Cold Junction Compensation

02/04/2008 4:28 PM

How to compensate the cold junction in thermocouple for temp measurement ..in both cases..

1. connection from thermocouple to temp transmitter and then to plc(or) dcs

2.Direct connection from thermocouple to plc(or) dcs..

Register to Reply
Pathfinder Tags: cold junction
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.

Good Answers:

These comments received enough positive votes to make them "good answers".

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
2
Guru
United Kingdom - Member - Not a New Member Hobbies - Musician - New Member Hobbies - Fishing - New Member

Join Date: May 2006
Location: Reading, Berkshire, UK. Going under cover.
Posts: 9684
Good Answers: 468
#1

Re: Cold Junction Compensation

02/04/2008 6:28 PM

Case 1: Any self-respecting temperature transmitter designed for operation with a thermocouple should already have cold junction compensation (CJC).

Case 2: If the PLC input module is designed for thermocouple input, it will almost certainly have CJC built in.

__________________
"Love justice, you who rule the world" - Dante Alighieri
Register to Reply Good Answer (Score 2)
Guru
Philippines - Member - New Member Engineering Fields - Instrumentation Engineering - New Member Engineering Fields - Control Engineering - Who am I?

Join Date: Oct 2006
Location: Northern Mindanao, Philippines
Posts: 2147
Good Answers: 53
#2

Re: Cold Junction Compensation

02/05/2008 6:57 AM

If your temperature transmitter/plc input/dcs input has a thermocouple input, it would most certainly have the cold junction compensation built in. No need to worry about it. Just connect and forget.

If you're connecting the thermocouple to a mV (millivolt) input, that's a different story. mV inputs are straight voltage inputs whereas thermocouple inputs have the compensation. Better check your equipment's manual to confirm.

One method of checking if the signal input has compensation is to countercheck the thermocouple reading with a thermometer (mercury/alcohol/digital whatever). If there's a difference (assuming the input is calibrated and properly configured), it is probably not compensated.

I emphasize the "probably" because I've had one technician condemn a thermocouple transmitter once because it wasn't reading correctly. It wasn't reading correctly because his indicator was configured for 0 to 150°C while his transmitter was configured for 0 to 100°C.

__________________
Miscommunication: when what people heard you say differs from what you said. Make yourself understood.
Register to Reply Score 1 for Good Answer
Member

Join Date: Jan 2008
Location: Tanzania
Posts: 7
#3
In reply to #2

Re: Cold Junction Compensation

02/05/2008 5:32 PM

I cannot crosscheck with thermometer, bcoz it is steam line of temperature range 485 deg......

we r getting temp through temp transmitter( yokokawa make)

Actually there is a temp difference of 30 deg(less) with temp gauge....

i had replaced with anothre temp gauges( 3 nos) and another make of temp transmitter, in that case,all these are showing correctly,i mean matching with gauge & transmitter value....

But, as per thermocouple chart value that yokokawa temprature( 30 deg less) value is correct........

plz suggest that, where may be thet fault....

Register to Reply
Guru
United Kingdom - Member - Not a New Member Hobbies - Musician - New Member Hobbies - Fishing - New Member

Join Date: May 2006
Location: Reading, Berkshire, UK. Going under cover.
Posts: 9684
Good Answers: 468
#4
In reply to #3

Re: Cold Junction Compensation

02/05/2008 6:04 PM

I'm having difficulty understanding your setup.

Am I correct in that you have a temperature gauge which is independent of the thermocouple/temperature transmitter?

And am I correct in that your thermocouple, when connected to the Yokokawa temperature transmitter, is reading 30° less than the gauge?

And am I also correct in that your thermocouple, when connected to another make of temperature transmitter, is reading the same value as your temperature gauge?

I'm afraid your last statement: "But, as per thermocouple chart value that yokokawa temperature( 30 deg less) value is correct........" has completely confused me.

Please clarify.

__________________
"Love justice, you who rule the world" - Dante Alighieri
Register to Reply
Guru
Canada - Member - New Member

Join Date: May 2006
Location: Montreal, Canada
Posts: 632
Good Answers: 11
#5
In reply to #4

Re: Cold Junction Compensation

02/05/2008 10:01 PM

May it be caused by a grounded TC and a non isolated transmitter VS an isolated transmitter?

__________________
''What the hell has my a** got to do with magic?" Don Quixote
Register to Reply
Guru
Philippines - Member - New Member Engineering Fields - Instrumentation Engineering - New Member Engineering Fields - Control Engineering - Who am I?

Join Date: Oct 2006
Location: Northern Mindanao, Philippines
Posts: 2147
Good Answers: 53
#6
In reply to #4

Re: Cold Junction Compensation

02/05/2008 10:14 PM

I'm afraid your last statement: "But, as per thermocouple chart value that yokokawa temperature( 30 deg less) value is correct........" has completely confused me.

Me too.

To shanmugam:

What are you basing your conclusion from? In other words, how can you be sure that the reading of 30°C less is correct?

One way to get a bit of confirmation, as I said, is to use a thermometer, say in an oil bath that's heated up to around 100°C or so. You don't need to raise it to 400+. All you're interested in is that the thermometer and thermocouple are reading the same. If the 30°C difference is still there, you may have:

  1. A defective transmitter - defective cjc or non-existent (check the manual)
  2. A wrongly configured transmitter.
  3. A thermocouple that has "micro-cracks" - microscopic defects on the thermocouple wires that are affecting the readings.

Now, it's possible that the 30°C difference may not exist or is not apparent at 100°C. The problem may now lie in the span setting (still in the configuration setting).

__________________
Miscommunication: when what people heard you say differs from what you said. Make yourself understood.
Register to Reply
Member

Join Date: Jan 2008
Location: Tanzania
Posts: 7
#8
In reply to #6

Re: Cold Junction Compensation

02/06/2008 5:16 PM

I'm afraid your last statement: "But, as per thermocouple chart value that yokokawa temperature( 30 deg less) value is correct........" has completely confused

mee too cofused...

Register to Reply
Commentator
Fans of Old Computers - Commodore 64 - New Member United States - US - Statue of Liberty - New Member Engineering Fields - Control Engineering - Process Control Engineer

Join Date: Dec 2007
Location: Idaho, USA
Posts: 79
Good Answers: 2
#7

Re: Cold Junction Compensation

02/06/2008 3:21 PM

Some DCS i/o only has CJC as an option. A thermocouple must be installed near the i/o and terminated on a designated CJC terminal. To test whether CJC is working, simply cool or heat the dcs i/o or transmitter. If it moves, you have no compensation. In one case, everytime a process i/o cabinet was opened, our process temperature changed and it affected out product when the controls reacted.

__________________
It is impossible to defeat a fool in an argument, he wil bring you down to his level and beat you with experience.
Register to Reply
Member

Join Date: Jan 2008
Location: Tanzania
Posts: 7
#9
In reply to #7

Re: Cold Junction Compensation

02/06/2008 5:22 PM

I'm afraid your last statement: "But, as per thermocouple chart value that yokokawa temperature( 30 deg less) value is correct........" has completely confused

mee too cofused...

Actually that was saturated temp of steam drum..the pressure was 47 kg/ cm2..

according to this condition the temp should be around 260 deg.. but that transmitter was showing 230 deg only...

i had conformed that 30 deg less by above mentioned case, also i had conformed with another gauge's and transmitter with a same range........

Register to Reply
Register to Reply 9 comments

Good Answers:

These comments received enough positive votes to make them "good answers".

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Copy to Clipboard

Users who posted comments:

AccuDave (1); gigaconcept.com (1); JohnDG (2); shanmugam_vps (3); Vulcan (2)