Anonymous Poster

Differential Protection And Auto Transfer System

12/12/2007 10:54 AM

In a low voltage substation, including two incomings and a coupling circuit breakers, incoming C.Bs are connected to two individual power transformers which are fed from upstream medium voltage system. The two low voltage bus bars are equipped by a fast auto transfer system which is considered for coupling C.B auto closing when one of two bus bars is dead.

Also each transformer is protected by standard differential relay that must trip medium and low voltage C.Bs via fast interposing trip relays.

The problem observed when a short circuit occurred in one of two transformer windings. The differential relay operated and only relevant medium voltage circuit breaker tripped. The fault clearing stage was done successfully and related low voltage bus bar was dead. In this case the auto transfer system closed the low voltage coupling circuit breaker, and the short circuit point energized again.

Indeed, the relevant low voltage C.B of faulty transformer couldn't open on time. Last investigation didn't show any problem in low voltage C.B mechanism or related circuits.

How can you explain the reason of low voltage C.B inactivity?

BEST REGARDS

MSJ

Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.
Guru

Join Date: Jun 2007
Location: chennai,India
Posts: 592
Good Answers: 19
#1

Re: Differential protection and auto transfer system

12/12/2007 11:44 AM

The differential protection is only for transformer.Apparently from your posting I could infer there was a short circuit within the trasformer and the medium voltage breaker and the LV breaker tripped.

When ATS switched on the bus only is charged and not the faulty transformer, the transformer will get charged only when lv breaker is closed there is no fault current flow.

Please let us know more info for study and proper solution.

__________________
Ramesh,Freelance Electrical/automation Consultant
Reply
Anonymous Poster
#2
In reply to #1

Re: Differential protection and auto transfer system

12/13/2007 1:37 AM

Please note to my explanation. I said about it.

The problem observed when a short circuit occurred in one of two transformer windings. The differential relay operated and only relevant medium voltage circuit breaker tripped. The fault clearing stage was done successfully and related low voltage bus bar was dead. In this case the auto transfer system closed the low voltage coupling circuit breaker, and the short circuit point energized again.

REGARDS

MSJ

Reply
Guru

Join Date: Jun 2007
Location: chennai,India
Posts: 592
Good Answers: 19
#3
In reply to #2

Re: Differential protection and auto transfer system

12/13/2007 2:18 AM

I am sorry.

In that case first we have to find out whether Diff. relay picked up,

Then high speed master trip relay for mv breaker and lv breaker has picked up.

If both relays has picked up then examine the trip circuit of the lv breaker.(since this has not tripped).

The control circuit is to be examined.I doubt whether Diff. relay is wired to trip the lv breaker.

Unless I look at the control circuit drawing it will be difficult to come to any conclusion May be you can send the as fitted drawing for review.

__________________
Ramesh,Freelance Electrical/automation Consultant
Reply
Power-User

Join Date: Oct 2006
Location: Kolkata, India
Posts: 447
#4

Re: Differential Protection And Auto Transfer System

12/20/2007 12:18 AM

I will suggest to give a trip command direct to I/C-2 coil from bus transfer scheme. as a backup.

__________________
BNDas
Reply
Anonymous Poster
#5
In reply to #4

Re: Differential Protection And Auto Transfer System

12/24/2007 8:04 AM

Please think about trip relay drop off time.

REGARDS

MSJ

Reply
Power-User

Join Date: Oct 2006
Location: Kolkata, India
Posts: 447
#6

Re: Differential Protection And Auto Transfer System

12/25/2007 11:35 PM

Now we are in the age of Fast operating relay, the drop-off time is negligible of modern development in relay protection.

__________________
BNDas
Reply