Purpose of Parallel Transformers - example

02/23/2008 10:10 AM

Could someone please give an example of paralleling XFORMERS and why they are utilized? I know at our utility we will do it for critical/large loads (like a couple of hospitals I know have 2000 kVA XFORMERS connected in parallel.). I know that we use J-BOXES for the connection point(which is smaller than a Primary PullBox).

Maybe someone could throw in a screen shot?


Thanks

__________________
gisdude
Register to Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.

Good Answers:

These comments received enough positive votes to make them "good answers".
4
Guru
New Zealand - Member - Interested in everything- see my Profile please APIX Pilot Plant Design Project - Member - Member Engineering Fields - Electrical Engineering - Member Engineering Fields - Power Engineering - Member Engineering Fields - Civil Engineering - Member Hobbies - Musician - Autoharp and Harmonica Hobbies - Hunting - Member Hobbies - Fishing - Member

Join Date: Nov 2007
Location: Christchurch, (The Garden City), South Island, New Zealand
Posts: 4395
Good Answers: 230
#1

Re: Purpose of Parallel Transformers - example

02/24/2008 3:24 AM

Hello GISdude

Parallel Transformers are used so that in case of a transformer failure, there is power still available, on a reduced level, for the load.

It is extremely important that the transformers are designed, and are connected in the same phase angle/vector angle = Dyn11, Dyn22 and so on.

It is normal for large Hospitals, which require large amounts of power in critical areas 24/7, that no cut in supply level is made.

Hospitals generally also have one or more Diesel Alternator units, which may supply power through the Essential Switchboards located next to the non-Essential Switchboards throughout the Hospital.

So in a hospital, Essential loads would include the following:

  1. Surgery Theatres
  2. Critical wards
  3. Boiler house
  4. Gas Supply = Oxygen and so on
  5. Circuits with Computers
  6. Circuits with patient monitoring equipment
  7. XRay
  8. Cat Scan
  9. Emergency Lighting
  10. 1 mains outlet per room, marked "Essential"
  11. HVAC Equipment
  12. And so on

Unable to give you screen shot/s, but the pair or more of identical Phase angle/vector angle transformers are just connected in parallel.

Protection Relays are very carefully set, so that in case of a fault, the transformers drop off one by one, with Circuit Breakers disconnecting the faulty Transformer and/or Circuits as required, then switching back on the OK transformers, via discrimination relays.

All that above normally is set to happen in under a second.

Meanwhile the Diesel Alternator system has cut in, at first fault indication, generally taking around 5 seconds to supply the Essential load, in parallel with the remaining transformer/s, if there are any, and that Alternator normally is set to shut down some 10 minutes after the power system stabilises.

Major Hospitals normally have an identical pair or more, of Emergency Diesel Alternator units, set to automatically start and switch onto supplying the Essential Load as required.

Major Hospitals will normally have a High Voltage Supply from 2 feeder cables, at 11kV, 33kV and once again the reason is to retain a power supply to the Hospital Main Switchboard, in case of fault/s.

The Protection Relay Systems for a large Hospital Complex, are quite sophisticated, requiring careful calculations, and normally being originally set with faults simulated via special Potential and Current Transformers, so that the Electrical Engineers know the system is as fail-safe as possible.

The J-Boxes you use will be smaller than the "Primary Pullbox", because in most cases the power supplied from a pair of identical transformers is equal.

This in practice, only very small mis-match currents actually flow through the J-Box, unless a major outage occurs in one transformer.

I hope your understanding of the situation is improved.

Advise further if I missed something you need to know.

Kind Regards....

__________________
"The number of inventions increases faster than the need for them at the time" - SparkY
Register to Reply Good Answer (Score 4)
Guru

Join Date: Jul 2006
Location: "Dancing over the abyss."
Posts: 4884
Good Answers: 243
#2
In reply to #1

Re: Purpose of Parallel Transformers - example

02/24/2008 4:36 PM

Great reply!

milo

__________________
People say between two opposed opinions the truth lies in the middle. Not at all! Between them lies the problem, what is unseeable,eternally active life, contemplated in repose. Goethe
Register to Reply
Power-User

Join Date: Oct 2006
Location: Kolkata, India
Posts: 447
#3
In reply to #1

Re: Purpose of Parallel Transformers - example

02/25/2008 7:24 AM

Well, Let me raise one point. Paralleling of transformer will increase the flow of fault current in the secondary side switchgear /distribution board/J Box bus. The design should permit to withstand the sckt current. This is very important specially in hospital, where we do a lot to maintain uninterrupted power supply.

I have seen, in hospital they keep two 'HOT' line power supply, One UPS supply, One AMF operated DG set. Thus the 'Redundancy' (a very technical term) is 3 fold. This is special requirement for OT.

__________________
BNDas
Register to Reply
Register to Reply 3 comments

Good Answers:

These comments received enough positive votes to make them "good answers".
Copy to Clipboard

Users who posted comments:

biswanath.das (1); Milo (1); Sparkstation (1)

Previous in Forum: HOW TO SELECT CU & DF   Next in Forum: Fault Calculation for DG

Advertisement