Anonymous Poster

MCB

04/20/2008 1:24 AM

MCB is rated for 6A, 230V A.C. Can it be used for 6A, 30V D.C.

Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.
Guru
United Kingdom - Member - Olde Member!! Engineering Fields - Instrumentation Engineering - New Member

Join Date: Jul 2006
Location: Dunstable, England
Posts: 2821
Good Answers: 45
#1

Re: MCB

04/20/2008 7:54 AM

If its only 30 volts dc then yes!

__________________
A little knowledge is a dangerous thing - Googling is far worse!
Reply
Guru
United States - Member - New Member Engineering Fields - Power Engineering - New Member

Join Date: Sep 2006
Location: California, USA, where the Godless live next door to God.
Posts: 4665
Good Answers: 804
#2
In reply to #1

Re: MCB

04/20/2008 11:13 PM

Only if it has a rating for switching DC.

__________________
** All I every really wanted to be, was... A LUMBERJACK!.**
Reply
Guru

Join Date: Oct 2006
Location: Surrey BC Canada
Posts: 1571
Good Answers: 42
#3

Re: MCB

04/21/2008 12:52 AM

What is the application?

Highly inductive loads can be a challenge.

Sometimes a cap across the contacts can let the contacts open before any significant voltage developes.

Reply
Participant

Join Date: Aug 2007
Posts: 3
#4

Re: MCB

04/21/2008 3:38 AM

You also need to check what power source you are using, I have had problems with a current limited power supply folding the current down before the CB trips resulting in power loss to all other circuits. The tripping times of the Cb also apear to be changed by the lower voltage, this might be dependant on the cb type and manufacturer.

Reply
Power-User

Join Date: Jan 2007
Location: Johannesburg, South Africa
Posts: 230
Good Answers: 16
#5

Re: MCB

04/21/2008 8:25 AM

As stated by others, if not highly inductive - yes. Best to use DC CBs when you can, but we've used AC CBs at a pinch and they do seem to last. I vaguely recall an old electrician's rule of thumb that you should reduce either the volts or the amps by a factor of around 10 to be safe. We've also often used 2-pole CBs, and connected both in series to effectively halve the voltage seen by each "switch". Yeah, I know about timing & such other things, but in practice it seems to work for the lower voltages. (I normally work with 3kA, 3kV circuit breakers or contactors, which are rather bigger and more specialised!)

Just a word of warning, if these CBs eventually fail due to contact wear, they do so rather spectacularly if you have big battery backup, due to no natural zero-amp point as in AC to extinguish the arc. So I would not recommend it to protect equipment that could see it tripping or being isolated/switched off too often, nor should you have anything flammable close by..

Reply
Power-User
Technical Fields - Education - New Member Technical Fields - Technical Writing - New Member

Join Date: Sep 2006
Posts: 367
Good Answers: 1
#6

Re: MCB

04/21/2008 10:13 PM

NO

Reply
Guru
Hobbies - HAM Radio - CE3AM....4X4SW....CE3NSW

Join Date: Aug 2006
Location: Santiago Chile.
Posts: 845
Good Answers: 7
#7

Re: MCB

04/25/2008 6:37 PM

NO

DC has totally different arcing behavour... A DC breaker will usually be rated at 30% lower tripping point as specified for an AC breaker. in your case it will be approx 4 Amp. for the same voltage rating. For lower voltage rating as is in your application, it might be little lower due to possibly lower arcing point.

My stupid question is: Why not use the correct MCB?

Wangito.

__________________
Never trade luck for skill.
Reply
Guru

Join Date: Oct 2006
Location: Surrey BC Canada
Posts: 1571
Good Answers: 42
#8
In reply to #7

Re: MCB

04/26/2008 12:01 AM

Almost any 230vac CB will have an interrupting capacity of 30ka AC. The trip setting can be very much lower. The catalog will list the DC interrupting capacity if it has been rated.

Again, we always miss the details.

If we had the CB part number and manufacturer we could give a proper answer.

For regen DC drives it is quite common to use an "AC" mag only (special low trip point) 600v MCB and put all 3 phases in series. And that is for 500V armatures.