RCCB Trips While ATS Source Changes from Normal to Generator

01/07/2024 11:38 PM

Hi, good day to everyone,

We are facing an issue in the newly installed emergency system. there is 4nos. 1600kVA, 415V transformer fed MLTPs fed to MSB then DBs. the DBs are provided with a 40A, 30mA RCCB as incomer for common earth leakage protection. normally the MLTPs are fed from normal source (transformers), during normal source failure the ATS will give start signal to generators and once the generator supply reaches the ATS, the ATS will transfer the load to the generator source supply. The issue is while the ATS switch to the generator supply (that time bus will be dead) the incomer RCCB of the DBs tripping.

The load of the DBs are almost all single phase power. RCCB rating 30mA, 40A.

The generators 415V - 6nos. x 1250kVA caterpillar synchronized.

Experiments done; RCCBs are found ok, when we changed the RCCB to 300mA no any tripping. means the leakage is below 300mA.

Thank you for your time. please let me know if further clarifications are needed.

Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Guru

Join Date: Mar 2007
Location: by the beach in Florida
Posts: 33392
Good Answers: 1817
#1

Re: RCCB TRIPS WHILE ATS SOURCE CHANGES FROM NORMAL TO GENERATOR

01/08/2024 12:57 AM

Perhaps an SST....In any case you need an EE to make a determination as to the solution...The 300mA choice might be acceptable in this setting...

https://onlinelibrary.wiley.com/doi/full/10.1002/2050-7038.12996

__________________
All living things seek to control their own destiny....this is the purpose of life
Reply
Anonymous Poster #1
#2
In reply to #1

Re: RCCB TRIPS WHILE ATS SOURCE CHANGES FROM NORMAL TO GENERATOR

01/08/2024 1:17 AM

hope so sir, also need to know the cause of tripping. it doesn't happen during normal source restoration. if sst it might happen that time also. during normal source restoration same switching is happening in the ATS. ie transfer from generator source to normal source. the ATS manufacturer Zenith/GE. 4pole. neutral type- last break-first connect.

Reply
Guru

Join Date: Mar 2007
Location: by the beach in Florida
Posts: 33392
Good Answers: 1817
#3
In reply to #2

Re: RCCB TRIPS WHILE ATS SOURCE CHANGES FROM NORMAL TO GENERATOR

01/08/2024 1:59 AM

When's the last time you megged out your gen windings? What are the ages? Might need a redip...

__________________
All living things seek to control their own destiny....this is the purpose of life
Reply
Anonymous Poster #1
#6
In reply to #3

Re: RCCB TRIPS WHILE ATS SOURCE CHANGES FROM NORMAL TO GENERATOR

01/08/2024 8:00 AM

Its new installation, there is reverese power relay is provided for each genset, so no chance of reverse feed. everything done pre-commissioning. commissioning also done 6month back. while now only started monthly testing with on load. initially there was not much load i think thts y there was no tripping that time.

Reply
Guru
United Kingdom - Member - Indeterminate Engineering Fields - Control Engineering - New Member

Join Date: Jan 2007
Location: In the bothy, 7 chains down the line from Dodman's Lane level crossing, in the nation formerly known as Great Britain. Kettle's on.
Posts: 32175
Good Answers: 839
#7
In reply to #6

Re: RCCB TRIPS WHILE ATS SOURCE CHANGES FROM NORMAL TO GENERATOR

01/08/2024 8:55 AM

The Commissioning Engineer's name will be on the commissioning documentation. Please describe the outcome of discussing this equipment's new behavio(u)r with this individual?

__________________
"Did you get my e-mail?" - "The biggest problem in communication is the illusion that it has taken place" - George Bernard Shaw, 1856
Reply
Power-User

Join Date: Jan 2010
Location: Hyderabad
Posts: 343
Good Answers: 22
#8
In reply to #2

Re: RCCB TRIPS WHILE ATS SOURCE CHANGES FROM NORMAL TO GENERATOR

01/08/2024 11:43 PM

"ATS manufacturer Zenith/GE. 4pole. neutral type- last break-first connect.." - this suggests that the generator is connected first before normal incomer is opened. To me, it seems the neutrals of both transformer and the generator are paralleled briefly at the time of changeover. Generator produces third harmonics required for its magnetisation. When the neutrals are paralleled, third harmonics being similar like zero sequence currents circulate through earth and cause RCCB maloperation.

Please check and ensure that the 'break' is complete before 'make' happens.

Generally speaking, 30mA is too sensitive for a DB incomer. 30mA is suggested for an individual circuit. 100mA or 300mA (depending on number of circuits connected) is more appropriate for the incomer. I mentioned this because the healthy leakage just before changeover could have been close to 30mA and the disturbance during changeover could be causing RCCB maloperation.

__________________
Raghunath
Reply
Anonymous Poster #1
#9
In reply to #8

Re: RCCB TRIPS WHILE ATS SOURCE CHANGES FROM NORMAL TO GENERATOR

01/09/2024 1:39 AM

ATS is open transition only. Neutral only provided the last break and first make, which ensure the neutral connection to the system, hence the earth and zero potential before the phase connects to the system. it is confirmed that there is no parallel operation in the ATS which is why 4 pole is used.

Reply
Guru
United Kingdom - Member - Indeterminate Engineering Fields - Control Engineering - New Member

Join Date: Jan 2007
Location: In the bothy, 7 chains down the line from Dodman's Lane level crossing, in the nation formerly known as Great Britain. Kettle's on.
Posts: 32175
Good Answers: 839
#4

Re: RCCB TRIPS WHILE ATS SOURCE CHANGES FROM NORMAL TO GENERATOR

01/08/2024 6:03 AM

<...further clarifications are needed....>

Well, some idea of the meaning of those TLAs and FLAs would be helpful for those looking to learn from this thread.

__________________
"Did you get my e-mail?" - "The biggest problem in communication is the illusion that it has taken place" - George Bernard Shaw, 1856
Reply Score 1 for Good Answer
Guru
United Kingdom - Member - Indeterminate Engineering Fields - Control Engineering - New Member

Join Date: Jan 2007
Location: In the bothy, 7 chains down the line from Dodman's Lane level crossing, in the nation formerly known as Great Britain. Kettle's on.
Posts: 32175
Good Answers: 839
#5

Re: RCCB Trips While ATS Source Changes from Normal to Generator

01/08/2024 7:20 AM

Please let the forum know the outcome of talking to these people.

__________________
"Did you get my e-mail?" - "The biggest problem in communication is the illusion that it has taken place" - George Bernard Shaw, 1856
Reply
Guru

Join Date: Jul 2016
Posts: 1375
Good Answers: 105
#10

Re: RCCB Trips While ATS Source Changes from Normal to Generator

01/09/2024 3:09 AM

Without the power system grounding detail, it will be difficult to nail down the possible causes.

I agree with raghun that 30mA RCCB as a main for a DB distribution board we think maybe, is a poor choice. The RCCBs if applied at all should be on your selected load breakers. The 3rd harmonic present when paralleling rotating machinery grounded in multiple places can be enough to cause a ground resistor to sizzle. I’m impressed you could keep the power system running at all.

The distributed cable capacitance is a fine source of apparent ground fault current, that is called also charging current, and there are references published which allow you to estimate the magnitude. A typical industrial system at 480 volts 1500 to 2000 kVA might be less than 10 amperes, I have measured 2-3 Amperes, milliamperes, Ha!

It is unlikely you can achieve any sort of system selectivity with cascaded RCCBs, and since ground faults are the most common fault, you are sentencing your power system reliability and availability to a very low score.

And some extra typing explaining all of your TLAs may actually get some good answers from people who are tired of having to look up every TLA and FLA they run across, and then decide TL;DR.

Reply
Reply to Forum Thread 10 comments

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!