Calibration for PSV Mounted on CO2 Gas Cylinders

02/21/2024 11:05 PM

Good morning, how you are? hope you are doing very well. I have query regarding calibration of PSV mounted on CO2 Gas Cylinders. We did a pneumatic test at the set pressure of 140 bar, and the test failed. the PSV was serviced and cleaned but again failed in the test.

inlet dia is 10 mm. the test machine minimum orific dia is 22 mm.

However, if we test by water, which is different than the service medium, the test is passed.

can you support in find out the reason behind this failure?

Regards,

Register to Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.
Guru

Join Date: Mar 2007
Location: by the beach in Florida
Posts: 33392
Good Answers: 1817
#1

Re: Calibration for PSV mounted on CO2 Gas Cylinders

02/21/2024 11:26 PM

Sounds like your gas gauge may be slightly out of calibration...raise the pressure of the gas a bit and it should pop off....

__________________
All living things seek to control their own destiny....this is the purpose of life
Register to Reply
Guru
United Kingdom - Member - Indeterminate Engineering Fields - Control Engineering - New Member

Join Date: Jan 2007
Location: In the bothy, 7 chains down the line from Dodman's Lane level crossing, in the nation formerly known as Great Britain. Kettle's on.
Posts: 32175
Good Answers: 839
#2

Re: Calibration for PSV mounted on CO2 Gas Cylinders

02/22/2024 3:06 AM

Assuming the abbreviation <...PSV...> means "pressure sustaining valve" or "pressure safety valve", what are the implications of a <...failed test...>; the sorts of questions to ask within the facility are:

  • How does this particular valve compare with others that may be present at the facility? What is different about this one compared to others?
  • Is it worth having a replacement new spare on standby? What is the lead time on its arrival?
  • Is it worth sending the valve in question away for specialist refurbishment and return?
  • What is the impact of operating the process at a different pressure, or not operating the process at all?
  • Is the test itself valid or would a different protocol be appropriate?
__________________
"Did you get my e-mail?" - "The biggest problem in communication is the illusion that it has taken place" - George Bernard Shaw, 1856
Register to Reply
Guru

Join Date: Jul 2016
Posts: 1367
Good Answers: 105
#3

Re: Calibration for PSV Mounted on CO2 Gas Cylinders

02/22/2024 11:32 PM

Does the method of test deliver more force on the sensing element due to the mass of the test media?

Does the incompressibility of the test fluid somehow deliver more actuating force to the sensing element?

Register to Reply
Guru

Join Date: May 2010
Location: Metro.Manila, Philippines.
Posts: 1269
Good Answers: 27
#4

Re: Calibration for PSV Mounted on CO2 Gas Cylinders

02/23/2024 8:56 AM

"can you support in find out the reason behind this failure?"

Pneumatic pressure testing is different than hydrostatic pressure testing is the reasoning for the different results....

Gas is compressible while the liquid media is not compressible... you may increase the gas pressure to match and equalize the pressure exerted by the liquid...

__________________
vsar
Register to Reply
Guru

Join Date: Apr 2009
Location: USA, Florida
Posts: 1595
Good Answers: 125
#5

Re: Calibration for PSV Mounted on CO2 Gas Cylinders

02/23/2024 1:42 PM

If the PSV is non-adjustable, replace it. A potential for failing is why testing is required.

__________________
An obstacle is something you see when you take your eyes off the goal.
Register to Reply
Guru
Philippines - Member - New Member Engineering Fields - Instrumentation Engineering - New Member Engineering Fields - Control Engineering - Who am I?

Join Date: Oct 2006
Location: Northern Mindanao, Philippines
Posts: 2147
Good Answers: 53
#6

Re: Calibration for PSV Mounted on CO2 Gas Cylinders

02/23/2024 7:18 PM

Works with liquid but doesn't work with gas...hmmm.

There are PSVs for liquids and PSVs for gases. There are PSVs for specific types of gases. Maybe you have the wrong type of PSV.

Just a thought.

regards,

Vulcan

__________________
Miscommunication: when what people heard you say differs from what you said. Make yourself understood.
Register to Reply
Register to Reply 6 comments
Copy to Clipboard

Users who posted comments:

PWSlack (1); rwilliams (1); SolarEagle (1); vsar (1); Vulcan (1); WJMFIRE (1)

Previous in Forum: Wood to Metal   Next in Forum: Highly Backdrivable, Fast and High Torque Manipulator

Advertisement