Regulator Balance Meter

11/12/2020 8:31 AM

Dear all

in exciter EX2100 from GE we have three meter (gen. field voltage,gen. field current and Regulator balance) what is the purpose of Regulator balance meter and what is the effect if it is reading positive or negative and what we will should be do to make it in zero position.

thanks

Register to Reply
Pathfinder Tags: Regulator balance meter
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.

Good Answers:

These comments received enough positive votes to make them "good answers".

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Guru
United Kingdom - Member - Indeterminate Engineering Fields - Control Engineering - New Member

Join Date: Jan 2007
Location: In the bothy, 7 chains down the line from Dodman's Lane level crossing, in the nation formerly known as Great Britain. Kettle's on.
Posts: 32175
Good Answers: 839
#1

Re: Regulator balance meter

11/12/2020 9:08 AM

CR4 does not provide access to telephone usage training.

It would be interesting to know why the <...we...> can't look this up in the information that was supplied with it, and why the <...we...> can't contact <...GE...> and obtain this information "from the horse's mouth", as it were.

__________________
"Did you get my e-mail?" - "The biggest problem in communication is the illusion that it has taken place" - George Bernard Shaw, 1856
Register to Reply
2
Guru

Join Date: Apr 2010
Location: About 4000 miles from the center of the earth (+/-100 mi)
Posts: 9910
Good Answers: 1141
#2

Re: Regulator balance meter

11/12/2020 9:14 AM

If you have two generators (or 1 generator and a bus) in parallel and the regulator voltages are not adjusted equally, there will be reactive current flowing between the generators. This reactive current is not contributing to any power output and is only heating up the generator coils, wasting energy. Adjust the voltage (excitation) on the generator until the meter reads zero.

  • "When generator sets operate in parallel the alternator field excitation system of each generator set controls the proportional sharing of the total reactive power requirements (kVAR) of the system.
  • The kVAR load sharing is achieved by increasing or decreasing the field excitation to the systems’ alternators.
  • As the field excitation of one generator set in a group is increased i.e. overexcited it will not lead to an increase in voltage (as it would if it were operating alone) but it will lead to an increase in the proportion of the total kVAR load it will deliver and a decrease in its power factor.
  • As the field excitation of one generator set in a group is decreased i.e. under-excited it will not lead to a decrease in voltage (as it would if it were operating alone) but it will lead to a decrease in the proportion of the total kVAR it will deliver an increase in its power factor."

https://dieselship.com/marine-technical-articles/marine-electro-technology/active-reactive-power-sharing-in-a-paralleled-generator-set-kw-kvar/#:~:text=When%20generator%20sets%20operate%20in%20parallel%20the%20alternator%20field%20excitation,excitation%20to%20the%20systems'%20alternators.

Register to Reply Good Answer (Score 2)
Guru

Join Date: Jul 2016
Posts: 1367
Good Answers: 105
#4
In reply to #2

Re: Regulator balance meter

11/13/2020 2:07 PM

If Regulator Balance is really reactive power or generator power factor, generating at unity power factor or less is the least stable operating point for the generator, providing little margin for pullout, and reducing the possible contribution to power system stability that the generator could provide. It’s generally better to operate the generator so it is exporting reactive power.

I wonder if the balance is between two regulator components, static (PPT) and SCT sources for excitation. You could bias the SCT excitation to balance out the sources to improve stability.

In any event, best to find out what it really indicates before setting targets or adjusting controls....

The GE EX 2100 user manual is useless for this, BTW

Register to Reply
Guru
Popular Science - Cosmology - Let's keep knowledge expanding Engineering Fields - Retired Engineers / Mentors - Hobbies - HAM Radio - New Member

Join Date: Dec 2006
Location: North America, Earth
Posts: 4528
Good Answers: 106
#3

Re: Regulator Balance Meter

11/13/2020 12:29 AM

Surely there is an operation manual for the unit. Lacking that you can call the company and talk to a technician or engineer for assistance.

__________________
“I would rather have questions that can't be answered than answers that can't be questioned.” - Richard Feynman
Register to Reply Score 1 for Good Answer
Guru

Join Date: Jul 2016
Posts: 1367
Good Answers: 105
#5

Re: Regulator Balance Meter

11/13/2020 3:10 PM

It’s likely you have redundant excitation supplies, and the meter shows how the operating supply compares with the backup supply. There should be a trim pot somewhere to adjust the tracking. Normally you might have automatic tracking, so the null meter should read close to zero throughout your operating range, providing everything is working ok.

Register to Reply
Active Contributor

Join Date: Jan 2016
Posts: 16
Good Answers: 1
#6

Re: Regulator Balance Meter

11/13/2020 6:37 PM

I believe that you have two regulators, the "Automatic" (AVR) adjusts the excitation current to follow the system voltage and produces the VAR load the system needs. The "Manual" (MVR) controls the excitation, directly, and is mostly used in bringing the unit on line or doing some on-line maintenance. To go from AVR to MVR one would get the balance to zero, first.

Register to Reply Score 1 for Good Answer
Register to Reply 6 comments

Good Answers:

These comments received enough positive votes to make them "good answers".

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Copy to Clipboard

Users who posted comments:

Power Prof (1); PWSlack (1); Rixter (1); rwilliams (2); StandardsGuy (1)