Outgoing Feeder RCBO Trips During UPS Normal Source Restoration

12/28/2023 7:34 AM

Good day to all,

I would like to bring this to your kind attention and request your valuable response. Every week there is routine testing of our 3phase UPS 20kVA which fed to a 3phase DB having 15nos. single phase RCBOs. The loads are IT servers.

The testing procedure is as follows; The main incomer of the UPS will be disconnected manually and the load will run on the ups battery for around 10 minutes, and the main source will be restored after that, hence ensuring that the UPS is healthy, this is the normal routine for 10 years old ups during these years.

last week when the ups people did the same routine test, 3nos. outgoing single-phase RCBOs in the DB have tripped instantly. This made a disconnection of load and made the ups meaningless.

We checked the outgoing circuit for any earth leakage or any faulty, but couldn't find anything abnormal. Then we repeated the ups test by disconnecting the main power and restoring it after some time, but nothing happened. The ups supplier says that its not ups issue and its related to outgoing load only. I am afraid this may happen later also. I regret that I couldn't trace the reason and I request your valuable reply. Thank you all

Register to Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.

Good Answers:

These comments received enough positive votes to make them "good answers".

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
2
Guru

Join Date: Mar 2007
Location: by the beach in Florida
Posts: 33392
Good Answers: 1817
#1

Re: Outgoing Feeder RCBO Trips During UPS Normal Source Restoration

12/28/2023 1:19 PM

I would check the breakers, monitor line amperage, and breaker temperatures....they do wear out...have replacements ready...or it could have been a momentary short of unknown origin....damn rats...

__________________
All living things seek to control their own destiny....this is the purpose of life
Register to Reply Good Answer (Score 2)
Commentator

Join Date: Dec 2011
Posts: 96
Good Answers: 2
#7
In reply to #1

Re: Outgoing Feeder RCBO Trips During UPS Normal Source Restoration

12/29/2023 11:45 PM

thankyou

Register to Reply
Power-User

Join Date: Jan 2010
Location: Hyderabad
Posts: 343
Good Answers: 22
#2

Re: Outgoing Feeder RCBO Trips During UPS Normal Source Restoration

12/29/2023 1:35 AM

The RCBO can trip for three reasons:

1. A fault giving rise to overcurrent

2. Earth leakage

3. Faulty Circuit Breaker

4. Inrush current

You ruled out earth leakage by testing those three circuits. Also, possibility of fault or earth leakage happening in three circuits simultaneously is very very unusual and hence can be ruled out.

Faulty Circuit breaker is a possibility, but in three circuits simultaneously???

Inrush current is possible depending on the type of load, the status of UPS voltage (in other words what is the remaining capacity of the UPS battery) just before mains was restored - you may like to look into. I presumed the trip took place just when the mains was switched on. Also, I presume the battery is 10 years old and hence could have capacity issues.

__________________
Raghunath
Register to Reply Score 1 for Good Answer
Commentator

Join Date: Dec 2011
Posts: 96
Good Answers: 2
#8
In reply to #2

Re: Outgoing Feeder RCBO Trips During UPS Normal Source Restoration

12/29/2023 11:46 PM

thankyou

Register to Reply
Guru

Join Date: Jul 2016
Posts: 1375
Good Answers: 105
#3

Re: Outgoing Feeder RCBO Trips During UPS Normal Source Restoration

12/29/2023 2:34 AM

What phase(s) were the three offending breakers connected to ?

Why are RCBOs applied in this case?

Register to Reply
Commentator

Join Date: Dec 2011
Posts: 96
Good Answers: 2
#5
In reply to #3

Re: Outgoing Feeder RCBO Trips During UPS Normal Source Restoration

12/29/2023 11:37 PM

thank you, 2 loads were in r phase, 1 was in blue phase, rcbos are always preferred for critical loads because if we provide common elcb for the complete db, the complete db will be failed during earth leakage in any one of the circuits. so ups are always essential load hence rcbos.

Register to Reply
Guru

Join Date: Jul 2016
Posts: 1375
Good Answers: 105
#9
In reply to #5

Re: Outgoing Feeder RCBO Trips During UPS Normal Source Restoration

12/30/2023 12:47 AM

It would be interesting to find out if those 3 circuits have any particular distinction over the others, cable construction, length, loads served. You could perhaps move the breakers to see if the problem follows the breaker, or the circuit.

I expect that the tripping is likely to happen again, and maybe has something to do with your particular RCBO sensor circuit and the THD (Total Harmonic Distortion) of your UPS inverter, possibly 3rd harmonic. The charging capacitance of your cables, the phase firing at just the right time, is possibly enough to produce apparent current in the return leg that is not sensed in the supply. This is a common occurrence when long cables are used with Ground Fault Circuit Interrupters in the US, or newer Inverter Generators, engine driven inverter used to reduce part load fuel consumption. Cable capacitance is the driving factor.

Assuming your power system is solidly grounded, not in a wet area frequented by people, any circuit breaker will easily clear a ground fault. You don’t need an RCBO to clear a ground fault from your panel. Your breaker is there to protect the wire, and unless you have a demonstrated risk of an arcing ground fault in your cables returning outside of the cable jacket, RCBOs may be technical over kill. Maybe you can do a formal risk analysis, and decide that the benefit of the over-application of technology comes with little to no benefit.

If you are uncomfortable with perhaps overriding your local codes, then I would investigate replacement RCBOs that use a different technology to sense ground fault current.

Register to Reply
Guru

Join Date: May 2010
Location: Metro.Manila, Philippines.
Posts: 1271
Good Answers: 27
#4

Re: Outgoing Feeder RCBO Trips During UPS Normal Source Restoration

12/29/2023 2:50 PM

I'm kind of wondering why the battery bank's condition has not been first established, validated and ascertained as part of the weekly routine testing or PM process prior to disconnecting the UPS from the mains...

I believe that should be the very first step as part of your QA processes..

__________________
vsar
Register to Reply
Commentator

Join Date: Dec 2011
Posts: 96
Good Answers: 2
#6
In reply to #4

Re: Outgoing Feeder RCBO Trips During UPS Normal Source Restoration

12/29/2023 11:39 PM

battery bank voltage usually checked in routine test and noted. there was nothing abnormal.

Register to Reply
Guru

Join Date: May 2010
Location: Metro.Manila, Philippines.
Posts: 1271
Good Answers: 27
#11
In reply to #6

Re: Outgoing Feeder RCBO Trips During UPS Normal Source Restoration

12/30/2023 9:43 AM

Battery charge condition changes and can be noted when and while in a fully loaded condition.

__________________
vsar
Register to Reply
Guru

Join Date: May 2010
Location: Metro.Manila, Philippines.
Posts: 1271
Good Answers: 27
#12
In reply to #11

Re: Outgoing Feeder RCBO Trips During UPS Normal Source Restoration

12/30/2023 10:19 AM

As the input power source, any imbalance especially in a polyphase application can produce unpredictable output behavior when fully loaded.

__________________
vsar
Register to Reply
Guru
United Kingdom - Member - Indeterminate Engineering Fields - Control Engineering - New Member

Join Date: Jan 2007
Location: In the bothy, 7 chains down the line from Dodman's Lane level crossing, in the nation formerly known as Great Britain. Kettle's on.
Posts: 32175
Good Answers: 839
#13
In reply to #12

Re: Outgoing Feeder RCBO Trips During UPS Normal Source Restoration

01/03/2024 7:23 AM

Please enlighten as to how an <...imbalance...> can cause such current in the circuit protective conductor as to cause <...Outgoing Feeder RCBO Trips....>?

__________________
"Did you get my e-mail?" - "The biggest problem in communication is the illusion that it has taken place" - George Bernard Shaw, 1856
Register to Reply
Guru

Join Date: May 2010
Location: Metro.Manila, Philippines.
Posts: 1271
Good Answers: 27
#14
In reply to #13

Re: Outgoing Feeder RCBO Trips During UPS Normal Source Restoration

01/03/2024 9:33 AM

Basically 3 single phase inverters are used, wired and configured for 3-phase operation to provide uninterrupted source of power.. and each inverter is backed by a DC source to ensure continues operations.. The battery banks in turn are being maintained and kept charged by the commercially available power source..

Hence as a result any imbalance in the battery bank conditions will be reflected onto the converted power output of the 3 phase system..that can trigger any of the circuit breakers to trip..

__________________
vsar
Register to Reply Score 1 for Good Answer
Guru

Join Date: Jul 2016
Posts: 1375
Good Answers: 105
#15
In reply to #14

Re: Outgoing Feeder RCBO Trips During UPS Normal Source Restoration

01/03/2024 11:39 AM

Isn’t it likely that there is only one battery bank?

Register to Reply
Guru

Join Date: May 2010
Location: Metro.Manila, Philippines.
Posts: 1271
Good Answers: 27
#16
In reply to #15

Re: Outgoing Feeder RCBO Trips During UPS Normal Source Restoration

01/03/2024 11:58 AM

Using a single battery bank power supply I believe would be appropriate depending upon the load applications and UPS rated power handling capacity..

__________________
vsar
Register to Reply
Guru
United Kingdom - Member - Indeterminate Engineering Fields - Control Engineering - New Member

Join Date: Jan 2007
Location: In the bothy, 7 chains down the line from Dodman's Lane level crossing, in the nation formerly known as Great Britain. Kettle's on.
Posts: 32175
Good Answers: 839
#17
In reply to #16

Re: Outgoing Feeder RCBO Trips During UPS Normal Source Restoration

01/04/2024 9:06 AM

The question of current in the circuit protective conductor remains unresolved, then.

__________________
"Did you get my e-mail?" - "The biggest problem in communication is the illusion that it has taken place" - George Bernard Shaw, 1856
Register to Reply
Guru

Join Date: May 2010
Location: Metro.Manila, Philippines.
Posts: 1271
Good Answers: 27
#18
In reply to #17

Re: Outgoing Feeder RCBO Trips During UPS Normal Source Restoration

01/04/2024 10:12 AM

In my opinion any minor UPS phase voltage differences at the input side in my view can be reflected as current imbalance at the output side which may also be just enough to trigger the tripping of the circuit breaker...

It is difficult not to do any speculation since the actual circuit diagram and load distribution for the phases were not provided by the OP..

__________________
vsar
Register to Reply
Guru

Join Date: Jul 2016
Posts: 1375
Good Answers: 105
#19
In reply to #18

Re: Outgoing Feeder RCBO Trips During UPS Normal Source Restoration

01/04/2024 10:57 AM

The 3 phase currents may be unbalanced, but a single phase circuit, either line to line or line to neutral would not be able to detect it. Apparent current due to charging of cable distributed capacitance to ground can fool the sensors. But occurring once in a great while is the mystery.

Register to Reply
Guru
United Kingdom - Member - Indeterminate Engineering Fields - Control Engineering - New Member

Join Date: Jan 2007
Location: In the bothy, 7 chains down the line from Dodman's Lane level crossing, in the nation formerly known as Great Britain. Kettle's on.
Posts: 32175
Good Answers: 839
#21
In reply to #19

Re: Outgoing Feeder RCBO Trips During UPS Normal Source Restoration

01/05/2024 3:59 AM

By definition, <...a single phase circuit...> fed from a 3-phase supply is <...unbalanced...>. The query is that of why imbalance would cause an <...RCBO...> to trip on earth/ground current, which needs to be expressed meaningfully. It is commonplace for <...RCBO...>s to be installed on single phase circuits without tripping on earth/ground current.

__________________
"Did you get my e-mail?" - "The biggest problem in communication is the illusion that it has taken place" - George Bernard Shaw, 1856
Register to Reply
Commentator

Join Date: Dec 2011
Posts: 96
Good Answers: 2
#23
In reply to #19

Re: Outgoing Feeder RCBO Trips During UPS Normal Source Restoration

01/07/2024 6:52 AM

yes, i think so, if its a 3phase rcbo there is a chance of tripping due to unbalance. but here all the outgoings are single phase only

Register to Reply
Guru

Join Date: May 2010
Location: Metro.Manila, Philippines.
Posts: 1271
Good Answers: 27
#25
In reply to #23

Re: Outgoing Feeder RCBO Trips During UPS Normal Source Restoration

01/09/2024 11:05 AM

Single phase loading distributions and scheduling may need to be factored in and considered so as not to affect and introduce much imbalance to the 3phase inverter system.

__________________
vsar
Register to Reply
Guru

Join Date: Jul 2016
Posts: 1375
Good Answers: 105
#26
In reply to #23

Re: Outgoing Feeder RCBO Trips During UPS Normal Source Restoration

01/09/2024 10:17 PM

Unbalanced phase loads will not trip a 3 phase RCBO, whether 3 wire or 4 wire design, unless there are significant harmonics not accounted for in the breaker design.

All load currents are sensed and summed.

Register to Reply Score 1 for Good Answer
Guru
United Kingdom - Member - Indeterminate Engineering Fields - Control Engineering - New Member

Join Date: Jan 2007
Location: In the bothy, 7 chains down the line from Dodman's Lane level crossing, in the nation formerly known as Great Britain. Kettle's on.
Posts: 32175
Good Answers: 839
#20
In reply to #17

Re: Outgoing Feeder RCBO Trips During UPS Normal Source Restoration

01/05/2024 3:54 AM

In a TN-C-S system, for example, it is normal to have current in the circuit protective conductor if a neutral conductor upstream of the installation is broken. Such currents present <...RCBO...>s with the conditions needed to trip on earth current.

That is why the services of a qualified local Electrician would be of value here. There is a lot that needs investigating.

Diverted Neutral Current Demonstration - Normal, Open CNE, Current Circulation (Part 2) (youtube.com)

__________________
"Did you get my e-mail?" - "The biggest problem in communication is the illusion that it has taken place" - George Bernard Shaw, 1856
Register to Reply
Guru

Join Date: Jul 2016
Posts: 1375
Good Answers: 105
#22
In reply to #20

Re: Outgoing Feeder RCBO Trips During UPS Normal Source Restoration

01/05/2024 9:13 PM

Other than in US dryers and stoves grandfathered in, where is TN-C-S a good idea? That YouTube video without a wiring diagram was not very helpful. Did I miss it?

Register to Reply
Guru
United Kingdom - Member - Indeterminate Engineering Fields - Control Engineering - New Member

Join Date: Jan 2007
Location: In the bothy, 7 chains down the line from Dodman's Lane level crossing, in the nation formerly known as Great Britain. Kettle's on.
Posts: 32175
Good Answers: 839
#24
In reply to #22

Re: Outgoing Feeder RCBO Trips During UPS Normal Source Restoration

01/09/2024 5:06 AM

The <...wiring diagram...> is in part 1.

__________________
"Did you get my e-mail?" - "The biggest problem in communication is the illusion that it has taken place" - George Bernard Shaw, 1856
Register to Reply Score 1 for Good Answer
Guru
United Kingdom - Member - Indeterminate Engineering Fields - Control Engineering - New Member

Join Date: Jan 2007
Location: In the bothy, 7 chains down the line from Dodman's Lane level crossing, in the nation formerly known as Great Britain. Kettle's on.
Posts: 32175
Good Answers: 839
#10

Re: Outgoing Feeder RCBO Trips During UPS Normal Source Restoration

12/30/2023 7:46 AM

Question the need for <...RCBO...>s on the downstream circuits if all that is being fed are <...IT servers...>. As well as overload the <...RCBO...> is there for personnel protection and if there is no risk of that prospect being needed then identically rated miniature circuit breakers [MCB] may be appropriate substitutes.

It may be that, if similar behaviour is exhibited by a temporarily-installed MCB, then there needs to be a review of the loads, the cabling, and the MCB characteristics for the purposes of selecting appropriately-rated circuit protective devices for the circuits in question.

If in doubt, consult a local qualified Electrician.

__________________
"Did you get my e-mail?" - "The biggest problem in communication is the illusion that it has taken place" - George Bernard Shaw, 1856
Register to Reply Score 1 for Good Answer
Register to Reply 26 comments

Good Answers:

These comments received enough positive votes to make them "good answers".

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Copy to Clipboard

Users who posted comments:

PWSlack (6); raghun (1); roykav (5); rwilliams (6); SolarEagle (1); vsar (7)