hi gang, i have 208/120 volt 3 phase in building, need to step up with 208/120 volt to 480 volt 3 phase, 3 wire 75 kva transformer, should i ground the center point of the 208 to ground? what could happen i don't ground it? thanks

Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.
Member

Join Date: May 2008
Posts: 5
#1

Re: pewe

05/09/2008 1:25 AM

Dear sir,

It is not necessary to ground the primary side(208)because the connection of transformer is DELTA - STAR in such case secondary side (480) need to solidlyground(earthed) for neutral purpose not primary(208)

Reply Off Topic (Score 5)
Guru
New Zealand - Member - Interested in everything- see my Profile please APIX Pilot Plant Design Project - Member - Member Engineering Fields - Electrical Engineering - Member Engineering Fields - Power Engineering - Member Engineering Fields - Civil Engineering - Member Hobbies - Musician - Autoharp and Harmonica Hobbies - Hunting - Member Hobbies - Fishing - Member

Join Date: Nov 2007
Location: Christchurch, (The Garden City), South Island, New Zealand
Posts: 4395
Good Answers: 230
#2

Re: pewe

05/09/2008 1:41 AM

Hello Guest,

It is not the "Centre-point" of the windings, but a "Star Point", almost surely.

If it is a "Star Point", you do not need to ground it, but keep clear of it, as under certain conditions, it may rise above ground potential.

We are trying to analyse your situation via CR4 remotely, and you need to be very careful with what you are doing.

A proper description of the transformer would assist.

If you intend to run another transformer in parallel with the proposed one, ensure that the phase angles of the transformers are identical, or large circulating currents will result, and may destroy equipment.

Kind Regards....

__________________
"The number of inventions increases faster than the need for them at the time" - SparkY
Reply
Power-User

Join Date: Oct 2007
Location: Hartwell Georgia N34* 56.770 / W83* 35.431
Posts: 222
Good Answers: 1
#3

Re: pewe

05/11/2008 11:43 AM

No, you don't need to ground the primary side. Size your breaker correctly, bond all metal parts back to the distribution ground and use a 208/480 three phase transformer. Better yet, utilize a local contractor for the installation.

Good luck,