We have to locate a phase to ground fault on a 33 kv underground cable (23km long) which has one phase grounded.

We have used a surge tester with not much joy.

Mr. Google was not of much help either.(i could find fault range upto 3 km)

Has anybody used any equipment which pinpoints the distance of the fault from the end of the cable?

If yes..then a link to that product will be appreciated.

Cheers.

__________________
He must be very ignorant as he answers all the questions he is asked. Voltaire
Register to Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.
Guru
Technical Fields - Architecture - New Member Popular Science - Weaponology - New Member Engineering Fields - Control Engineering - New Member Engineering Fields - Electrical Engineering - New Member Engineering Fields - Electromechanical Engineering - New Member Hobbies - Fishing - New Member Hobbies - Target Shooting - New Member Hobbies - Hunting - New Member

Join Date: Dec 2005
Location: Clemson, South Carolina
Posts: 1722
Good Answers: 18
#1

Re: Underground cable fault locator

04/21/2008 9:29 AM

Try this site for Fault Location in Transmission Lines

This unit measures up to 200 km.

__________________
We have met the enemy and he is us . . . Walt Kelly
Register to Reply
Power-User

Join Date: Aug 2007
Location: Bhopal India
Posts: 234
Good Answers: 5
#2
In reply to #1

Re: Underground cable fault locator

04/21/2008 10:53 AM

Thanks Bill but just checking the link..given by you..

http://www.hvtest.co.za/Company/PDF/Baur/IRG%203000.pdf

in this data sheet it says measuring range as 10m to 3 300 km.

(.) is missing as i doubt it could be 3,300 km.

cheers.

__________________
He must be very ignorant as he answers all the questions he is asked. Voltaire
Register to Reply
Guru
Technical Fields - Architecture - New Member Popular Science - Weaponology - New Member Engineering Fields - Control Engineering - New Member Engineering Fields - Electrical Engineering - New Member Engineering Fields - Electromechanical Engineering - New Member Hobbies - Fishing - New Member Hobbies - Target Shooting - New Member Hobbies - Hunting - New Member

Join Date: Dec 2005
Location: Clemson, South Carolina
Posts: 1722
Good Answers: 18
#6
In reply to #2

Re: Underground cable fault locator

04/21/2008 1:23 PM

I suspect the range is 3,300 km. The surprise is the 10 m minimum -- I would have suspected it to be more. That unit uses TDR (time domain reflectometry) and high voltage pulses injected into an impedance, ideally matched to the characteristic impedance of the cable for maximum power transfer. The impedance range is from 12 ohms to 2000 ohms, which tells me that if your cable is 350 mcm or larger, its characteristic impedance will be less than 2000 ohms.

__________________
We have met the enemy and he is us . . . Walt Kelly
Register to Reply
Commentator

Join Date: Mar 2008
Location: South Texas - SOMETIMES
Posts: 88
Good Answers: 4
#3

Re: Underground cable fault locator

04/21/2008 12:10 PM

I have had the best luck with Megger test equipment..

http://www.megger.com/common/documents/PFL40_DS_en_V02.pdf

Register to Reply
Guru
Canada - Member - Our strength is our diversity

Join Date: Jan 2007
Location: Canada
Posts: 1024
Good Answers: 40
#4

Re: Underground cable fault locator

04/21/2008 12:13 PM

I have done it two ways:

1. Echo location, Send a pulse from a frequency generator, monitor with a scope (synched to the pulse) for the electronic echo, calculate the distance travelled and divide by 2 (signal has travelled to the break and back)

2. Using a test machine designed on a half wave bridge rectifier, where the cable Impedance of the cable is matched. The machine was specifically designed and calibrated for the cable.

__________________
Perfection is a subjective and abstract concept.
Register to Reply
Member

Join Date: Apr 2008
Posts: 7
#5

Re: Underground cable fault locator

04/21/2008 12:26 PM

here is a thought,maybe using an underground cable locator on the grounded phase the only problem is that it would have to be de-energized.you connect the cable locator to the grounded phase and when you lose the signal that should be where the fault is.in the 70's we used similar technology for finding telephone cable faults.interesting problem let me know how it works out.

Register to Reply
Guru
Canada - Member - Specialized in power electronics

Join Date: Feb 2008
Location: Montreal, Canada.
Posts: 1372
Good Answers: 80
#7

Re: Underground cable fault locator

04/22/2008 12:00 AM

Feed enough power to it and the fault will be under the new volcano you will have created...

Seriously, what kind of precision are you looking for? If you have junctions boxes here and there, Flow a small current to it from a low voltage transformer and use a current clamp to locate the defective segment.

Or use a DC source and divide the voltage by the current. Use the resistance with the cable ohm/Km to calculate the approximate distance. Don't forget to add the resistance of the main cable to the resistance of the ground conductor.

You might get different results if it is a dead short than if it is a high resistance short.

Good luck.

__________________
Experienced is earned, common sense is taught, both are rare essentials of life.
Register to Reply
Guru
Canada - Member - New Member Hobbies - Musician - New Member

Join Date: Dec 2006
Location: Western Canada
Posts: 1863
Good Answers: 39
#8
In reply to #7

Re: Underground cable fault locator

04/22/2008 2:34 AM

I used this brand of equipment when I worked for a power utility .

http://www.radiodetection.com/products.asp?sec_id=2689

Call the sales rep and ask for a demo. Various fault types require different equipment. Radio Detection seem sto have th ebroadest applicability. I used them all from a "thumper" to a Rycom, to TDR, Metrotech and even dowsing rods.

Good luck!

__________________
Elnav
Register to Reply
Power-User

Join Date: Apr 2005
Location: Scotland
Posts: 164
Good Answers: 8
#9

Re: Underground cable fault locator

04/22/2008 5:14 AM

Noticed that your location is Saudi so the cable is probably under the sand between ends? A break of that magnitude may have left a mark on the surface or if you are really lucky you will find a very black JCB or a pair of smoking boots with a hacksaw next to them. Might be worth travelling the route and seeing if there has been any disturbance to the lie of the cable.

If you are using a high voltage tester such as a megger be very carefull to discharge the capacitance from the cable - I witnessed a near fatal accident where a technician went to unclip the megger after testing a 4km coax cable and received a 500V shock which left him unconcious for several minutes.

Register to Reply
Guru
Safety - ESD - New Member India - Member - New Member Engineering Fields - Energy Engineering - New Member

Join Date: May 2007
Location: Pune , India
Posts: 875
Good Answers: 42
#10

Re: Underground cable fault locater

04/22/2008 2:55 PM

I am using cable fault locating instruments of Aplab make for power and telephone cables. When there was emergency the company used to do the fault locating with their staff and equipments. They are very fast and most accurate. They have helped me to locate cable fault in many occasions and can certify that they can locate any faults very close range of few feet accurately.i have purchased their equipments also.

You can see the details of their equipments in the following link :-

http://www.aplab.com/cfl/cfl02.htm

Their contact detail is :-

Tel. : 91-022-25821861 Fax : 91-022-25823137 Email : response@aplab.com .

If you want any more details about any model or immediate availability I can be of help to you. No busyness please. Only friendly gesture ( if you feel that you want any help).

Register to Reply
Power-User

Join Date: Aug 2007
Location: Bhopal India
Posts: 234
Good Answers: 5
#12
In reply to #10

Re: Underground cable fault locater

04/22/2008 11:35 PM

Thanks everybody for the help. Thanks Abraham for your inputs.

We located the fault at 8km from the source. We used the ohm/km method (using wheatstone bridge).

No black JCB's or boots, or camels with missing legs... there was cable fault(most likely a manufacturing defect)

Cheers.

__________________
He must be very ignorant as he answers all the questions he is asked. Voltaire
Register to Reply
Guru
Safety - ESD - New Member India - Member - New Member Engineering Fields - Energy Engineering - New Member

Join Date: May 2007
Location: Pune , India
Posts: 875
Good Answers: 42
#11

Re: Underground cable fault locator

04/22/2008 3:03 PM

Surge Wave Receiver - Model SLE 90

Download Catalogue

SLE 90 is a highly sensitive instrument to exactly locate the fault point in a short time. It can be used on LT as well as HT networks effectively. The success of locating exact fault point on the underground cable depends on the search carried out on the lay of the cable. This calls for an indication to guide the operator to walk precisely on the route. The magnetic channel in dual LCD display indicates the strength of magnetic field on the ground surface. This helps the operator to reach the fault point in a short time.

High Voltage Test Instruments - Model HVG

Download Catalogue

Easy to perform HIPOT test Comprehensive safety features
Continuously adjustable output voltage Selectable current ranges
Built in auto discharge in case of mains power failure or instrument switch off Timer provision to switch off the instrument automatically after the preset period
Register to Reply
Guru
Hobbies - HAM Radio - CE3AM....4X4SW....CE3NSW

Join Date: Aug 2006
Location: Santiago Chile.
Posts: 845
Good Answers: 7
#13

Re: Underground cable fault locator

04/25/2008 4:09 PM

Can you disconnect power for a few minutes? I guess it is already disconnected...

If so look for a good TDR (Time Domain Reflectometer) It will give you the fault location in a matter of minutes...Tektronix makes excellent ones, And you can rent one for a day. some of them go as far as 30Km.

Wangito.

__________________
Never trade luck for skill.
Register to Reply
Register to Reply 13 comments
Copy to Clipboard

Users who posted comments:

Bill (2); chaterpilar (2); ekiechle (1); elnav (1); marcot (1); proffessorr (1); techno (1); tom (1); V.I.Abraham (2); wangito (1)

Previous in Forum: Current and Flux density   Next in Forum: "Electrical" Urgent please

Advertisement