Anonymous Poster

Fault Calculation for DG

02/24/2008 12:36 AM

If I have running DG on load and short crt. happens and If I have DG ready for suuply but not load connected and then short circuit happens, in both the cases fault calculation will differ?????????

Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.
Guru

Join Date: Jun 2007
Location: chennai,India
Posts: 592
Good Answers: 19
#1

Re: Fault Calculation for DG

02/24/2008 1:37 AM

Irrespective of the load, the fault current fed by the generator would be same.if the load is connected and if the load is motor load then there will be some contribution of fault current from the motor.

__________________
Ramesh,Freelance Electrical/automation Consultant
Reply
Associate

Join Date: Nov 2007
Location: Indonesia
Posts: 29
#2

Re: Fault Calculation for DG

02/24/2008 11:11 PM

It's a simple I=V/Z relation. If the Z changes, then I will change also.

__________________
"I know less than all, but more than many who know less"
Reply
Power-User

Join Date: Oct 2006
Location: Kolkata, India
Posts: 447
#3
In reply to #2

Re: Fault Calculation for DG

02/25/2008 7:29 AM

Fault calculation procedure will be the same but fault current will be different due to load impedence as well as momentary contribution of motor load which acts as generator at the instant of fault.

__________________
BNDas
Reply
Anonymous Poster
#9
In reply to #2

Re: Fault Calculation for DG

12/03/2009 3:30 AM

Thats not true at all , at the point where the fault happens current flows and it flows from the source , since fault doesnt depend on load it depends on source , only if motor is connected load , due to sudden dip in voltage and inertia of the rotor the motor starts acting like a generator for sometime then is such a case fault current will be addtion of fault supplied by the source and this motor acting as a generator.

Reply
Anonymous Poster
#4

Re: Fault Calculation for DG

02/25/2008 12:17 PM

The fault level in terms of KVA or MVA will be the same and determined the generator capacity and other parameters.However fault current will vary at different locations depending upon the impedance in between the generator and the fault location.

Reply
Anonymous Poster
#5

Re: Fault Calculation for DG

04/20/2008 6:21 AM

i have 380 KVA DG set make by KIRLOSKAR, i don't Know the impedence of DG but i know the lenth of the cable from DG to LT panel. it is 3.5*400sqmm AL*2R lenth is 50 m each. now tell me what is Fault level of DG breaker in LT panel

Reply
Anonymous Poster
#6
In reply to #5

Re: Fault Calculation for DG

04/20/2008 6:22 AM

plz help me

Reply
Guru

Join Date: Jun 2007
Location: chennai,India
Posts: 592
Good Answers: 19
#7
In reply to #6

Re: Fault Calculation for DG

04/20/2008 9:38 AM

Generally the % impedancew will be between 10 and 14 %

For 10 % impedance the fault current at the generator terminal would be 4.9 kA and it will be 4.7 kA after 50 met of cable of 2 runs 3.5 x 400 sq.mm Al cable

For 14 % impedance the fault current at the generator terminal would be 3.5 kA and it will be 3.4 kA after 50 met of cable of 2 runs 3.5 x 400 sq.mm Al cable

__________________
Ramesh,Freelance Electrical/automation Consultant
Reply
Anonymous Poster
#8
In reply to #7

Re: Fault Calculation for DG

06/13/2008 8:01 AM

Can you please tell me the formula used for above calculation?

Thanks

Reply
Anonymous Poster
#10
In reply to #5

Re: Fault Calculation for DG

02/12/2010 5:31 AM

It is important to know the sub transient impedance of D.G. set ie ZSq=Xd'Sq+RaSq.And Isc=Rated voltage/Z.

Reply
Anonymous Poster
#11

Re: Fault Calculation for DG

07/20/2010 2:58 AM

yes but obvious.............

Reply