Flickering in Power System

05/09/2008 12:08 AM

Hi there,

what's the effect of high current in neutral line?

In our power system we found that ampere in neutral line reach 300 Ampere.

Curent each Phase ( R= 1800 S= 1700 T=1785 amp)

when Voltage dip / flickering about one second exist in our power system, ACB with neutral current immediately trip and it detect as a ground fault by ACB's protection relay. But after that we can reset the ACB, and every thing back to normal

My Question, Is it any relationship between high current in neutral with ground fault detected by ACB? Is the trip caused by high current in neutral line?

How to explain this case ?

Need help from the experd

Register to Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.
Guru
New Zealand - Member - Interested in everything- see my Profile please APIX Pilot Plant Design Project - Member - Member Engineering Fields - Electrical Engineering - Member Engineering Fields - Power Engineering - Member Engineering Fields - Civil Engineering - Member Hobbies - Musician - Autoharp and Harmonica Hobbies - Hunting - Member Hobbies - Fishing - Member

Join Date: Nov 2007
Location: Christchurch, (The Garden City), South Island, New Zealand
Posts: 4395
Good Answers: 230
#1

Re: Flickering in power system

05/09/2008 1:34 AM

Hello adrian

Is that <" Voltage dip / flickering about one second exist in our power system"> caused by internal load, is does that Voltage Dip arrive from outside the plant = from the High Voltage line to your local transformer/s?


Reply with

Kind Regards....

__________________
"The number of inventions increases faster than the need for them at the time" - SparkY
Register to Reply
Active Contributor

Join Date: Jan 2008
Posts: 17
#2
In reply to #1

Re: Flickering in power system

05/09/2008 2:25 AM

Voltage dip comes from external source (medium voltage size , 20 KV), and affect to our load.

cheer

Register to Reply
Anonymous Poster
#4
In reply to #1

Re: Flickering in power system

05/10/2008 3:14 PM

adrian; does this happen more on windy days? sound like a tree branch hitting the hi-

voltage power line, should be self trimming perry

Register to Reply
Guru
New Zealand - Member - Interested in everything- see my Profile please APIX Pilot Plant Design Project - Member - Member Engineering Fields - Electrical Engineering - Member Engineering Fields - Power Engineering - Member Engineering Fields - Civil Engineering - Member Hobbies - Musician - Autoharp and Harmonica Hobbies - Hunting - Member Hobbies - Fishing - Member

Join Date: Nov 2007
Location: Christchurch, (The Garden City), South Island, New Zealand
Posts: 4395
Good Answers: 230
#3

Re: Flickering in power system

05/09/2008 3:35 AM

Hello again, adrian

Your out-of-balance current is probably a reflection through your local plant transformer of a severe Voltage drop on a single one of the supply phases from your Electricity provider.

If you increased the size of your local transformer, perhaps by 10% or 15%, the reflection may not be as noticeable, because there would be more iron in the magnetic circuit to absorb the transient fault.

This is an expensive transformer increase, should you choose to make it.

If your Electricity provider often has this type of fault, you are going to get the reflected imbalance, and associated neutral current, as your local system tries to cope with the HT fault in the supply.

Without having your full plant and equipment details, along with complete schematics, I cannot properly advise you to alter the ACB Protection relay settings, because the settings are both a safety and Insurance issue, and "remote control via CR4" is not a good idea - If I was actually on-site then the advice may be quite different.

The settings would normally be specified in the initial Works Installation Manual, and they are set at what appears to be a reasonable amount, for protection of persons and equipment at the Works.

Can you establish which phase of the High Tension Supply line gets the Voltage drop fault?

If so, and it is always the same phase, either there is a faulty insulator/transformer or other equipment on that phase, branch of tree intermittently touching that phase, or lightning strike to that phase only, or some local interference - in all these cases, you should advise the Electrical Engineer of that Distribution Network, so that remedial action/s may be made.

Advise further, as needed.

Kind Regards....

__________________
"The number of inventions increases faster than the need for them at the time" - SparkY
Register to Reply