A 400V,3Ph+N, 50Hz, Isc=50kA/1Second, In=400A, MCC panel with two incoming power sources is required. Interlock 1 of 2 is required and no bus-coupler is to be considered by costumer. The control voltage is supplied from 220V DC un-interruptible Power supply. Contract standard is IEC.

Similar to this, is a 230V, 1Ph, Isc=10kA/1Second, In=100A, distribution panel with two incoming power sources.

There are several methods for design of Auto change Over Scheme for example by using two contactors, by using auto change over circuit breakers, by two individual circuit breakers. But I don't have more detail information / experience about them.

I need experiments and advices of engineers or related useful links.

__________________
A thousand-mile journey begins with the first step.
Register to Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.
Guru

Join Date: Jun 2007
Location: chennai,India
Posts: 592
Good Answers: 19
#1

Re: Auto change Over Scheme

02/24/2008 7:01 AM

What do you want? Circuit/application.

You have already explained the function.

For MCC- since the rating is only 400 Amps, you can consider motorised MCCB with suitable electrical and mechanical interlock.Since there are two sources and seperate control supply,you should have two nos under voltage relays located in each of the incoming source

Alternatively you can consider two 400 A contactors with Switch disconnectors.the 400A contactors can be electrically and mechanically interlocked.


same logic will be applicable for 100 Amps DB

__________________
Ramesh,Freelance Electrical/automation Consultant
Register to Reply
Associate

Join Date: Sep 2007
Posts: 49
Good Answers: 1
#2
In reply to #1

Re: Auto change Over Scheme

02/24/2008 8:08 AM

Thank you dear ramvinod,

The already case was Medium voltage and with bus-coupler.

I think the contactor solution is cheaper than motorized MCCB. But 400 A contactors with Switch disconnectors combination can withstand 50kA/1S short circuit current? However a simple circuit will be useful for both cases.

__________________
A thousand-mile journey begins with the first step.
Register to Reply
Power-User

Join Date: Oct 2006
Location: Kolkata, India
Posts: 447
#3
In reply to #2

Re: Auto change Over Scheme

02/25/2008 7:33 AM

Check with Vacuum Contactor sckt level.

__________________
BNDas
Register to Reply
Guru

Join Date: Nov 2006
Posts: 729
Good Answers: 2
#4

Re: Auto change Over Scheme

02/25/2008 12:28 PM

The question need to be clearly stated.Any how wth what I have understood i think u can use contactors to change over.You will need a monitoring relay which will ensure change over and control sequence.RTU ATS panels are available these days.

__________________
To avoid crticism do nothing,say nothing,be nothing