Gas detection in heat exchanger

03/13/2008 11:57 AM

I have 25 natural gas rack ovens that are 250,000btu/hr. Yesterday I walked through the production break room and one of the bakers mentioned...quite casually(!!!)...that he smelled gas in the oven area. I went out to check and immediately found a very heavy fume concentration spread across a large area.

I went through the drill...emergency shutdown and personnel evacuation. And then after venting the area, went searching. What I found was very simple and very disturbing. One of the ovens that was out of cycle for the day (this particular product run needs 20 ovens) had a gas valve leaking past the seat when off. It had literally filled the heat exchanger and was coming out the exhaust port and, being heavy, making its way down to the floor. It's amazing we didn't have an explosion. If someone had switched this oven on, certainly death and destruction woud have followed. I'm actually pretty surprised one of the other ovens didn't spark it off.

Anyway...I'm going to install gas sensors and alarm panel in the area, that's the easy part.

The more difficult part is that I want a gas sensor installed into each of my heat exchangers to be used as a permissive for firing. I'm hoping someone here knows of a high temp sensor I can use... I did some preliminary searching but haven't come up with anything yet.

Does anyone know of a sensor or supplier that would suit this purpose?

__________________
Speed doesn't kill. Sudden stops, brick walls, and old ladies in Buicks do.
Register to Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Guru
Hobbies - CNC - New Member Hobbies - DIY Welding - New Member Engineering Fields - Electromechanical Engineering - New Member

Join Date: Aug 2007
Posts: 23647
Good Answers: 420
#1

Re: Gas detection in heat exchanger

03/13/2008 1:05 PM

Switchman,

I assume you check industrials suppliers for sniffers.

I also assume you follow NFPA 86 for start up, might be a good idea to review it,

I do it, keeps me updated and less complacent?

Your very lucky, on a tangent since this oven was not in use do you not have a main manual shut off for this oven when not in use?

phoenix911

__________________
“ When people get what they want, they are often surprised when they get what they deserve " - James Wood
Register to Reply
Power-User

Join Date: Aug 2007
Location: San Francisco Bay Area
Posts: 266
Good Answers: 21
#3
In reply to #1

Re: Gas detection in heat exchanger

03/13/2008 3:00 PM

Phoenix911,

Thanks for your reply. I do have a couple of good Bacharach sniffers and a full range of test equipment such as combustion gas analyzers, pressure testers, flame circuit meters, etc. I have both a weekly and monthly PM where all safeties are verified, CO ppm and % of O2 is checked and adjusted, and everything is cleaned.

I have a copy of NFPA 86 on the shelf next to me, and portions as part of a quarterly training session, as well as a link to the online version in my list. We do several inspections every year ranging from the local fire captain to our insurance guy.

I do have two manual shutoff valves on each unit. One on top, 6" down of the main line. Then I have one right before the electrically operated gas valve. After yesterdays situation I have my guys going out and shutting off the manual valve until I can resolve this.

But I still want to add a gas sensor permissive to the pre-ignition safeties. I don't believe the pre purge...at 30 seconds...would have cleared this exchanger.

__________________
Speed doesn't kill. Sudden stops, brick walls, and old ladies in Buicks do.
Register to Reply
Guru
Hobbies - CNC - New Member Hobbies - DIY Welding - New Member Engineering Fields - Electromechanical Engineering - New Member

Join Date: Aug 2007
Posts: 23647
Good Answers: 420
#4
In reply to #3

Re: Gas detection in heat exchanger

03/13/2008 3:20 PM

Switchman,

sounds you have the safety in place, although purge is only a safety proceedure, it does not solve or detect your leak,

And as you know the purge is not time constraint but air exchange believe it to be 4x volume, (do not have NFPA 86 at my side at this time, so this is off of my memory, and not a reliable source)

May have to reprogram your logic, sorry I was'nt any help.

good luck,

phoenix911

__________________
“ When people get what they want, they are often surprised when they get what they deserve " - James Wood
Register to Reply
Guru
Hobbies - CNC - New Member Hobbies - DIY Welding - New Member Engineering Fields - Electromechanical Engineering - New Member

Join Date: Aug 2007
Posts: 23647
Good Answers: 420
#6
In reply to #3

Re: Gas detection in heat exchanger

03/13/2008 3:59 PM

Sorry, guess I was'nt trying too hard for you,

These people have been good to me,

http://www.eclipsenet.com/products/products.aspx?pid=259780

__________________
“ When people get what they want, they are often surprised when they get what they deserve " - James Wood
Register to Reply
Power-User

Join Date: Aug 2007
Location: San Francisco Bay Area
Posts: 266
Good Answers: 21
#7
In reply to #6

Re: Gas detection in heat exchanger

03/13/2008 4:30 PM

I'll dig through eclipsenet and see if they have a sensor.

NFPA 86 sec 8.4 does call for a pre-ignition time...but I can find no specific time period, mine is 30s. The next line down calls for at least 4 standard cubic feet (scf) of air or inert gas to be introduced during the purge. Although,I have not calculated out...I'm sure all this is as it should be. My ovens don't cough, sputter, rumble, or worse...backfire on start.

I have flow 'sail' switches in my burners as well as diaphragm pressure switches for constant burner air blower monitoring.

These units have been in service plenty of time...work great and we put lots of product through. I just want to prevent ignition in the situation like yesterday. No way pre purge would have cleared this.

__________________
Speed doesn't kill. Sudden stops, brick walls, and old ladies in Buicks do.
Register to Reply
Guru
Hobbies - CNC - New Member Hobbies - DIY Welding - New Member Engineering Fields - Electromechanical Engineering - New Member

Join Date: Aug 2007
Posts: 23647
Good Answers: 420
#8
In reply to #7

Re: Gas detection in heat exchanger

03/13/2008 5:14 PM

off on a tangent, the reason I mentioned purging.

I had designed a pizza tunnel oven about (2) years ago. with customed ceramic burner tubes. (seven burners @500,000btu/hr and seven tubes). and had supplied the subcontractor that was to fabricated this oven as well as the tubes and they made up the tubes and sat it for approx. six months. On start up due to delays because the plant was not ready I was to do the start up and commission the day before the first production run. All when well, and 5:00 I sent home our installer and fabricators. (internal company issues) I was shutting down the oven feeling good. When the dam thing barked and I saw dust raise on the other side.

When it cooled down, I found that the subcontractor that did the tubes pulled all the forms out except one, Which was in the instructions. (the ceramic was still green ("wet"). As the moisture turned into the steam. the forms kept it contain until it collapsed.

One good thing, My blow out doors worked great for that section.

worked all night to to bring it online, with only 4 of the 7 burners going. (one because of the tube, one because of a faulty valve, and one because of a problem with the blower. Because of the redundancy I had design into the oven. When the day was over, I briefed the customer that only 4 of the 7 burners where working, They didn't even know that.

Since I talked to them last. about 3 months ago, they have been running it pretty much 24/7, no shut down for clean up or maintenance (abuse). but their time is coming.

good luck,

phoenix911

__________________
“ When people get what they want, they are often surprised when they get what they deserve " - James Wood
Register to Reply Off Topic (Score 5)
Participant

Join Date: Jul 2007
Location: Darkest Africa
Posts: 3
#2

Re: Gas detection in heat exchanger

03/13/2008 2:29 PM

You didn't specify the temperature in your heat exchangers. By natural gas, I presume you mean methane...........

Have a look at http://www.tectra.hu/pdf-docs/Thermox-WDG-iv_atex_6-06_lo.pdf

This is probably overkill (1600oC!) for a bakery operation. If so, you will have to extract a continuous gas sample from each oven, cool it down to an acceptable temperature - around 60oC - (an interesting little engineering exercise itself) and run the samples through conventional sensors. Frontline Safety UK have a combustible gas detector rated up to 200oC but I don't know if methane is included.

Register to Reply Score 1 for Good Answer
Power-User

Join Date: Aug 2007
Location: San Francisco Bay Area
Posts: 266
Good Answers: 21
#5
In reply to #2

Re: Gas detection in heat exchanger

03/13/2008 3:51 PM

Yes, I think the natural gas is a mix of methane and other gases...not quite sure of the composition...but if necessary our utility will give me a breakdown, I'm sure.

These ovens have a max temp of 500o f so I would think a sensor rated for 1000 would be safe.

I looked at the file you attached and it's a bit different from what I'm after...I saw this one and it's more a flue gas process control. I have an account with Ametek so I'll send them an email also and see if they have something.

What I'm looking to do is essentially use a sniffer sensor in the exchanger so that if gas is present above a certain level (due to a leak) I will block ignition prior to igniting a bomb. The sensor will be disabled once I enable the ignition sequence.

__________________
Speed doesn't kill. Sudden stops, brick walls, and old ladies in Buicks do.
Register to Reply
Anonymous Poster
#9
In reply to #5

Re: Gas detection in heat exchanger

03/14/2008 4:23 AM

Hi¡

instead of measuring temperature you can use other 2 systems more reliables and quicker, these are ionization flame detection and UV (ultraviolet) flame detection,anyway you have to buy special gas controller and valve

Have a look at Honeywell

Sensors:

http://europe.hbc.honeywell.com/oem/combustion/residential_heating/gas/sensors.htm

Controllers: http://europe.hbc.honeywell.com/oem/combustion/residential_heating/boilers/boiler_electronics.htm

Register to Reply
Power-User

Join Date: Aug 2007
Location: San Francisco Bay Area
Posts: 266
Good Answers: 21
#10
In reply to #9

Re: Gas detection in heat exchanger

03/14/2008 10:35 AM

Sorry guest...you misunderstand...

You're talking just opposite of what I need. I currently have proper and correct ignition modules which have built-in µA flame sensing and control the valve.

The issue is that I had a gas valve leak into the exchanger when off. I need to put in a gas sensor. Prior to firing the oven off I will use the gas sensor in the exchanger to enable the firing cycle. If my oven is full of leaked fuel I do not want to fire it.

Thanks

__________________
Speed doesn't kill. Sudden stops, brick walls, and old ladies in Buicks do.
Register to Reply
Guru

Join Date: Dec 2006
Location: Hop around Toronto, New York & Karachi
Posts: 1876
Good Answers: 19
#11

Re: Gas detection in heat exchanger

03/15/2008 7:04 AM

Try Bacharach Inc. 625 Alpha Drive, Pittsburg, PA (412) 963-2000.

Fax (412) 963-2091

__________________
I not only use all the brains that I have, but all that I can borrow. Woodrow Wilson
Register to Reply
Anonymous Poster
#12

Re: Gas detection in heat exchanger

05/12/2008 8:01 PM

Don't know how often you check for CO etc , but you should perform a leakdowd test at the gas valve every 4 months or so(assuming you run the ovens 24/7).... [ monthly would be sweet ]gas valves are rated for about 100,000 cycles..then need to be replaced...I perform a leakdown test on all gas appliances , each time I service one , and write the date of the first test if I don't know the history of the equipment...I always run the model and serial# to see how old the unit is..and assume that the gas valve has never been changed..

As a side note...also get into checking your draft at the burner and at the draft inducer..should be pretty much equal..if you are .05 at the burner and .02 at the inducer...your heat exchanger is is impacted (obstructed) and needs to be cleaned..

Register to Reply
Register to Reply 12 comments

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Copy to Clipboard

Users who posted comments:

Anonymous Poster (2); ducon (1); Old Colonial (1); phoenix911 (4); Switchman (4)