HT yard CT confusion

11/18/2007 3:51 AM

hi every one

In HT Yard for 11KV we have three CTs.each CT has rating 100-50/5-5amps & ammeter has same rating too.what is the meaning of that.will it work according to 100/5amps or 50/5amps.if it will work for both the ratings then how it will work. While checking the current which rating we should consider or how we can findout in ammeter for which rating it is working.& One more each CT has 6 terminals.Two terminals for primary output.Two terminals for core protection one.Another two terminals for core protection two.aprt primary output termanls what is other four terminals core protection & core protection two.

__________________
manish
Register to Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Guru
Safety - ESD - New Member India - Member - New Member Engineering Fields - Energy Engineering - New Member

Join Date: May 2007
Location: Pune , India
Posts: 875
Good Answers: 42
#1

Re: HT yard CT confusion

11/18/2007 9:09 AM

100-50/5 is given for the installation engineer to decide what ratio he require for protecting the system depending on the output load of the breaker to be protected. As per the design of the system requirement the ratio is decided . Once it is set ,the ratio selected should be written clearly on the panel for the information of the operating and maintenance staff.

Register to Reply
Guru

Join Date: Jun 2007
Location: chennai,India
Posts: 592
Good Answers: 19
#2

Re: HT yard CT confusion

11/18/2007 12:31 PM

CTs will have primary and secondary.General conventional say 100/5 means 100 amps primary 5 amps secondary.this will have secondary terminals s1 and s2 for secondary and terminal P1 and P2 for primary.

In your case you have mentioned 100-50/5, this means dual ratio CT ,which means there will be tappings on the secondary side and terminals will be marked as S1,S2and S3and primary terminals will be P1 and P2.

This dual ratio CTs are incorporated in a system where in there will be increase in load at a later stage or for expansion,.In your case may be initialy you will have 50 Amps primary current and later you will increase to 100 amps.

In this instance you may have to connect the ammeter to s1 and s2 and short terminals s2 and s3 for ratio of 50/5.

for ratio of 100/5, you have to connect ammeter to the terminals s1 and s3.

Since you have mentioned 6 terminals I presume the Cts are dual core,dual ratio.Dual core means one core will be used for instruments and other core will be used for protection.You should not mix the cores,the class rating for instruments may be class1 and protection core may me 5p10.

I suggest send the drawings to us for study and advise.

__________________
Ramesh,Freelance Electrical/automation Consultant
Register to Reply Score 1 for Good Answer
Anonymous Poster
#3
In reply to #2

Re: HT yard CT confusion

11/19/2007 5:01 PM

thankyou sir,

what ever u sent to me i got it.how it works.but i have one doubt.CT has two core protections.core protection one & core protection two.that i didn't get two core protection for what.please reply me sir.thanks

Register to Reply
Guru

Join Date: Jun 2007
Location: chennai,India
Posts: 592
Good Answers: 19
#4
In reply to #3

Re: HT yard CT confusion

11/20/2007 12:06 AM

It is usual practice to have 2 core CTs, one for instruments circuit and other core for protection circuit.In certain cases both the cores will be used for protection circuit with different class, may be one core for IDMT relay and other one Differential protection relay.I can not comment without looking at the complete drawings of the Substation.

Are you same person posted the query or different person?

__________________
Ramesh,Freelance Electrical/automation Consultant
Register to Reply
Guru

Join Date: Jun 2007
Location: chennai,India
Posts: 592
Good Answers: 19
#5
In reply to #2

Re: HT yard CT confusion

12/12/2007 12:14 AM

Sorry I made a mistake, there is no need to short the terminals s2 and s3 when you connect the instrument /relay between s1 and s2.

I deeply regret for the error.

__________________
Ramesh,Freelance Electrical/automation Consultant
Register to Reply
Anonymous Poster
#6

Re: HT yard CT confusion

03/21/2008 8:32 AM

Sir,

I have one doubt in this context. PLease tell me how to interpret the CT class "5P10" or whatever?

Register to Reply
Register to Reply 6 comments

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Copy to Clipboard

Users who posted comments:

Anonymous Poster (2); ramvinod (3); V.I.Abraham (1)

Previous in Forum: generator earthing   Next in Forum: three phase voltage variation
You might be interested in: Wire Terminals, Core Shafts and Mandrels, Core Modules

Advertisement