Wiring 3 phase transformers

12/06/2007 9:27 PM

If a 3 phase step down general purpose transformer such as one with a 480 volt primary with a 240 volt secondary is wired in reverse, in other words 240 volts is appplied to the secondary to achieve an ouput of 480 volts what effect is had on the transformer's kva rating?

Register to Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Power-User

Join Date: Mar 2007
Location: Northeast Pennsylvania, USA
Posts: 173
#1

Re: Wiring 3 phase transformers

12/06/2007 10:24 PM

Kva rating is still exactly that. It doesn't change. You can step the voltage up or down with a transformer and you must not exceed its rated amperage rating

__________________
Unless you're the lead dog on the sled, the view is always the same....
Register to Reply Score 1 for Good Answer
Guru
New Zealand - Member - Interested in everything- see my Profile please APIX Pilot Plant Design Project - Member - Member Engineering Fields - Electrical Engineering - Member Engineering Fields - Power Engineering - Member Engineering Fields - Civil Engineering - Member Hobbies - Musician - Autoharp and Harmonica Hobbies - Hunting - Member Hobbies - Fishing - Member

Join Date: Nov 2007
Location: Christchurch, (The Garden City), South Island, New Zealand
Posts: 4395
Good Answers: 230
#2

Re: Wiring 3 phase transformers

12/06/2007 10:28 PM

Hello yardbird,

No effect on transformer rating.

Before you try this, check the transformer terminals and connections.

Also check that the currents the transformer windings are capable of, are suitable for your project.

Normally the transformer may be Delta connected Primary (480 Volts) and Star Connected Secondary (240 Volts).

Each Winding is normally brought out as a separate pair, with moveable copper or brass strips to "jumper across the various terminals to achieve Delta/Delta, Delta/Star, Star/Delta, Star/Star.

If your transformer is of reasonable size, there should be a nameplate or connection diagram, inside the connections box/es.

Ensure that your transformer is truly a 3 phase transformer, if you need 3 phase. (It may be 480-0-480 Volt to 240-0-240 Volt = Centre tapped both primary and secondary) = Single Phase.

See how it goes for you, let's know how you progress.....

__________________
"The number of inventions increases faster than the need for them at the time" - SparkY
Register to Reply
Active Contributor

Join Date: Dec 2007
Location: india
Posts: 15
#3

Re: Wiring 3 phase transformers

12/07/2007 1:19 AM

hi,

its not at all possible because the py. wdg will be designed to withstand 480v and viceversa.

P=VI,if V INCREASES THEN I DECREASES and viceversa.

but u can give the sy voltage and achieve py. voltage.

thank u,

naveen.m

__________________
naveen
Register to Reply Score 1 for Off Topic
Anonymous Poster
#20
In reply to #3

Re: Wiring 3 phase transformers

07/09/2008 10:19 PM

It is possible. You are technically backfeeding the transformer. Instead of the incoming current being on the 480V, or the H1, H2, H3 terminals (normally the primary on this type of transformer) the incoming current is being fed into the 240V terminals X1, X2....

Register to Reply
Guru
Safety - ESD - New Member India - Member - New Member Engineering Fields - Energy Engineering - New Member

Join Date: May 2007
Location: Pune , India
Posts: 875
Good Answers: 42
#4

Re: Wiring 3 phase transformers

12/07/2007 2:53 AM

The information provided is incomplete. You have not specified weather the transformer you are using is Delta/Star , D/D S/S or three phase to single phase. If star connected weather the star point is internally done or externally done . You want to use a transformer designed for step down to be used as step up. So post complete details so that correct guidance can be given.

Register to Reply
Anonymous Poster
#5

Re: Wiring 3 phase transformers

12/07/2007 4:00 AM

hi,

i too understand that concept but what i mean is that, if we are reversing the voltage it will not effect the KVA rating.the thing is it wii act as stepup transformer .but we can use the 3ph 415 load with the py. current rating only and not with the sy. current rating.

thank you and best regards,

naveen.m

Register to Reply
Guru
Canada - Member - If there is a way to screw someting up, there is someone to do so! Safety - Hazmat - New Member

Join Date: Mar 2007
Location: Iqaluit, NU. Canada
Posts: 1854
Good Answers: 140
#6

Re: Wiring 3 phase transformers

12/07/2007 7:56 PM

To answer your question... there is no effect on KVA rating of the transformer at all. I do hope you recognize the current voltage relationship of this setup.

A few posters have asked about whether or not the winding configurations are D/S or S/D or S/S or D/D. A 480/240 volt transformer would more then likely be a D/D.

Using such a transformer as a step up one would raise some interesting issues around grounding, as if it is in fact D/D there is no way to ground it other then to corner ground one leg of the 480 three phase primary.

Best advice... be very careful and well understand what you are doing and how to do it.

Rick...

__________________
Joe Contractor to Electrical Inspector, "What do you mean you are going to make me follow the code?".
Register to Reply
Participant

Join Date: Nov 2007
Posts: 2
#7

Re: Wiring 3 phase transformers

12/07/2007 11:07 PM

i may mention to take care about the vector group relationship of the reversed 3-phase transformer will be changed

so take care if you want to connect it as parallel supply

Register to Reply
Anonymous Poster
#8

Re: Wiring 3 phase transformers

12/08/2007 1:55 AM

No Effect. Because over all KVA rating will be Same.

Register to Reply
Anonymous Poster
#9

Re: Wiring 3 phase transformers

12/08/2007 8:45 AM

Do not forget that the short circuit current, in this case, for the low voltage winding will be severaly increased.

Regards

Register to Reply
Guru
Hobbies - DIY Welding - New Member

Join Date: Feb 2007
Location: Next to the Prime Merridian (51°29'34.50"N 0°13'32.85"W)
Posts: 780
Good Answers: 1
#10

Re: Wiring 3 phase transformers

12/08/2007 9:20 AM

Hi everyone, I think you all put in something interesting.

Idealy I tend to agree with those who claim there's no difference and you can use a transformer both ways (as step up or step down).

However, there's hickup though because some transformers are really designed to be used in just one way as they work more efficiently than if you try to use them the other way.

Most small general purpose TRFs do work equaly well in both ways but not necessarily the larger 3 phase ones including the toroidal types.

I will leave this puzzle up to you to figure it out but will be happy to get back about it later.

This is not a mind game it is quite serious.

__________________
Making mistake is part of learning.
Register to Reply
Member

Join Date: Dec 2007
Posts: 5
#11
In reply to #10

Re: Wiring 3 phase transformers

12/08/2007 9:41 AM

Thanks to everyone for their responses. The transformer in question is designated as a step down transformer with a primary of 480 and a secondary of 240 with a rating of 75KVA. The unit was already in service in the reverse mode when I ran across it. The application is showing a current draw of 28 Amps on the secondary side. Sorry that I did not give enough info regarding the wiring configuration(Star,Delta/Wye). I will have to look when I go back into the plant. I tend to think that due to the physical size of the respective windings that one would lose some capacity as well as a greater chance of over current shorting on the secondary winding.

Register to Reply
Active Contributor

Join Date: Jul 2007
Location: Los Angeles
Posts: 23
#12
In reply to #11

Re: Wiring 3 phase transformers

12/08/2007 11:02 AM

There is a difference in the construction of a step-up and step down transformer. I don't know the specifics. I have ordered both for customers. I have seen a few installations were they are used opposite and they do work, however they get noisy and fail prematurely. I suggest you contact a few of the specialty transformer Manufactures ( in North America Olsun Electric, and MGM transformer come to mind).

Register to Reply
Power-User
Hobbies - Fishing - New Member

Join Date: Feb 2007
Location: Suva Fiji Islands
Posts: 229
Good Answers: 3
#13

Re: Wiring 3 phase transformers

12/12/2007 5:09 AM

Hi yardbird

Ther are some good answers in this thread. Hopefully they will enlighten you

BUT if you didnt know the answer before you asked the question then you shouldnt be messing with electricity. The results of ignorance are aften fatal!

__________________
"Multa ferunt anni venientes commoda secum, Multa recedente adimiunt". (The years as they come bring many agreeable things with them; As they go they take many away).
Register to Reply
Member

Join Date: Dec 2007
Posts: 5
#14
In reply to #13

Re: Wiring 3 phase transformers

12/12/2007 7:06 PM

Thanks for your response. According to all of the responses all of which were very informative, this is not a condition ran across by electricial engineers everyday. As for my experience with electricial issues, I have never met but one man who claimed to know it all and he almost got me killed. Remember the old saying; The only dumb question is the one not asked.

Register to Reply
Guru
Canada - Member - If there is a way to screw someting up, there is someone to do so! Safety - Hazmat - New Member

Join Date: Mar 2007
Location: Iqaluit, NU. Canada
Posts: 1854
Good Answers: 140
#16
In reply to #14

Re: Wiring 3 phase transformers

12/12/2007 10:40 PM

Very very true!

__________________
Joe Contractor to Electrical Inspector, "What do you mean you are going to make me follow the code?".
Register to Reply
Member

Join Date: Dec 2007
Posts: 5
#15

Re: Wiring 3 phase transformers

12/12/2007 7:16 PM

Did a little bit of checking on this issue. A plasma cutter unit is being supplied by this arrangement. With a current draw of 29 amps on the 480VAC(now the secondary) side of the transformer, a current draw of 72 Amps is seen on the 240VAC(Primary)of the transformer. Transformer is fed with a 100A circuit on the 240VAC side.Transformer is a 3 phase unit.

Register to Reply
Guru
Canada - Member - If there is a way to screw someting up, there is someone to do so! Safety - Hazmat - New Member

Join Date: Mar 2007
Location: Iqaluit, NU. Canada
Posts: 1854
Good Answers: 140
#17
In reply to #15

Re: Wiring 3 phase transformers

12/12/2007 10:44 PM

How did you ground the 480 volt 3 phase secondary? Please don't tell me it is not grounded! If it is not grounded, did you install a ground fault indication system?

__________________
Joe Contractor to Electrical Inspector, "What do you mean you are going to make me follow the code?".
Register to Reply
Member

Join Date: Dec 2007
Posts: 5
#18
In reply to #17

Re: Wiring 3 phase transformers

12/13/2007 6:54 PM

I did not install this system. It was already in service when I was brought in to do some controls design and installation. The said equipment was to be set up for motor voltage of 480 volts. I informed the management staff that the primary coming into the building was 240 volt 3 phase. They in turn said no we have 480 volts. This is how I became involved with this issue. No ground fault system is in place. As for grounding I have not had the time to open up the unit. All I can say is there is a ground wire leaving the unit and does show continuity to other grounds and the conduit from the unit.

Thanks

Yardbird

Register to Reply
Guru

Join Date: Feb 2006
Posts: 1758
Good Answers: 6
#19

Re: Wiring 3 phase transformers

04/01/2008 8:32 PM

Regards !

All such trasformers can be used & are made to be used both way.

NOT AT ALL ANY DIFFERENCE IN CONSTRUCTION FOR USE IN ONE WAY OR THE OTHER.

If it is a multi Windings/Taps Transformer, then using only one tap as primary

will give only the VA of that winding /tap.

Single tap Step-up or Step-down are the same thing & only the ratio of windins /voltage will decide what it is Step-up or Step-down.

Simple rule of TRANSFORMATION.

Register to Reply
Anonymous Poster
#21
In reply to #19

Re: 3 phase transformers

07/10/2008 4:04 AM

pls clarify that for a star-star transformer of 15MVA we have to include terdiary delta winding or noy.

if yes pls give solution.

Register to Reply
Register to Reply 21 comments

"Almost" Good Answers: