Anonymous Poster

Voltage drop

01/23/2008 4:15 PM

Gentlemen:

We need know what size of aluminum cable will be used for the following conditions:

1. Distance between transformer to panelboad (overhead):600ft

2. Voltage: 208 Vac, single phase

3. load in ampers: 30 amps

Regards

Anthony

Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Power-User

Join Date: Oct 2007
Location: Hartwell Georgia N34* 56.770 / W83* 35.431
Posts: 222
Good Answers: 1
#1

Re: Voltage drop

01/23/2008 6:47 PM

You might be better off asking the power company to place a pole and mount a meter at the base. Your looking at #2 COPPER / 75C with a #8 copper ground. This needs to be in conduit, couplings, hangers, hardware, suck in a string, pull in a rope, wire lube, ect... Based on 75/C #2 copper you get a Voltage drop of 11.1 / 3.4%. (Electricalc Pro) Any more info on where you live and what your wanting to do?

James

__________________
" adapt, improvise, overcome "
Reply
Commentator

Join Date: Dec 2005
Posts: 92
Good Answers: 5
#2

Re: Voltage drop

01/23/2008 7:04 PM

In order to keep the voltage drop within 3% you need to use a 2AWG cable, this would give you about 201 volts at the load

Reply
Anonymous Poster
#3

Re: Voltage drop

01/23/2008 9:14 PM

#2 AWG Copper

Reply
Guru
United Kingdom - Member - Indeterminate Engineering Fields - Control Engineering - New Member

Join Date: Jan 2007
Location: In the bothy, 7 chains down the line from Dodman's Lane level crossing, in the nation formerly known as Great Britain. Kettle's on.
Posts: 32175
Good Answers: 839
#4

Re: Voltage drop

01/24/2008 7:01 AM

The latest edition of the Wiring Regulations by the Institution of Electrical Engineers can provide illumination on this subject.

__________________
"Did you get my e-mail?" - "The biggest problem in communication is the illusion that it has taken place" - George Bernard Shaw, 1856
Reply
Guru
Canada - Member - If there is a way to screw someting up, there is someone to do so! Safety - Hazmat - New Member

Join Date: Mar 2007
Location: Iqaluit, NU. Canada
Posts: 1854
Good Answers: 140
#5

Re: Voltage drop

01/24/2008 9:15 AM

As is the case with a large majority of the questions and answers in this forum, you need to verify the requirements for voltage drop in your jurisdiction.

Some posters have suggested that the use of a #2 copper conductor will meet your need. Perhaps it may meet the criteria you presented in the jurisdiction of the responders to your question.

But as you asked about an aluminum conductor... In my region a 3% voltage drop is the maximum permitted on a feeder. As such, given the conditions you mentioned, a 2/0 aluminum conductor would be required for this feeder.

If the conductor was made of copper, a #2 would still not meet the requirement in my region and a #1 conductor would be required.

Therefore... may I suggest you verify the code requirements for maximum voltage drop in your jurisdiction then consult a document such as PW Slack has mentioned.

For an excellent spreadsheet...

http://mikeholt.com/documents/freestuff/other/VoltageDropCalculator.xls

Rick...

__________________
Joe Contractor to Electrical Inspector, "What do you mean you are going to make me follow the code?".
Reply Score 1 for Good Answer
Power-User
Engineering Fields - Electrical Engineering - New Member

Join Date: Aug 2007
Location: Toronto
Posts: 239
Good Answers: 9
#6
In reply to #5

Re: Voltage drop

01/24/2008 2:06 PM

Thanks for that link North of 60. Great tool for anyone's toolbox.

Reply
Power-User

Join Date: Oct 2007
Location: Hartwell Georgia N34* 56.770 / W83* 35.431
Posts: 222
Good Answers: 1
#7
In reply to #5

Re: Voltage drop

01/24/2008 7:04 PM

I asked where he might live. In America he will use the National Electrical Code. It recommends in Article 215 that the voltage drop not exceed 5%,.... "will provide reasonable efficiency of operation". If he uses 2/0 Aluminum his conduit costs will be much higher. Using EMT as an example he will need 4". If he uses #2 copper he will use 1 1/2. #2 copper will also be easier to pull and the risk of damage will be much lower. These selections can be minimized to a degree by selecting different temperature ratings. He might be better off seeing if the power company will place a pole for him, or placing a step down transformer at the end, thereby using smaller wire as feeders.

James

__________________
" adapt, improvise, overcome "
Reply
Reply to Forum Thread 7 comments

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Copy to Clipboard

Users who posted comments:

Anonymous Poster (1); Graebeard (1); hastingselectric (2); North of 60 (1); PWSlack (1); shogun7 (1)