Can RH Be >100% In The Return Air Duct??

12/06/2007 12:00 PM

Hi all

There is something that puzzles me..i saw that my RH reading was 102%! [more than 100%!!] in my return air duct into the AHU. can RH be MORE THAN 100%??!! or does the RH meter instrument in the return air duct out of spec.? or the feedback signal to my software is out of tune?! how can it be more than 100%??!!

supply air temp was around 17deg and return was 22deg. Also i observe sweating around the cws/cwr duct around the AHU unit.. mmm..

Register to Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.
Guru
United Kingdom - Member - Olde Member!! Engineering Fields - Instrumentation Engineering - New Member

Join Date: Jul 2006
Location: Dunstable, England
Posts: 2821
Good Answers: 45
#1

Re: can RH be >100% in the return air duct??

12/06/2007 2:26 PM

The spec for a typical RH sensor is only +/- 2% of reading, please note that this is for a limited range say 10% to 90%

So anything outside of that RH say above 90% can not be relied upon. Also many RH sensors can not operate satisfactorily if they are wetted, so your sensor may need drying out and recalibrating... In fact some of the adsorbing types can not tolerate some chemicals.

Either way check the calibration of your instrument at its end points near 90% etc...

John.

__________________
A little knowledge is a dangerous thing - Googling is far worse!
Register to Reply
Commentator

Join Date: Dec 2005
Posts: 92
Good Answers: 5
#2

Re: Can RH Be >100% In The Return Air Duct??

12/06/2007 5:17 PM

Show me a Psycrometric chart that shows you can get more then 100% RH.

More then 100% RH and you get condensation

Register to Reply
Power-User

Join Date: Apr 2007
Posts: 319
Good Answers: 4
#3

Re: Can RH Be >100% In The Return Air Duct??

12/06/2007 11:32 PM

If you looked at the basics probably you may not have asked this question.

Relative humidity in simple terms is defined as amount of moisture in a given air volume of air divided by amount of moisture in same amount of air volume when air is saturated with moisture.

So by definition RH cannot go above 100%. If RH is 100% and if you coll air further excess moisture will condensate.

Remember lower the temperature you need less moisture to saturate air.

Obviously something is wrong with your meters or readings are out side the limits.

__________________
sisira
Register to Reply
Guru
New Zealand - Member - Interested in everything- see my Profile please APIX Pilot Plant Design Project - Member - Member Engineering Fields - Electrical Engineering - Member Engineering Fields - Power Engineering - Member Engineering Fields - Civil Engineering - Member Hobbies - Musician - Autoharp and Harmonica Hobbies - Hunting - Member Hobbies - Fishing - Member

Join Date: Nov 2007
Location: Christchurch, (The Garden City), South Island, New Zealand
Posts: 4395
Good Answers: 230
#4

Re: Can RH Be >100% In The Return Air Duct??

12/07/2007 12:17 AM

Hello waterlucky,

100% RH is fully saturated, and the air cannot hold any more unless warmed, which then alters the RH, of course....

If it was really 102%, it would be pouring rain inside that return duct, and time to look around for a pump and a boat.

Kind Regards.....

__________________
"The number of inventions increases faster than the need for them at the time" - SparkY
Register to Reply
Anonymous Poster
#5
In reply to #4

Re: Can RH Be >100% In The Return Air Duct??

12/07/2007 3:34 AM

Love the annimation...where did you get it from

Andy

andy@cds-concrete.com

Register to Reply Off Topic (Score 5)
Guru
New Zealand - Member - Interested in everything- see my Profile please APIX Pilot Plant Design Project - Member - Member Engineering Fields - Electrical Engineering - Member Engineering Fields - Power Engineering - Member Engineering Fields - Civil Engineering - Member Hobbies - Musician - Autoharp and Harmonica Hobbies - Hunting - Member Hobbies - Fishing - Member

Join Date: Nov 2007
Location: Christchurch, (The Garden City), South Island, New Zealand
Posts: 4395
Good Answers: 230
#6
In reply to #5

Re: Can RH Be >100% In The Return Air Duct??

12/07/2007 4:28 AM

Hello Andy,

OFF THE MAIN TOPIC, but helpful to others, I trust.

Pleased to assist you, and other happy readers.

Email Address:

It's really not a good idea to put your email address in the Forum, because this Forum is accessible to Search Engines, thus your email address may then be harvested by a spam bot, and sold to others. There is the same advice in the CR4 FAQ.

Re: Graphics - Animated and otherwise:

I sometimes "liberate" graphics after doing a Google Graphics search for what I want.

So, let's say I want an animated picture of an umbrella, I type into Google Graphics Search Engine the two words umbrella ani (not in bold case, of course).

The Google gears spin, and moments later I have a selection of umbrella pics, hopefully animated (ani = animated).

I surf through, locate a likely one, and very importantly I ensure I go to the actual website, then the full-size graphic. (I don't want the fixed thumb nail picture as shown on Google)

I check for animation, if OK, I save to my PC system desktop in the meantime, (later moving it to a more permanent location), so I can easily locate it, and also rename the file, so I can remember what it is.

So now I have the file in my system, click in the text Editor in the Forum, (where I want that graphic), go to the small button which looks like a camera (Insert/Edit Image) and click on that.

A small Graphics Editor window pops up, I choose the middle option of "Image Path".

That allows me to explore my PC System here, until I locate the graphic I want (easy if that graphic is temporarily on the desktop).

Once the small Graphics Editor has "grabbed the file", I press the "Submit" button,and the graphic file is UPLOADED to the CR4 website, and given a reference number to locate it in the Post I make.

Then the Graphic appears in the Text Editor, (If animated, it is not yet seen as animated in the Text Editor Window), I carry on and press the "Preview Comment" button in the normal way.

The Preview Comment window opens,and if the graphic file is compatible with the CR4 Forum Software, that animation now shows the animation. (Sometimesthe animation doesnot work, in that case I "Cut" the file, to remove it, back in the Text Editor).

If the picture is in the wrong place, I Edit Post, use Right Click on the graphic (Firefox Browser), and "Cut", then move the cursor to the new location, and ctrl + V = Paste the graphic into the text Box.

Repeat the "Preview Comment" and if OK, Post the completed Comment.

You will be aware that it does pay to look at the completed Post, as it may need further Editing, and CR4 Forum Software advises there is only a total time of 15 minutes allowable for any further Edits.

Please note the above instructions are for the CR4 Forum (This Forum), and instructions for other Forums vary somewhat from the above, depending on the Forum Software, and Forum Rules.....

I have now "several" GB of useful graphics on my local system, all categorised, renamed, and in folders so they are easily located - When I locate any useful graphic, I 'liberate it" for future use.

I also have purchased hundreds of GB of various graphics from others, as required.

You can also Right Click in Firefox Browser, on most Websites (including this one), and "Save As", almost all graphics.

Have a go, nobody taught me how, I just tried things until they worked - here is a real picture of myself

Kind Regards.....

__________________
"The number of inventions increases faster than the need for them at the time" - SparkY
Register to Reply Off Topic (Score 5)
Guru
Engineering Fields - Retired Engineers / Mentors - New Member

Join Date: Dec 2006
Location: Brecksville, OH
Posts: 1621
Good Answers: 18
#7

Re: Can RH Be >100% In The Return Air Duct??

12/07/2007 11:06 AM

I would concur that your RH unit is out of calibration or out of the range of specified accuracy. Greater than 100% RH is not possible, rather you should see signs of condensation on the unit.

__________________
"Consensus Science got us into this mess, then why can't it get us out?" : Rephrase of Will Rogers Comment
Register to Reply
Anonymous Poster
#8

Re: Can RH Be >100% In The Return Air Duct??

12/07/2007 6:05 PM

no

Register to Reply Off Topic (Score 5)
Guru

Join Date: Jul 2006
Location: Eastern Kansas USA
Posts: 1503
Good Answers: 128
#9

Re: Can RH Be >100% In The Return Air Duct??

12/10/2007 10:49 PM

Friends,

I have to disagree with the logical answer given. Supersaturation is a fairly common event. There are two conditions which drive this effect--the lack of a nucleus on which to condense and the speed of temperature change. A supersaturated gaseous solution is unstable and therefore short-lived, so it would be difficult to observe or measure. Therefore an unstable condition of RH being above 100% is quite reasonable.

Beyond the above phenomenon, the basic question in the post was well answered by noting the limits of calibration and accuracy of the sensor involved.

Regards--JMM

Register to Reply
Guru
New Zealand - Member - Interested in everything- see my Profile please APIX Pilot Plant Design Project - Member - Member Engineering Fields - Electrical Engineering - Member Engineering Fields - Power Engineering - Member Engineering Fields - Civil Engineering - Member Hobbies - Musician - Autoharp and Harmonica Hobbies - Hunting - Member Hobbies - Fishing - Member

Join Date: Nov 2007
Location: Christchurch, (The Garden City), South Island, New Zealand
Posts: 4395
Good Answers: 230
#10
In reply to #9

Re: Can RH Be >100% In The Return Air Duct??

12/10/2007 11:36 PM

Hello JMM,

I do agree with your explanation of Supersaturation, and this is often seen in New Zealand's Southern Alps, where Supersaturated air runs into a snowcapped mountain peak, chills instantly, and the cascade effect means extremely heavy rain, for a short time.

Mount Egmont, all alone away from other hills or mountains, 8000+ foot volcanic peak, in NZ's Taranaki region of the North Island, has also the same effect.

Many climbers at or near the peak of Mt. Egmont, have been caught out, with a clear sky and within a few seconds heavy rain or snow falling - a few have lost their lives, because of this effect - The weather front is not actually seen, until after it has arrived.

I have seen a 45 degree sloped mountainside, in the Southern Alps, running 2+ inches deep with water, and the sheer volume of water falling, made me thank God, that He designed noses the way they are, similar to an umbrella.

At that time, 12 miles further down the valley, the hotel rain gauge overfilled, and the rainfall there was over 12 inches in under 9 minutes.

I have yet to see a return air duct big enough to have clouds forming inside, although there are hangars and NASA assembly buildings in the US, where rain has fallen inside, due to the lowering of the Saturation point....

__________________
"The number of inventions increases faster than the need for them at the time" - SparkY
Register to Reply
Active Contributor

Join Date: Dec 2007
Posts: 17
Good Answers: 1
#11
In reply to #10

Re: Can RH Be >100% In The Return Air Duct??

12/12/2007 5:04 AM

"I have yet to see a return air duct big enough to have clouds forming inside, although there are hangars and NASA assembly buildings in the US, where rain has fallen inside, due to the lowering of the Saturation point....

"

They have a big enviro chamber hangar in florida. The USAF wanted to do cold weather start tests on an SR-71 there. The Lockheed guys asked if the air conditioning in the building could handle the SR's engines and were assured it could. The idea was that the exhaust would be ducted/sucked out to keep the hangar cold.

So, they did the test... and collapsed the ducting in the hangar. The SR-71's engines blew air out faster than the building ducts could replace it and they got sucked down flat - like when the milk shake gets frozen solid and you cant suck it up. The Egland AFB guys were pretty embarrassed, but they had tested big cargo planes and didn't figure a little measly 150,000GTOW plane could hurt them - it was apparently pretty funny

Register to Reply
Power-User

Join Date: Mar 2007
Location: Northeast Pennsylvania, USA
Posts: 173
#12
In reply to #9

Re: Can RH Be >100% In The Return Air Duct??

12/15/2007 12:52 AM

Actually, I think that you are mistaken, even though "super saturation" events as you describe could possibly exist. RH is abreviation for relative humidity with no definitive answer for actual grains of moisture and is described as the present amount of moisture in the air compared to the MOST it can hold at that temperature ( dewpoint.). 100% is "tops". Any attempt to add more moisture results in the moisture "raining out". Same holds true for lowering air temp which decreases ability to hold water, but the result is the same....100% RH.

An interesting observation is to place a hygrometer / thermometer in a supply air duct during AC operation. Typically you would see an 18° to 22° F drop in discharge air temp but the RH may RISE by 20% to 30% ( in the duct only ). But when it mixes with the room air, the resultant will be lower temp and lower RH after some period of time.

I like to limit duct RH to 90% in hope of never condensing moisture and growing mold.

__________________
Unless you're the lead dog on the sled, the view is always the same....
Register to Reply
Guru

Join Date: Jul 2006
Location: Eastern Kansas USA
Posts: 1503
Good Answers: 128
#13
In reply to #12

Re: Can RH Be >100% In The Return Air Duct??

12/15/2007 1:54 AM

Sniccus,

I would tend to agree with both yourself and Agua-Doc, that RH by definition ranges between 0 and 100%. Certainly in the design and installation of HVAC ductwork and systems you want the 100% point with its condensation to occur only at the evaporator coils where a drain is readily available. You are correct to note that the %RH is strictly a function of the air temperature so long as the absolute humidity does not change during that time.

However, at the microscopic level two molecules of water do not magically find each other and immediately form a drop when that magic dew point is reached, which we call 100% RH. There is almost always some very small particle of dust or other material in the air which becomes the nucleus around which the water can condense back to a liquid. In highly purified air, where these particles are considerably less common, you can cool the air noticeably below the saturation temperature before even micro-drops (fog) form. And, as I said in my post, if you cool typical outdoor or indoor air quickly there will be a brief time before the molecules will have had enough time to move together and condense. Under either of these conditions (highly purified moist air or rapidly cooled moist air), you briefly have a greater amount of water (by weight) in the vapor phase than would normally saturate the air. Mathematically this would demand that the RH be expressed as a number greater than 100%.

We generally don't look at things from this viewpoint. So your assertion that we "can't" have RH over 100% is understandable even though it is incorrect.

regards--John M.