we have a capacitor after GCB with specifications (125 nanofarad, 27kv,In 0.2A) now
this capacitor it is damaged,and we have a new capacitor with specifications (75
nanofarad,27kv,In 0.5A) can we use it, and if we can use is what is the effect.
thakks
Pathfinder Tags: capacitor
Re: capacitor
06/05/2022 4:28 AM
Re: capacitor
06/05/2022 1:11 PM
What you have to do is ask yourself, why is this capacitor here, what is its function? ...and have things changed regarding this reason...like a change in load characteristics?...or a capacitor bank added? ...or some other modification...Has the new capacitor been recommended by an engineer or industry professional?...surely this isn't some random part you just had lying around, it was ordered for a reason, or did you receive the wrong part? What will happen depends on these facts...
Re: capacitor
06/05/2022 7:13 AM
More information will yield more and better results.
A circuit diagram,perhaps,frequency,application?
All these acronyms have got to stop!---- ASAP!
Re: capacitor
06/05/2022 10:26 AM
No! You should not use this capacitor. You do not grasp all of the critical information needed to evaluate how a capacitor works in a circuit design.
The replacement capacitor at the rated voltage will store about 27 Joules of energy while the damaged capacitor will store about 45 Joules of energy.
These energy levels are dangerous. A novice should not be involved in evaluating, handling, installing, or designing any circuitry utilizing this much energy. You clearly are a novice.
Now, other members of your collective "we" hopefully do have enough knowledge and experience in circuitry to select a replacement capacitor. The difference in energy storage may even be why the original capacitor was damaged. I cannot tell from the information you have provided.
Re: Capacitor
06/06/2022 5:17 AM
Looking at the capacitor supplied you would need 2 in parallel to provide 150nF. Another parameter is the tolerance % of the capacitor. Ie +-5%, +-10% +-20%.
You could measure the capacitance of the replacement capacitor to see its actual capacitance and then determine a parallel replacement to give 120nF.
Hare today, goon tomorrow!
Re: Capacitor
06/06/2022 7:16 AM
thank you very much for your reply
Re: Capacitor
06/06/2022 7:17 AM
How did the telephone call between the original equipment manufacturer and the <...we...> go?
Re: Capacitor
06/06/2022 7:21 AM
What you don't know CAN hurt you in some cases.
Re: Capacitor
06/06/2022 9:14 AM
It certainly has the capacity to do so...
Re: Capacitor
06/06/2022 11:06 AM
Very good,2 dogs.
Re: Capacitor
06/06/2022 6:03 PM
Is '2 dogs' his spirit name?
Re: Capacitor
06/07/2022 5:48 AM
No,it is the name of a spirit:Two Dogs Lemon Brew,a lemon based alcoholic beverage originating in Australia.A very sharp drink,like the answer.
Good Answers: 54
Re: Capacitor
06/06/2022 9:51 PM
In cases of deciding whether a replacement part will work, you need to consider what the original part was used for.
In electronic circuits, if the capacitor is used for timing, you absolutely need to used the exact same spec. If you use a different spec, you need to have something to adjust the timing or you'll need to change some other parts to get the exact, same timing.
If it's used for power rail filtering, you might get away with a slight difference in spec if the circuit is a low frequency circuit (say for audio). In high frequency applications, it might have an effect, particularly with noise or interference.
Having said all that, I would have to say that the difference in capacitance of your replacement part is too large no matter what the application is.
In short, no, I don't think you can use it.
regards,
Vulcan
Re: Capacitor
06/07/2022 5:23 AM
Ah: Generator circuit breaker?
Do you have a circuit diagram; or can you take a picture so that we can reverse engineer the circuit.
What sort of circuit is it in?
Re: Capacitor
06/07/2022 7:21 AM
<...can we use it...>
CR4 is not a permission-giving entity.
Re: Capacitor
06/08/2022 4:08 AM
He didn't say "May we use it?" he said "Can we use it?": which opens up a totally different kettle of red herrings .
Re: Capacitor
06/09/2022 10:29 AM
Ah! That explains things, because the two verbs are interchanged without due care in modern parlance.
<... kettle of red herrings...> Burpy pardloes.
Location: 3rd rock from the sun,a small dust mote,in a small insignificant spiral galaxy referred to locally as the Milky Way
Re: Capacitor
06/07/2022 3:56 PM
No ...Effect will be expected consequences,but not good.
There is no darkness except for ignorance..Shakespeare
Good Answers: 88
Re: Capacitor
06/08/2022 12:14 PM
Assuming your GCB you mean Generator circuit braker, the capacitor is there to absorb some of the system inductance stored energy in order to avoid contact arcing damage. Well, those components are chosen with high safety margins and since it failed some underlying problems can be hiding like bad contacts, chattering etc. I'd start from there, and choose a same or higher voltage rated cap if possible. Choises change whether we are talking for DC or AC gen. S.M.
Re: Capacitor
06/08/2022 5:44 PM
Re: Capacitor
06/11/2022 9:34 AM
Re: Capacitor
06/12/2022 2:09 PM
The surge arrestor acts like a dead short when the voltage exceeds a certain threshold.
The capacitor acts like a resistor to limit the amount of current through the surge arrestor.The resistance increases as the frequency of the surge increases,so a very fast surge(which is normal) will pass less current through the surge arrestor.It is a sacrificial device intended to fail to prevent a catastrophic failure of the surge arrestor.If the capacitor failed,the surge arrestor probably also failed.
It should be replaced with the same type and rating to preserve the design integrity of the surge arrestor circuit.
Chances are pretty high that the surge arrestor is also damaged.
I suggest replacing both to prevent compromising protection of downstream components.
Good Answers: 22
Re: Capacitor
06/10/2022 8:08 AM
Kasrop,
Surge Capacitor and Surge Arrester together are sized and calibrated to protect generator against transferred surges from the grid (through Unit Transformer).
It is very rare to see this capacitor failure and could be an indicator of a bigger problem. Hence, it is important to investigate the capacitor failure before making the decision on replacement so that the incident is not repeated.
Also, an incorrect size of the capacitor could endanger the generator itself (which is much more expensive).
I am sure generator manufacturer too will be interested to analyse the failure. Please do get in touch.
(The generator manufacturer takes in to account grid parameters as well as generator transformer parameters for sizing the Surge protection assembly).
Likely causes of capacitor failures are,
1) ageing
2) Manufacturing defect
3) incorrect sizing / Changed input parameters
Raghunath