Date: Mar 2007
Location: by the beach in Florida
Posts: 33392
Good Answers: 1817
#16
In reply to #15

Re: Insulation Monitoring Device for DC Fast Charging Station

11/23/2020 7:28 AM
__________________
All living things seek to control their own destiny....this is the purpose of life
Reply
Guru
United Kingdom - Member - Indeterminate Engineering Fields - Control Engineering - New Member

Join Date: Jan 2007
Location: In the bothy, 7 chains down the line from Dodman's Lane level crossing, in the nation formerly known as Great Britain. Kettle's on.
Posts: 32175
Good Answers: 839
#17
In reply to #15

Re: Insulation Monitoring Device for DC Fast Charging Station

11/23/2020 7:28 AM

British Standard 7671. Again.

__________________
"Did you get my e-mail?" - "The biggest problem in communication is the illusion that it has taken place" - George Bernard Shaw, 1856