Electrical power cable cabinet penetrations.

02/06/2008 2:02 PM

I was surprised to see separate electrical cable cabinet penetrations for each phase at an oil platform in the Golf of Mexico. I have always considered that all the three phases of a power cable (including the neutral/ground if applicable) must use the same penetration. This is to minimize the induction of current in the cabinet steel. Although parallel groups could use separate penetrations. The practice of having one phase per hole on a steel cabinet (at many hundreds of amps) seems to be common there as I saw many examples of it. Is it an acceptable practice or is it just a cheap job?

__________________
Experienced is earned, common sense is taught, both are rare essentials of life.
Register to Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Guru
New Zealand - Member - Interested in everything- see my Profile please APIX Pilot Plant Design Project - Member - Member Engineering Fields - Electrical Engineering - Member Engineering Fields - Power Engineering - Member Engineering Fields - Civil Engineering - Member Hobbies - Musician - Autoharp and Harmonica Hobbies - Hunting - Member Hobbies - Fishing - Member

Join Date: Nov 2007
Location: Christchurch, (The Garden City), South Island, New Zealand
Posts: 4395
Good Answers: 230
#1

Re: Electrical power cable cabinet penetrations.

02/06/2008 4:49 PM

Hello marcot

It may well be that the installation did not use plain steel for the penetration plate.

If plain steel was used, there would normally be a longitudinal slot, the width of even 0.5mm running across the hole centres for the cables, to minimise eddy currents in the plate.

Here in similar situations, I have seen insulating plates used, with the earthing bushes directly fitted on each of the cables, which gets around the problem.

But if that plate penetration is plain steel, without the slotting between, there would be heavy circulating currents in it, not a good practice.

Kind Regards....

__________________
"The number of inventions increases faster than the need for them at the time" - SparkY
Register to Reply
Guru
Canada - Member - Specialized in power electronics

Join Date: Feb 2008
Location: Montreal, Canada.
Posts: 1372
Good Answers: 80
#2
In reply to #1

Re: Electrical power cable cabinet penetrations.

02/06/2008 5:49 PM

I agree with you about the circulating currents. The holes were in plain steel with a bushing per cable. No slots or glan plates were used. I would have liked to measure the cabinet temperature at full load but they were operating at low capacity. My IR thermometer didn't record much of a delta T. I didn't see any discoloration of the paint so the temperature rise should be below 100C. When I asked their electrical engineer about it, he told me that they always do it that way.

__________________
Experienced is earned, common sense is taught, both are rare essentials of life.
Register to Reply
Guru
New Zealand - Member - Interested in everything- see my Profile please APIX Pilot Plant Design Project - Member - Member Engineering Fields - Electrical Engineering - Member Engineering Fields - Power Engineering - Member Engineering Fields - Civil Engineering - Member Hobbies - Musician - Autoharp and Harmonica Hobbies - Hunting - Member Hobbies - Fishing - Member

Join Date: Nov 2007
Location: Christchurch, (The Garden City), South Island, New Zealand
Posts: 4395
Good Answers: 230
#3
In reply to #2

Re: Electrical power cable cabinet penetrations.

02/07/2008 4:32 AM

Hello again marcot

It may well be that the Electrical Engineer has used steel for the Gland plates, and has weighed up the flameproofing requirements of the cabinet using a full steel enclosure, against the heating losses incurred by the circulating currents.

As an alternative, the Gland plate may be made of heavy brass, aluminium alloy ("Birmabright" or similar alloy suitable for maritime conditions).

If non-magnetic materials are used for the Gland plate, the circulating currents are minimised, being localised in the immediate vicinity of each phase.

Kind Regards....

__________________
"The number of inventions increases faster than the need for them at the time" - SparkY
Register to Reply Score 1 for Good Answer
Anonymous Poster
#4

Re: Electrical power cable cabinet penetrations.

02/28/2008 2:21 AM

Dear friend,

The Cable size is designed separately and the cut out size depends on the GA of the Panel which we are going to use. For ex. if we have as Panel of size 800 x 450 mm then we can have a 3Cx 630 sq.mmcable to transmit 11 kV Voltage considering the cable dia . of around 57 mm .

For higher size which is used in the case of Transformer of 220/66 kV volatge class a 2 runs x of 1000 sq.m cable can be used per phase and a separate cable for neutral bushing which will not be terminated inside the cable box. The cable box normallly oil filled type and for this kV rating. A separate cut out will be there for each phase cable. The cable box must be designed in such a way to accomdate all the three phase cables. This practically applied in many locations.

Regards,

N.Suresh

Register to Reply
Anonymous Poster
#5
In reply to #4

Re: Electrical power cable cabinet penetrations.

04/11/2008 2:26 PM

Hello

I have answered your Post/comments,

Generally best to use the Cable Maker of your particular cable, but try:

http://relemaccables.com/

If you are still needing help, reply with

Kind Regards....

Register to Reply
Register to Reply 5 comments

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Copy to Clipboard

Users who posted comments:

Anonymous Poster (2); marcot (1); Sparkstation (2)

Previous in Forum: Do It Yourself PICkit2 programmer design, Au Group Electronics-CB0703   Next in Forum: How to Determine Rotor Slot Dimensions
You might be interested in: Cable Laying Services, Cable Assemblies, Cable Trays

Advertisement