Calculating the Distributive Capacitance for 2 14AWG Cu conductors over 2000ft?

02/13/2008 10:50 AM

I need to pull in a coil on a control relay approximately 2000ft from the source voltage (wireless is not an option) My question is would it be better to use DC or AC source? AC relay coil inruse 133VA and holding 20VA @ 120VAC, and DC coil is 0.53W @ 12VDC. Both coils have approx 15% swing + or -. Quick calc shows DC voltage drop to be 0.822v (which is acceptable), but I am having problems calculating the voltage drop on the AC circuit due to the effects of the inductive and capacitive properties of the parallel conductors (use air as dielectric please and distance to be insulator thickness). Could someone point me to a formula that could assist me?

Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.

Good Answers:

These comments received enough positive votes to make them "good answers".
Guru
United Kingdom - Member - Olde Member!! Engineering Fields - Instrumentation Engineering - New Member

Join Date: Jul 2006
Location: Dunstable, England
Posts: 2821
Good Answers: 45
#1

Re: Calculating the Distributive Capacitance for 2 14AWG Cu conductors over 2000ft?

02/13/2008 11:23 AM

For ac you must think along the lines of the supply wires being a transmission line and not just a capacitive coupled line.

For almost ½ mile run of cable the capacitance and inductance form a fixed impedance transmission line...

As for the formulae to calculate the impedances, they would be pretty inaccurate depending on the type of wire you will be using...

If you were to use coaxial cable the impedances would be well known and documented, it would be more expensive, but if the capacitance and inductance is a concern for you - and I can't think why it should be - then use coaxial cable!

John.

__________________
A little knowledge is a dangerous thing - Googling is far worse!
Reply
Anonymous Poster
#2
In reply to #1

Re: Calculating the Distributive Capacitance for 2 14AWG Cu conductors over 2000

02/13/2008 11:58 AM

To further define my question. The reason of concern is actually dropping out the coil when the source voltage is no longer present. Since holding VA is only 20VA on the AC coil; is there enough residual charge do to the capacitance to keep the coil pulled in for an unacceptable period of time?

Reply
Guru
United Kingdom - Member - Olde Member!! Engineering Fields - Instrumentation Engineering - New Member

Join Date: Jul 2006
Location: Dunstable, England
Posts: 2821
Good Answers: 45
#5
In reply to #2

Re: Calculating the Distributive Capacitance for 2 14AWG Cu conductors over 2000

02/13/2008 3:48 PM

If it is a concern then why not when turning the power to the relay off, put a short on the wire to give a positive short circuit to any capacitive storage current flow?

__________________
A little knowledge is a dangerous thing - Googling is far worse!
Reply
Guru
United Kingdom - Member - Indeterminate Engineering Fields - Control Engineering - New Member

Join Date: Jan 2007
Location: In the bothy, 7 chains down the line from Dodman's Lane level crossing, in the nation formerly known as Great Britain. Kettle's on.
Posts: 32175
Good Answers: 839
#3

Re: Calculating the Distributive Capacitance for 2 14AWG Cu conductors over 2000ft?

02/13/2008 12:00 PM

The acceptance criteria need to be stated.

  • If, as already stated, the voltage drop at 12VDC is acceptable, then 12VDC is self-evidently acceptable!
  • It is unlikely an AC load of this size would present any difficulty to a 120VAC control circuit, so the AC solution is also acceptable. The voltage drop is likely to be lower for the AC circuit.

24VDC and 110VAC are common industrial control voltages in the UK and neither of these would present any difficulty in the situation posted.

__________________
"Did you get my e-mail?" - "The biggest problem in communication is the illusion that it has taken place" - George Bernard Shaw, 1856
Reply
Anonymous Poster
#4
In reply to #3

Re: Calculating the Distributive Capacitance for 2 14AWG Cu conductors over 2000

02/13/2008 12:41 PM

I agree, but to reference the statement "It is unlikely an AC load of this size would present any difficulty to a 120VAC control circuit". As Engineers don't you want to know what that "unlikely" value is? Isn't it our job to calculate it?

Reply
3
Guru
Popular Science - Weaponology - New Member United Kingdom - Member - New Member

Join Date: May 2007
Location: Harlow England
Posts: 16512
Good Answers: 670
#6
In reply to #4

Re: Calculating the Distributive Capacitance for 2 14AWG Cu conductors over 2000

02/13/2008 5:36 PM

As Engineers don't you want to know what that "unlikely" value is? Isn't it our job to calculate it?

Not if we know it is going to be irrelevant!
Easy enough to do a quick order of magnitude calculation...take xpF per metre (figures for various cables easilly available..or if you can't find 'em use figures for coax...double 'em if you like!) work out the total C and the energy stored therein and compare with the hold in requirement... or even easier, get a 'C' of about that value and slap it across the relay and observe with a scope that it makes very little difference.
Ok what do I mean by 'very little'...I mean less than a tenth of the delay caused by mechanical inertia.

We would never design or build anything if we rigourously calculated every single current, time-constant and value. It's called experience and when you consider the tolerances on most components it would be a waste of time...The skill is in knowing what to calculate and when.

Del

__________________
health warning: These posts may contain traces of nut.
Reply Good Answer (Score 3)
Guru
United Kingdom - Member - Not a New Member Hobbies - Musician - New Member Hobbies - Fishing - New Member

Join Date: May 2006
Location: Reading, Berkshire, UK. Going under cover.
Posts: 9684
Good Answers: 468
#7
In reply to #6

Re: Calculating the Distributive Capacitance for 2 14AWG Cu conductors over 2000

02/13/2008 6:40 PM
__________________
"Love justice, you who rule the world" - Dante Alighieri
Reply
Guru
United Kingdom - Member - Indeterminate Engineering Fields - Control Engineering - New Member

Join Date: Jan 2007
Location: In the bothy, 7 chains down the line from Dodman's Lane level crossing, in the nation formerly known as Great Britain. Kettle's on.
Posts: 32175
Good Answers: 839
#9
In reply to #6

Re: Calculating the Distributive Capacitance for 2 14AWG Cu conductors over 2000

02/14/2008 5:24 AM
__________________
"Did you get my e-mail?" - "The biggest problem in communication is the illusion that it has taken place" - George Bernard Shaw, 1856
Reply
Guru
United Kingdom - Member - Olde Member!! Engineering Fields - Instrumentation Engineering - New Member

Join Date: Jul 2006
Location: Dunstable, England
Posts: 2821
Good Answers: 45
#12
In reply to #6

Re: Calculating the Distributive Capacitance for 2 14AWG Cu conductors over 2000

02/14/2008 8:20 AM

Well said!! Where do you get those smilies from??

John. Ahhhhhhhhhhh copy and paste does it

__________________
A little knowledge is a dangerous thing - Googling is far worse!
Reply
Guru

Join Date: Jul 2007
Posts: 4448
Good Answers: 143
#8

Re: Calculating the Distributive Capacitance for 2 14AWG Cu conductors over 2000ft?

02/13/2008 7:58 PM

Just a thought, but 2000' of 120 VAC has got to be pretty expensive. If this isn't a classified area, the 12 VDC looks cheaper to me?

__________________
"Well, I've wrestled with reality for 35 years, Doctor, and I'm happy to state I finally won out over it." Elwood P. Dowd
Reply
Guru
United Kingdom - Member - Indeterminate Engineering Fields - Control Engineering - New Member

Join Date: Jan 2007
Location: In the bothy, 7 chains down the line from Dodman's Lane level crossing, in the nation formerly known as Great Britain. Kettle's on.
Posts: 32175
Good Answers: 839
#10
In reply to #8

Re: Calculating the Distributive Capacitance for 2 14AWG Cu conductors over 2000ft?

02/14/2008 5:38 AM

Well, it depends. If the conductor size is constrained by various specifications, then the marginal costing is [control transformer if required and not already provided] v [12VDC power supply to be supplied if not already provided]. The forum can't see the original poster's [OP] local specifications, customs and practices, so really only the OP can make that call, n'est-ce pas?

__________________
"Did you get my e-mail?" - "The biggest problem in communication is the illusion that it has taken place" - George Bernard Shaw, 1856
Reply
Guru

Join Date: Jul 2007
Posts: 4448
Good Answers: 143
#11
In reply to #10

Re: Calculating the Distributive Capacitance for 2 14AWG Cu conductors over 2000ft?

02/14/2008 7:27 AM

You're right. I had my xenophobic blinders on and was thinking NEC and the like.

__________________
"Well, I've wrestled with reality for 35 years, Doctor, and I'm happy to state I finally won out over it." Elwood P. Dowd
Reply
Power-User

Join Date: Sep 2006
Location: Houston Texas
Posts: 282
Good Answers: 16
#13

Re: Calculating the Distributive Capacitance for 2 14AWG Cu conductors over 2000

02/14/2008 9:23 AM

If I were going to pay for the expense to pull a ½ mile cable then I would be dang sure to plan for future expansion. What would you do if next month you wanted to add more control points?

Many of the common PLC's feature open standard network communications. For example, a simple Allen-Bradley DH+ (Data Highway Plus) trunkline can span up to 10,000 feet. It will be very easy to add more analog or digital I/O to the existing network.

Click for info:
http://www.ab.com/en/epub/catalogs/12762/2181376/214372/1491278/

Regards, Delmar Schmidt
Melfi Technologies Houston
www.melfitechnologies.com

__________________
Specializing in Dynamic Weighing Systems for Powder and Bulk Solids Handling
Reply
Reply to Forum Thread 13 comments

Good Answers:

These comments received enough positive votes to make them "good answers".
Copy to Clipboard

Users who posted comments:

Anonymous Poster (2); Delmar (1); Electroman (3); JohnDG (1); PWSlack (3); TVP45 (2); user-deleted-1105 (1)

Previous in Forum: Electronic thermal managment   Next in Forum: Isolator

Advertisement