Line to Neutral Fault on TN-S System

01/22/2024 7:05 AM

Does the RCD trip for line to neutral fault on TN-S system? (or)

Does it trip only for line to earth fault on TN-S system?

Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.

Good Answers:

These comments received enough positive votes to make them "good answers".
2
Guru

Join Date: Aug 2005
Location: Hemel Hempstead, UK
Posts: 5826
Good Answers: 322
#1

Re: Line to Neutral Fault on TN-S System

01/22/2024 7:40 AM

No: a live to neutral fault just looks like a load.

Of course, if the fault load is high other safety devices should react.

__________________
If you spend all your time looking for people and things to complain about: trust me, you will find plenty to complain about.
Reply Good Answer (Score 2)
3
Guru
United Kingdom - Member - Indeterminate Engineering Fields - Control Engineering - New Member

Join Date: Jan 2007
Location: In the bothy, 7 chains down the line from Dodman's Lane level crossing, in the nation formerly known as Great Britain. Kettle's on.
Posts: 32175
Good Answers: 839
#2

Re: Line to Neutral Fault on TN-S System

01/22/2024 11:10 AM

A1) An <...RCD...> won't; see GA #1⇑. A residual current breaker overload [RCBO] will, however, on the overcurrent function and not the earth current function.

A2) Both <...RCD...> and RCBO will also trip on neutral-to-earth fault.

<...TN-S...>

The earthing arrangement deployed is irrelevant in this discussion.

__________________
"Did you get my e-mail?" - "The biggest problem in communication is the illusion that it has taken place" - George Bernard Shaw, 1856
Reply Good Answer (Score 3)
Power-User

Join Date: Jan 2010
Location: Hyderabad
Posts: 343
Good Answers: 22
#3

Re: Line to Neutral Fault on TN-S System

01/23/2024 2:00 AM

RCD will not trip for Line-to-Neutral fault as the device takes in the neutral current (along with line current) for summation.

Earth involvement in fault is necessary for RCD to trip.

__________________
Raghunath
Reply
Guru

Join Date: May 2010
Location: Metro.Manila, Philippines.
Posts: 1271
Good Answers: 27
#4

Re: Line to Neutral Fault on TN-S System

01/23/2024 8:36 AM

On a TN-S system generally any "Fault" with respect to the ground as the safety reference point of the earthing mechanisms should trip any of the protective circuit devices incorporated in the system...

Faults like any electrical safety related earth referenced fault that can be due to like a high leakage current, an abnormally drawn current overload or lightning induced surge current, etc..

__________________
vsar
Reply
Reply to Forum Thread 4 comments

Good Answers:

These comments received enough positive votes to make them "good answers".
Copy to Clipboard

Users who posted comments:

PWSlack (1); raghun (1); Randall (1); vsar (1)

Previous in Forum: Earth Rods and Inspection Pits   Next in Forum: TVS in Series

Advertisement