Anonymous Poster

HADJI APPLIANCES

12/11/2007 10:14 PM

Just recently got back from Iraq after a 7 month stint with my Guard unit. As an engineer our job was to bulid the first base back in Feb. 07 for the troop surge. All of the American electrical assets (power gen) were typically 120/208 3ph 4w...unfortunately we sometimes had to feed Hadji (Iraqi for "man") appliances which were 230v single phase (one hot leg of 230v). The way we made this work was to feed the appliance, i.e., clippers, coolers, etc, with two 120v legs instead of (1) 230v leg and (1) neut. This seemed to work fine?! What, if any would be the long term problems associated with doing this???? MSGT. Martin Philpott

Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.

Good Answers:

These comments received enough positive votes to make them "good answers".

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Guru
Canada - Member - If there is a way to screw someting up, there is someone to do so! Safety - Hazmat - New Member

Join Date: Mar 2007
Location: Iqaluit, NU. Canada
Posts: 1854
Good Answers: 140
#1

Re: HADJI APPLIANCES

12/11/2007 10:36 PM

Well... not much. If your system was 120/208 3ph 4w what you were sending to those Hadji appliances was 208 volts which is close enough.

__________________
Joe Contractor to Electrical Inspector, "What do you mean you are going to make me follow the code?".
Reply
Guru

Join Date: Aug 2007
Location: Earth - I think.
Posts: 2143
Good Answers: 165
#2

Re: HADJI APPLIANCES

12/12/2007 12:19 AM

Load balancing and safety.

Since you are talking about a 3 phase system, your equipment was designed to use all 3 phases (L1,L2,L3, Neutral) in a balanced manner. If the Hadji loads were of a small enough current draw, that isn't a big deal. If the current draw on one leg is too large (in relation to the others), then you will run into problems. Usually the safeties will kick-in and kill the generator.

The other thing is safety. Since each phase has a potential above ground/neutral, it could give somebody a pretty bad jolt. An itermediary transformer would be a better way to go, but hey, it's a war zone, and they are lucky to be getting any power.

P.S. Semper Fi! And THANK YOU, God Bless!

__________________
TANSTAAFL (If you don't know what that means, Google it - yourself)
Reply Score 1 for Good Answer
4
Guru
New Zealand - Member - Interested in everything- see my Profile please APIX Pilot Plant Design Project - Member - Member Engineering Fields - Electrical Engineering - Member Engineering Fields - Power Engineering - Member Engineering Fields - Civil Engineering - Member Hobbies - Musician - Autoharp and Harmonica Hobbies - Hunting - Member Hobbies - Fishing - Member

Join Date: Nov 2007
Location: Christchurch, (The Garden City), South Island, New Zealand
Posts: 4395
Good Answers: 230
#3

Re: HADJI APPLIANCES

12/12/2007 2:35 AM

Hello Martin,

There should be no trouble, as stated above, providing the load was balanced fairly equally across all secondary windings.

However, all appliances using that 208 volt secondary should have a dual-pole switch, to properly isolate both legs of the supply.

My suggestion would be to earth that secondary neutral point, and also connect it with an extra wire to the metallic chassis or frame of each load appliance.

I don't know what your local arrangements are, and presume in the hot desert conditions, an earth stake would be of little use.

If your arrangements are more than immediately temporary, an earth mat under the appliances, bonded to the appliance chassis would also be useful to prevent stray shocks.

If you are in permanent buildings, and those have steel reinforced concrete or steel portal framing, bond all exposed metal, stainless steel bench-tops, appliance frames/chassis etc, to that star point.

In that way, the shock potential is minimised.

You could also use ELCB protection, but if your floor is desert sand, that is not going to work, at all.

Here in New Zealand, we use 400v 3 phase/230v single phase MEN (Multiple Earthed Neutral System), where every switchboard has connection to a local earth stake. NZ soils are fairly conductive, so that works fine here.

Please advise here further, your progress, thank you....

__________________
"The number of inventions increases faster than the need for them at the time" - SparkY
Reply Good Answer (Score 4)
Guru
Popular Science - Weaponology - New Member Safety - ESD - New Member Hobbies - Fishing - New Member

Join Date: Sep 2006
Location: Near Frankfurt am Main, Germany. 50.390866N, 8.884827E
Posts: 17996
Good Answers: 200
#4
In reply to #3

Re: HADJI APPLIANCES

12/13/2007 6:21 AM

Dear Sparkstation,

you give some of the best answers I have seen in this area, long may you reign!!

Another perfect answer in a very "readable" format....

I vote for you almost every time I see something from you!!

__________________
"What others say about you reveals more about them, than it does you." Anon.
Reply
Guru
Hobbies - HAM Radio - CE3AM....4X4SW....CE3NSW

Join Date: Aug 2006
Location: Santiago Chile.
Posts: 845
Good Answers: 7
#5

Re: HADJI APPLIANCES

12/13/2007 7:47 AM

All very good answers,

If I were you I would also slow down the gen set's RPM to get 50 cycles for those rotating Hadji's appliances.

However, there are some (or maybe many) Hadjis that I would connect directly to the 3φ 400V system. (with strings attached)

Wangito.

__________________
Never trade luck for skill.
Reply
Reply to Forum Thread 5 comments

Good Answers:

These comments received enough positive votes to make them "good answers".

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Copy to Clipboard

Users who posted comments:

Andy Germany (1); Kilowatt0 (1); North of 60 (1); Sparkstation (1); wangito (1)

Previous in Forum: Harmonic Currents   Next in Forum: Power quality

Advertisement