I have heard that an open secondary CT at primary full load conditions may become dangerous as high secondary voltages are produced as there is no secondary back emf etc and may cause arcing and hence damage.Lets look at this technically
A CT is basically a step-up transformer(from voltage point of view).In the case of 400/1 A CT the primary turn is 1(say the busbar)and the secondary turns is 400.How much will be the primary voltage drop?? it will be in millivolts for a busbar.So this millivolts multiplied by 400 will cause just around a few volts (say 3 to 10V) for an open secondary.But i have read that the secondary voltage will reach a few kilovolts for a 400/1A CT at full load conditions.My question is how it will reach a few kilovolts and damage the CT on open secondary condition?As we have seen above the max voltage wil be just in few volts.So please someone correct me where i am wrong??