Electron Man

04/25/2008 12:58 AM

On a 480/90 amp contactor and a 240 volts coil. I have a open coil, could I bump start the contactor by pushing in the contactor to see if the compressor will start.

Register to Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.
Guru
New Zealand - Member - Interested in everything- see my Profile please APIX Pilot Plant Design Project - Member - Member Engineering Fields - Electrical Engineering - Member Engineering Fields - Power Engineering - Member Engineering Fields - Civil Engineering - Member Hobbies - Musician - Autoharp and Harmonica Hobbies - Hunting - Member Hobbies - Fishing - Member

Join Date: Nov 2007
Location: Christchurch, (The Garden City), South Island, New Zealand
Posts: 4395
Good Answers: 230
#1

Re: Electron Man

04/25/2008 1:36 AM

Hello vcummings

If you value your eyesight, facial skin, hair and possibly your life, do not attempt manually pushing the contactor.

It is not possible to reliably close the contactor contacts, and hold them in position by hand, since the electrical operation normally takes only a few thousandths of a second.

Secondly, there is normally a chain of safety or control switches in the circuit to the contactor coil, and one of those safety or control switches may presently be operated, and your manual operation attempt would bypass all safety devices.

You are risking a lovely explosion and subsequent fireball rated at more than 480 Volts 3 Phase 90 Amps, = 129,000+ Watts, and much more on short circuit, perhaps 500kW fault surge, if you attempt manual operation.

A large fault surge may destroy the contactor, switchboard, and your good self, in less than a second.

Safely test all circuitry, coils and the like, remove from supply before manual operation of that contactor, to see if there is some physical reason for the non-operation.

Remember that some contactors are mechanically and electrically interlocked with others, at various stages of normal operation.

Hope you read this, before you attempt the manual operation of that contactor, and are not presently needing a wooden overcoat.

Kind Regards....

__________________
"The number of inventions increases faster than the need for them at the time" - SparkY
Register to Reply
Guru
United Kingdom - Member - Indeterminate Engineering Fields - Control Engineering - New Member

Join Date: Jan 2007
Location: In the bothy, 7 chains down the line from Dodman's Lane level crossing, in the nation formerly known as Great Britain. Kettle's on.
Posts: 32175
Good Answers: 839
#2

Re: Electron Man

04/25/2008 8:01 AM
__________________
"Did you get my e-mail?" - "The biggest problem in communication is the illusion that it has taken place" - George Bernard Shaw, 1856