UPS

02/17/2008 5:00 AM

Hi, I am looking after the maintenance of building services in a large R&D Institute of Govt. of India. My major concern has always been indiscriminate use of UPS system. I would like to request senior members to throw some light on

1.Selection of UPS rating i.e. how the KVA rating and backup time should be selected.

2. What would be a better choice, a centralized UPS system for the entire campus or standalone on-line UPS for various equipment.

3. Under given circumstances, how UPS size and the size of mains cable (raw power) are interrelated.

__________________
It takes considerable knowledge just to reaIise your own extent of ignorance.
Register to Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.

Good Answers:

These comments received enough positive votes to make them "good answers".

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Guru
Popular Science - Weaponology - New Member United Kingdom - Member - New Member

Join Date: May 2007
Location: Harlow England
Posts: 16512
Good Answers: 670
#1

Re: UPS

02/17/2008 5:07 AM

Hi,

Not my field of expertise..but I'm V interested in Q2. As this applies to all sorts of facilities.
My personal preference is a number of stand alone UPS. This avoids everything failing at once, it probably simplifies wiring but increases cost.

There must be some some point of maximum effectiveness.

I s'pose the other alternative is to have your own generator for the whole establishment.

Del

__________________
health warning: These posts may contain traces of nut.
Register to Reply
Associate
Engineering Fields - Energy Engineering - New Member India - Member - Jack of all trades

Join Date: Jan 2008
Location: India
Posts: 43
Good Answers: 2
#2

Re: UPS

02/17/2008 5:21 AM

Thanks Del,

We do have a 100 percent back up system through diesel generator sets yet there are some equipment like Nuclear Magnetic Resonance Spectrometer and a hundred others alike, for which uninterrupted power supply is very crucial. Standalone UPS does have own advantages but I have noticed that they not only create disbalance in the three phase system but at the same time pollute the power system network by injecting harmonics. I would appreciate if you can advise after considering these factors.

Regards,


Kamal

__________________
It takes considerable knowledge just to reaIise your own extent of ignorance.
Register to Reply Score 1 for Good Answer
Guru
Popular Science - Weaponology - New Member United Kingdom - Member - New Member

Join Date: May 2007
Location: Harlow England
Posts: 16512
Good Answers: 670
#4
In reply to #2

Re: UPS

02/17/2008 5:32 AM

Cheers, I can't advise sorry...
like I said 'not my field of expertise' and I do try not to talk about stuff that I don't know about! (although I sure some would beg to differ )
Del

__________________
health warning: These posts may contain traces of nut.
Register to Reply Off Topic (Score 6)
Guru
Engineering Fields - Systems Engineering - New Member Hobbies - Model Rocketry - New Member

Join Date: Dec 2006
Location: Long.92E,Lat.26N
Posts: 1336
Good Answers: 14
#8
In reply to #2

Re: UPS

02/17/2008 8:35 AM

Del's commonsense suggestion to#2 is the one we should follow.

< pollute the power system network by injecting harmonics> This may turn out to be a misplaced fear.

Pollutes the mains supply? But mains Transformer's star delta windings absorbs all 3rd harmonic distortions. And you can put in a Low-pass(high stop) filter into UPS.

Register to Reply
2
Guru
New Zealand - Member - Interested in everything- see my Profile please APIX Pilot Plant Design Project - Member - Member Engineering Fields - Electrical Engineering - Member Engineering Fields - Power Engineering - Member Engineering Fields - Civil Engineering - Member Hobbies - Musician - Autoharp and Harmonica Hobbies - Hunting - Member Hobbies - Fishing - Member

Join Date: Nov 2007
Location: Christchurch, (The Garden City), South Island, New Zealand
Posts: 4395
Good Answers: 230
#3

Re: UPS

02/17/2008 5:24 AM

Hello j_kamal

A) The capital costs of a centralised system, and the extra power distribution required, weigh heavily in favour of stand-alone units for various equipment.

B) Add to that, the problem of a centralised UPS system failure, which would probably happen at a time of mains power failure. (Expect the worst...it's going to happen sometime).

C) The main advantage of stand-alone units is that these are made by the millions, and if you did a deal with a Supplier, then because you are purchasing perhaps a few standard sizes, but many of each, you should be able to get a really good price offer from Suppliers.

D) The extra benefit of the stand-alone UPS is that if you carry a few spares in the campus workshop, a malfunctioning unit is quickly and easily replaced.

E) The only problem which may occur with stand-alone units is one of Security - If there is thievery around the Campus these and other equipment items may be stolen.

F) To prevent theft, each item should be marked with a riveted on plus epoxy adhesive fixed Equipment plate with the Individual Plant Number - A database which cross-matches those Plant Numbers to the Serial and Model/Brand of equipment should be used, along with Ultraviolet markings and/or Microdots.

G) As far as UPS size and cable size, until equipment lists are made, it is impractical to advise re those questions.

Advise with further details, please.

Kind Regards....

__________________
"The number of inventions increases faster than the need for them at the time" - SparkY
Register to Reply Good Answer (Score 2)
Associate
Engineering Fields - Energy Engineering - New Member India - Member - Jack of all trades

Join Date: Jan 2008
Location: India
Posts: 43
Good Answers: 2
#5
In reply to #3

Re: UPS

02/17/2008 5:35 AM

Thanks Sparky,

I do appreciate your thoughtful comments, as for cable sizing, let us for instance consider a 35 KVA, 3-Phase input and 1-Phase output UPS. Would you please let me know the rule of the thumb for calculating the cable size after accounting for the battery charging current in the event of complete discharge.

Regards,


Kamal

__________________
It takes considerable knowledge just to reaIise your own extent of ignorance.
Register to Reply
Guru
New Zealand - Member - Interested in everything- see my Profile please APIX Pilot Plant Design Project - Member - Member Engineering Fields - Electrical Engineering - Member Engineering Fields - Power Engineering - Member Engineering Fields - Civil Engineering - Member Hobbies - Musician - Autoharp and Harmonica Hobbies - Hunting - Member Hobbies - Fishing - Member

Join Date: Nov 2007
Location: Christchurch, (The Garden City), South Island, New Zealand
Posts: 4395
Good Answers: 230
#6
In reply to #5

Re: UPS

02/17/2008 5:50 AM

Hello again j_kamal

To answer re cable sizes, one would need to know the length of cable involved, along with voltages used.

As it's almost midnight here, I'll check back in the morning.

Meanwhile another Member may have given you an answer.

Cheers.

Kind Regards from far away....

__________________
"The number of inventions increases faster than the need for them at the time" - SparkY
Register to Reply
Anonymous Poster
#11
In reply to #6

Re: UPS

02/17/2008 10:45 PM

Thanks Sparky,

The lenth of Input Cable is 15 Meters and the connected to the UPS is 22 KW. System voltage is 400 V Phase to Phase.

Regards,

Kamal

Register to Reply
Associate

Join Date: Sep 2007
Posts: 49
Good Answers: 1
#9
In reply to #5

Re: UPS

02/17/2008 8:53 AM

The UPS output is 35kVA. By dividing to UPS efficiency you have the input kVA to UPS (without considering the charging power). consider the efficiency to be 85% the input power will be 35kVA/0.85=41.2kVA

Now you can add the battery bank boost charge current.

If the battery bank is 1*100%, Ni-Cd type, 30 Minute. back-up time and the nominal DC voltage is 110V. Roughly the battery size will be 91*236AH SBH type and the charging current will be about 20% of 236A i.e 47A. So the charging power will be 47A*91*1.5V=6400W

the UPS input power at the worst conditions will be about 41.2+6.4=47.6kVA

for the 400V system the current will be 47.6/(1.73*0.4)=69A.

Now you can follow the cable sizing.

__________________
A thousand-mile journey begins with the first step.
Register to Reply
Anonymous Poster
#12
In reply to #9

Re: UPS

02/17/2008 10:49 PM

Well Abbas,

That answers my question. Thanks

Regards,

Kamal

Register to Reply
Power-User

Join Date: Aug 2006
Posts: 183
Good Answers: 2
#15
In reply to #12

Re: UPS

02/18/2008 12:16 AM

Generally the battery bank is mounted close to the UPS and therefore not much of voltage drop will take place & therefore battery cable operating current density of approx. 1.5/2.0 A/sq.mm is sufficient. But when AC supply is distributed then depending on the distance at which load is located, cable sizing has to be done. You can decide how much is the max. permissible voltage drop at the load end. Say V at current I. Cable resistance ( neglecting the reactance ) will then be V/I. From the cable table, for this Resistance value, check suitable gauge size, for the length concerned.

Last but not the least, though costly, high efficiency ups are ALWAYS preferable. Sometimes high efficiency UPS might even be cheaper, if the battery capacity requirement of a high efficiency ups is lower than that of a lower efficiency ups. Alternatively high efficiency ups would give greater backup time.

Thanks and regards

Ashok Toshniwal, Bangalore, India

Register to Reply
Guru
Popular Science - Weaponology - New Member United Kingdom - Member - New Member

Join Date: May 2007
Location: Harlow England
Posts: 16512
Good Answers: 670
#7
In reply to #3

Re: UPS

02/17/2008 5:52 AM

Hi Sparky,
I couldn't help smiling at (F)...
Marking things doesn't stop 'em being nicked....Weld 'em (or bole 'em with 'security bolts' to an RSJ might .

Other than that...great answer....I'll even mark it as such, even tho' it grieves me to my very core....
Del

__________________
health warning: These posts may contain traces of nut.
Register to Reply Off Topic (Score 6)
Guru
New Zealand - Member - Interested in everything- see my Profile please APIX Pilot Plant Design Project - Member - Member Engineering Fields - Electrical Engineering - Member Engineering Fields - Power Engineering - Member Engineering Fields - Civil Engineering - Member Hobbies - Musician - Autoharp and Harmonica Hobbies - Hunting - Member Hobbies - Fishing - Member

Join Date: Nov 2007
Location: Christchurch, (The Garden City), South Island, New Zealand
Posts: 4395
Good Answers: 230
#10
In reply to #7

Re: UPS

02/17/2008 4:28 PM

Hello Del the cat

I remember years ago, when electronic calculators were using nixie tubes, the size of a briefcase, made only by Hewlett Packard, and cost NZ$14,000 each.

Canterbury University in Christchurch, where I live, had several of these in the Engineering Lab, and to prevent thievery, had strong chains padlocked to the calculators, as well as bolting them to the bench tops.

Even so, I understand, one went "missing", but turned up later in the campus grounds.

I guess a student, or group of students, saw the anti-theft precautions as an engineering challenge.

Of course within a few months, a consortium of Japanese Electronic makers, led by Hitachi, had made smaller and faster green gas plasma didplay calculators.

They got around the "square root key" problem (a patent of HP's was evaded by doing this), by doing the divide by and equals button, which effectively gave a square root to 12 decimal places, 8 visible, and the other 4 "around the corner", which 4 digits could be seen by pressing an extra button.

I purchased one of the first Hitachi calculators as it arrived in New Zealand, (I still have this unit in working order), cost was then NZ$150, within 3 months prices slumped to NZ$75, and another 3 months Casio came out with the first LCD unit for NZ$32.

Now the Casio Scientific calculator can be purchased for NZ$9.95.

Sorry to hear about yourwhat you need is

Kind Regards....

__________________
"The number of inventions increases faster than the need for them at the time" - SparkY
Register to Reply Off Topic (Score 5)
Guru

Join Date: Feb 2006
Posts: 757
Good Answers: 12
#13

Re: UPS

02/17/2008 11:41 PM

What exactly means: indiscriminant use of UPS? Having too much back up power? Please clarify.

If single UPS (wow what a battery) safeguards power to the whole campus, single UPS failure (or down time) removes said safeguards for the entire campus...including safeguards like emergency services dispatch.

Register to Reply
Anonymous Poster
#14
In reply to #13

Re: UPS

02/18/2008 12:12 AM

Yes exactly!

You know in a scientific institute, people are paranoid about availability of uninterrupted power supply. I have come across guys who would buy UPS just for sake of it. Anyways, that is the reason I talked about centrailzed system in the first instance.

Regards,

Kamal

Register to Reply
Guru

Join Date: Feb 2006
Posts: 757
Good Answers: 12
#18
In reply to #14

Re: UPS

02/18/2008 12:30 PM

Okay, so you're saying "indiscriminant" means, un-centralized (I think). Seems to me, however, that that's backwards; and that centralized would be (or would tend to be) the most "indiscriminant." (Here I'm ignoring the fact that localized UPSs will probably still be installed, central UPS or no.)

You speak of a scientific institute and of paranoia about uninterrupted power. But you make it sound as if the institute is peopled by a bunch of yahoos without a clue. Would it be unreasonable...paranoia about loss of critical (scientific research and such) information stored in computers and in instrument controllers? Would it be unreasonable to want the (uninterruptible) back-up power resource (online or offline) to be as close as possible to the point(s) of application? For you, could it not be more reasonable to have single point failures in the "system" already partially isolated? Because the UPS's are localized (as well as isolated) near the points of failure symptoms on the grid?

You say you have backup power already in the form of diesel generators, (Possibly you might also procure backup power utility company as is done by businesses in U.S.) So it seems that the concept for centralizing the campus UPS's might be more about "control" and "make work" than about any real need. That said, perhaps a study (involving yourself and end users of the power) might lead (apart from keeping things as they are) to some kind of "hybrid" system (centralize where it makes sense only). Again, bear in mind that total centralizing is quite unlikely to keep localized UPS's from being installed anyway--whether maintenance engineer agrees or not. (Also, there's where you might run into problems--when glitches and transients in the central UPS office begin showing up as (indiscriminant) power failures (UPS switching and alerts) all around the campus. Would you as maintenance engineer want to take on the task of policing all power users to prevent such things?)

So I'm simply asking you to consider carefully whether this is not simply a bright idea looking for an application--as opposed to a real problem looking for a cure.

Register to Reply
Guru
Safety - ESD - New Member India - Member - New Member Engineering Fields - Energy Engineering - New Member

Join Date: May 2007
Location: Pune , India
Posts: 875
Good Answers: 42
#16

Re: UPS

02/18/2008 2:43 AM

Hi Mr. Kamal,

You got very good and valuable recommendations. I would like to add only few points.

1. Since your organisation being R&D and under Govt. of India, I hope finance will not be a constrain so long as you can convince the sanctioning authority. So technical considerations are more important. For taking a decision for installing UPS. There are two consideration for calculating the capacity requirement.

(1) What is the frequency of power failure and the time period the power outing is expected. I mean weather your organisation come under regular load shedding from electricity board.

(2) Weather do you really need uninterrupted power supply for all the equipment including lighting and air conditioning or only for few vital machines computers and instruments where uninterrupted power s required for specific process where the power interruption may cause damage to the ongoing research job.

(3) What is the quality of power required for the specific equipment.

From best of my experience I feel you should go for UPS, only for your computers and most frequently used sophisticated equipments.The UPS should be of good quality stand alone UPS (of reputed manufacture) which provide harmonic suppressors and and sine wave output )depending on the capacity of the particular machine with consideration of actual peak load requirement. Here also depending upon the continuity of supply with out break is a point of consideration. If a small break in power supply is not permissible for the process then you should go for online UPS where the equipment is powered from UPS and backup battery and the battery is in floating condition so that power interruption will not have any effect on power outings. Other wise Inverters with change over switch can be used. Why I suggest this is it will reduce maintenance and equipment cost.

For the rest of the load if you anticipate long power failure go for captive diesel generating sets with change over switch. They are cheap and easy to operate and maintain.

Register to Reply Score 1 for Good Answer
2
Power-User
United Kingdom - Member - New Member Engineering Fields - Transportation Engineering - New Member Technical Fields - Marketing/Advertising - New Member Hobbies - Target Shooting - New Member

Join Date: Sep 2007
Location: South coast of England
Posts: 411
Good Answers: 36
#17

Re: UPS

02/18/2008 4:42 AM

It is some years since I worked with big UPS systems (auxiliary supplies for dark starting power stations), but it may be worth looking at the virtues of large a large UPS.

In general large UPS systems are built to higher standards than small one, both in reliability and with respect to emc and power factor. It is easier to fit them with large battery banks and manage their maintenance. Battery banks can be properly installed with correct fusing and ventilation. I have so often seen UPSs with straggling wires to car or truck batteries (not the sealed type) in offices in India and elsewhere. These hazards are avoided with professionally manged central systems. cheap UPS systems are often less reliable than the system they are protecting.

The down side of the centralised system is first cost, it will be more expensive, it needs to be bigger if it is to support the entire facility rather than selected loads, or else there will need to be separate wiring for protected circuits. Localised UPSs also protect against failures in the final circuits and breakers. A localised UPS can be connected via a serial data link to the equipment it is protecting to shut it down in a controlled way before the batteries fully discharge, this is generally impractical with centralised systems.

Register to Reply Good Answer (Score 2)
Associate

Join Date: Feb 2008
Location: Hawick, Scotland
Posts: 34
Good Answers: 3
#19

Re: UPS

02/18/2008 3:56 PM

As you suggest, the indiscriminate use of UPSs is wasteful on many levels. It takes time to work out what equipment needs to have a maintained supply (eg, CPUs, emergency lights) and what can flicker off and back on when the mains power returns (computer screens, recreational equipment). I recently specified a system that had three levels of backup powering different coloured sockets: white—no backup, direct from mains supply; green—generator backup; red—UPS. There was also a DC line that offered the highest level of power security as the equipment ran from the battery bank all of the time.

The more equipment that can be run off ELV DC power supplies, the better. 12V has advantages in terms of availability of equipment but 24V and higher has advantages in lower losses in the conductors (due to reduced current).

My preference is for centralised systems and good quality deep-cycle cells but distribution distance becomes a problem unless you use a high voltage. If individuals purchase their own stand-alone UPS for their own equipment, it will typically be undersized and overpriced and have too much plugged into it.

It sounds like you have quite a job on your hands! Good luck.

__________________
If you never change your mind, why have one? — Edward deBono
Register to Reply
Anonymous Poster
#20

Re: UPS

02/21/2008 1:17 PM

Here's a couple of articles that would be helpful to determine which avenue will be beneficial to your Gov't.

This is the sixth article in a series covering basic engineering and code issues for standby generators and critical systems used in commercial building.

When a power event occurs, the uninterruptible power supply provides the temporary ridethrough until the generator kicks in. In this installment of the series, I summarize some of the rotary and flywheel UPS technology available today. These technologies will be evaluated in conjunction with standby generators for critical environments.

A majority of UPS backup systems that I have designed are provided with a battery arrangements. These systems are typically provided with five to 15 minutes of battery backup at full load. The majority of these systems in a critical environment are backed up with a standby generator. If the generator is also serving life safety loads, as specified in the National Electrical Code Article 700, it must be running and providing alternating current power within 10 seconds of a power outage. Even if the generator is not designed for life safety, it can typically be up and running within 10 to 15 seconds after a power failure. Most of the flywheel UPS systems will supply 15 seconds of full-load power and can actually serve up to several minutes at less than full load. In addition, most of the utility disturbances will last for 5 seconds or less. For these reasons, a rotary or flywheel UPS can be a viable option over conventional battery backup systems.

A DC flywheel system can be utilized by itself or in combination with batteries. The DC flywheel would feed the inverter of a UPS system. This combination approach with a DC flywheel and batteries would represent higher first cost, but would provide for a longer life and potentially simpler maintenance. In addition, a system that only implements a DC flywheel requires a smaller footprint than a battery system. A conventional battery-powered UPS system that is augmented by a DC flywheel could serve the majority of utility outages—typically lasting for five seconds or less—through the flywheel and not the batteries. This would greatly increase the life of the batteries.

Other advantages of a flywheel (kinetic energy) system in lieu of a battery system include the following:

• Flywheel reliability is typically greater than a single battery string.
• A flywheel requires less maintenance than battery systems.
• Flywheel UPS systems do not require the controlled environment that a UPS battery system requires. A battery system must be kept close to 77ºF for good performance and life expectancy. In addition, a battery system can also represent a risk of explosion or acid spill.
• A flywheel will take up less space than a UPS battery system.
• A battery system can require spill control and neutralization and hydrogen sensors. Eye wash stations can also be required with battery installations. In addition, the battery system should be continuously monitored to ensure top performance and life expectancy.

The rotational speed of the flywheel (kinetic energy) has a dramatic effect on the amount of stored energy available for critical loads. Doubling the rotations per minute of the flywheel will quadruple the available stored energy. High-speed flywheel systems require a different design approach than low-speed systems. The former are typically made from carbon or carbon and fiberglass composite materials. These materials can withstand the higher stresses associated with the high-speed systems. In addition, these systems utilize magnetic bearings and vacuum enclosures to reduce rotational friction and system losses.

In a hybrid rotary UPS approach, a motor generator incorporates two fully rated power paths. The first path is through a conventional rectifier and inverter and the second path is around the rectifier and inverter, through a static switch to the motor generator. (See diagram below). In this situation, the rectifier continually provides power to the batteries, but the power is normally regulated and conditioned through the motor generator. The rotating inertia of the motor generator will provide a power ride through for brief utility power interruptions. The motor generator provides for true power isolation. No utility power disturbances pass through to the critical load. When the main power fails, the DC batteries provide power through the inverter and to the load through the motor generator. The inverter is normally off in this situation. The benefits to this design scenario include the following:

• The system provides for two conditioned paths of power.
• The system can provide for two independent power sources. The batteries are only utilized if both paths of power fail.
• The hybrid system can have a greater overload capability.
• The hybrid uninterruptible power supply system approach can offers high fault clearing ability without going into bypass.


This diagram represents a hybrid approach. The motor generator provided continuous conditioned power to the load. The rotating inertia of the motor generator will provide a power ride through for brief utility power interruptions. The inverter will only operate when the power fails for more than a brief interruption and the generator is in the process of starting.

Another UPS system approach is called kinetic power cell technology. The system offers a line-interactive UPS system. Voltage transients are suppressed through the transient voltage surge suppressors. When the system senses a voltage sag, the system takes energy from the flywheel to maintain the output voltage. These systems are matched with the generator to provide for seamless power. These systems claim a UPS system efficiency of 96% to 97%. These systems indicate that there is no restriction on the number of energy discharges. In contrast, a large number of energy discharges on a battery system can reduce life expectancy.

Moreover, flywheel UPS are "generator friendly". By reducing harmonic distortion and by eliminating block loading, the generator systems may not have to be oversized when feeding a flywheel UPS. This is typically not the case with battery UPS. Due to uninterruptible power supply system efficiency losses, the harmonic distortion created by the UPS system as well as the potential simultaneous charging of the battery supply after discharge and serving the critical loads, a generator feeding a battery UPS system may have to be oversized. Voltage distortion can be the result of a heavily loaded generator feeding a large UPS system that creates harmonic distortion.

Some of the flywheel UPS manufacturers indicate that a short ridethrough of 15 seconds can be adequate in lieu of the traditional 15 minutes typically provided in a battery UPS if the system is designed with higher reliability. The intent of the argument is that a highly reliable data center is counting on the generator to start the first time, every time.Strict maintenance and redundant starting circuits can ensure that optimum reliability is attained. In addition, redundant generators are typically designed into a high end data center.

This approach may not be appropriate in a typical Tier I data center or facility installation with a single standby generator. In addition, these installations will typically not have a 24-hour maintenance and operation staff that follow a rigorous fuel and battery system maintenance protocol. Generator starting reliability in these types of facilities is not going to be as high as in a Tier IV data center.

These manufacturers further indicate that the conventional wisdom is that a 15 minute backup system provided with a battery UPS system will allow time for an orderly shutdown and additional cranking of the generator. The argument against this conventional wisdom is that a 15 minute orderly shutdown will still result in an unacceptable loss of load.

Furthermore, if the generator does not start within the first few seconds, the chances are that it will not start within 15 minutes. In addition, flywheel UPS vendor literature indicates that the reliability of VRLA batteries drops off considerable two to three years into the life of the UPS system. This in and of itself can reduce reliability of the battery system over the flywheel option. One study indicates that batteries cause 70% of the failures in a conventional battery operated uninterruptible power supply system.

Generator starting reliability can be improved when a flywheel system provides 24 volts DC to the generator starting system. The power supply from the flywheel system to the generator starting system can be monitored by the UPS system to add even greater starting reliability.

The design engineer should understand the owner's objectives, maintenance and operations procedures and comfort level concerning back up times. With this information at hand, the rotary or flywheel UPS system options do represent a viable solution and should be considered on future projects.

Flywheel vs. Battery

Comparison Matrix

Active Power CleanSource® Battery-based Alternatives

Flywheel Technology

VRLA
(10 year)

VRLA
(20 year)

Flooded
(20 year)

Life Span

• Design: 20+
• Operational: since 1997
• Design: 10 in float service
• Operational: 3 to 6, typical
• Design: 20 in float service
• Operational: 10 to 15, typical
• Design: 20 in float service
• Operational: 10 to 18, typical

Discharge Cycles

• Unlimited for product life span • 1000-2000 shallow
• 100-200 deep
• 2500-5000 shallow
• 250-500 deep
• 2500-5000 shallow
• 250-500 deep

Optimal Temp (deg C)

• -20 to +40 • 25 • 25 • 25

Maintenance

• Air filters: as req.
• Oil Change: 12 mos.
• Bearings: 30 mos.
• Preventative maintenance: 3 to 6 mos.
• Jar replacements: as req.
• Preventative maintenance: 3 to 6 mos.
• Jar replacements: as req.
• Preventative maintenance: 3 to 6 mos.
• Jar replacements: as req.

Predictability

• Self Diagnostics: standard
• Monitoring software & cards: optional
• Requires battery monitoring system • Requires battery monitoring system • Requires battery monitoring system

Footprint (w/ service access)

• 500kW =>
• 20 sq.ft.
• 500kW =>
• 60-80 sq.ft.
• 500kW =>
• 100+ sq.ft.
• 500kW =>
• 200+ sq.ft.

"Green" Technology

• No environmental hazards • HazMat disposal issues
• Spill containment
• Personnel safety
• EPA regulations
• HazMat disposal issues
• Spill containment
• Personnel safety
• EPA regulations
• HazMat disposal issues
• Spill containment
• Personnel safety
• EPA regulations
• HVAC requirements

Rudy

Register to Reply Score 1 for Good Answer
Guru
United Kingdom - Member - Indeterminate Engineering Fields - Control Engineering - New Member

Join Date: Jan 2007
Location: In the bothy, 7 chains down the line from Dodman's Lane level crossing, in the nation formerly known as Great Britain. Kettle's on.
Posts: 32175
Good Answers: 839
#21

Re: UPS

08/12/2024 10:29 AM

A1) This is a matter of discussion with the end user(s).

A2) This is a matter of discussion with the end user(s).

A3) Use the electrical standards prevailing in the country of installation. In the UK, BS7671 applies, for example.

__________________
"Did you get my e-mail?" - "The biggest problem in communication is the illusion that it has taken place" - George Bernard Shaw, 1856
Register to Reply
Register to Reply 21 comments

Good Answers:

These comments received enough positive votes to make them "good answers".

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Copy to Clipboard

Users who posted comments:

Abbas (1); AndyinHawick (1); Anonymous Poster (4); ashoktoshniwal (1); Chankley (1); CowAnon (2); j_kamal (2); MUKULMAHANT (1); PWSlack (1); Sparkstation (3); user-deleted-1105 (3); V.I.Abraham (1)

Previous in Forum: variable voltage source for 0 - 5VDC   Next in Forum: SLIM (1937)

Advertisement