Hi, good day to everyone,
We are facing an issue in the newly installed emergency system. there is 4nos. 1600kVA, 415V transformer fed MLTPs fed to MSB then DBs. the DBs are provided with a 40A, 30mA RCCB as incomer for common earth leakage protection. normally the MLTPs are fed from normal source (transformers), during normal source failure the ATS will give start signal to generators and once the generator supply reaches the ATS, the ATS will transfer the load to the generator source supply. The issue is while the ATS switch to the generator supply (that time bus will be dead) the incomer RCCB of the DBs tripping.
The load of the DBs are almost all single phase power. RCCB rating 30mA, 40A.
The generators 415V - 6nos. x 1250kVA caterpillar synchronized.
Experiments done; RCCBs are found ok, when we changed the RCCB to 300mA no any tripping. means the leakage is below 300mA.
Thank you for your time. please let me know if further clarifications are needed.