3 element boiler drum level control

05/31/2008 7:13 AM

Dear Sirs/frnds,

Pl let me know the 3 element boiler drum level control like, control loop,importance of math block, remote set point for slave controllers & many more related to boiler control loop.

Register to Reply
Pathfinder Tags: boiler drum level
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.
Guru
United Kingdom - Member - Olde Member!! Engineering Fields - Instrumentation Engineering - New Member

Join Date: Jul 2006
Location: Dunstable, England
Posts: 2821
Good Answers: 45
#1

Re: 3 element boiler drum level control

05/31/2008 8:07 AM

For someone calling himself 'instrumentation engineer' you seem to be lacking in instrumentation knowledge, or at least the basic art of describing what it is you want answered...

__________________
A little knowledge is a dangerous thing - Googling is far worse!
Register to Reply
Guru
Philippines - Member - New Member Engineering Fields - Instrumentation Engineering - New Member Engineering Fields - Control Engineering - Who am I?

Join Date: Oct 2006
Location: Northern Mindanao, Philippines
Posts: 2147
Good Answers: 53
#2

Re: 3 element boiler drum level control

06/01/2008 6:31 AM

What you're asking for could take up a whole chapter in an instrumentation handbook.

I suggest you google "boiler drum level control". I'm sure you'll find what you're looking for.

__________________
Miscommunication: when what people heard you say differs from what you said. Make yourself understood.
Register to Reply
Power-User

Join Date: Mar 2007
Location: South East of Las Vegas just far enough to see the lights but far enough to not hear the coins falling
Posts: 282
Good Answers: 8
#3

Re: 3 element boiler drum level control

06/01/2008 11:24 PM

From the field;

You are getting into the most critical area of boiler safety. 70% of all boiler failures (in the US) are caused by water lever control failures or improper maintenance. You my unknown friend should studying this very closely and then do not touch a system without a qualified individual with you. If you email me directly I will prove to best resource for this boiler control circuit.

Please do not alter any boiler circuit without help.

Respectfully,

miketheboilerguy@aol.com

__________________
Rule number one; Never ask a question unless you are prepared for an answer that you may not like.
Register to Reply
Associate

Join Date: Jan 2007
Posts: 35
Good Answers: 1
#4
In reply to #3

Re: 3 element boiler drum level control

06/02/2008 3:16 AM

I am giving below the write up for the Three element drum level control what we normally follow in our boiler.

THREE ELEMENT DRUM LEVEL (FEED WATER) CONTROL

1.0 Introduction:

In the boiler the steam flow changes according to the load demand from the turbine or from the process consuming the steam energy. To match the steam take off from the boiler, the feed water flow has to be increased or decreased as required. The feed water is automatically controlled by suitably positioning Feed Water Control Valve (FCV) provided in the feed water line at boiler inlet.

2.0 Three Element Feed water Control:

For automatic control of the feed water flow to the boiler, following three (elements) primary inputs are normally being considered.

2.1 Drum level.

2.2 Main Steam flow.

2.3 Feed water flow.

In addition, measurements of Drum Pressure, Main Steam Pressure and Main

Steam temperature are also taken for correction/compensation purpose as

detailed below.

Following paragraphs briefly explains how the feed water flow is regulated to match the steam demand from the boiler

3.0 Drum level measurement:

Two numbers of level transmitters (dP transmitters) one on left hand side and the right hand side of the Boiler Steam Drum are provided to measure drum level.

3.1 The two level signals from these transmitters are averaged and connected to a manual three-way selector switch. The other two inputs for the three-way selector switch are directly from the two transmitters. Normally the average signal is selected for the control. In case any problem with any one of the transmitters; the healthy transmitter is selected in the three-way selector switch for the control.

3.2 The functioning of two level transmitters is continuously monitored through a deviation monitor. In case of difference between the two level transmitters is higher than the preset value, and then the control is automatically transferred to Manual with an annunciation.

3.3 The selected drum level signal is compensated for density variation in the drum water due to pressure changes (actually due to temperature changes) in the drum, through a function generating with drum pressure signal.

4.0 Drum Level Control:

The compensated drum level signal fed to a reverse acting P I controller as process variable. This measured drum level is compared with set point and a correcting signal (with proportional plus integral action) is generated in the controller according the deviation between the measured process variable (drum level) and the set point.

5.0 Main steam flow measurement:

The dP Transmitter measures the dP across the ventury nozzle, provided in the main steam line (The dP measured is proportional to the square of the flow through the ventury nozzle and hence the square root of the dP taken as proportional to flow.) The measured dP is square rooted and compensated density variations due to change of Pressure and Temperature.

6.0 Feed water flow measurement:

The dP Transmitter measures the dP across the orifice fitting is provided in the Feed water line. The measured dP is square rooted to arrive at the feed water flow.

7.0 Feed water flow control:

The compensated steam flow is added with the corrected signal generated in the drum level controller. This sum is taken as the demand of feed water flow (cascade set point) for the boiler and compared with the actual feed water flow to the boiler. The deviation between the demand and the actual feed water flow, fed to the P & I controller. The processed out put from the controller is given to the final control element through a 'Hand selector switch' and an 'Auto – Manual station' – the Feed water control valve as positioning signal.

8.0 Single Element Control:

During low load operation, three-element control is not required. Drum level measurement with it's set point is adequate. Hence the output of the Drum Level Controller is directly given to the Feed water Control Valve through the selector switch provided after Cascade P & I Controller.

9.0 Auto Manual Operation:

An Auto Manual Control Station is provided as the last element of control system. Auto or Manual operation can be selected from the Auto Manual Selector Switch in this Control Station. If auto selected, the positioning signal from the selected controller (through Hand selector switch) will go to the Final control Element – Feed water Control Valve. If manual is selected, the controller's outputs are isolated and the Feed water Control valve can be positioned from this control station.

Raise/Lower push buttons are provided in this control station through which Feed water Control valve can be opened or closed as desired by the operator. Bump less transfer facility shall be built in as part of the Control Station to avoid sudden jump of control valve position during change over from auto to manual or vice versa.

10.0 Indications:

Normally Set point value indication, Deviation indication, Final Control element (Feed water Control valve) position indication and Process value indication are provided either part of the Auto Manual Control Station or separately.

11.0 Alarm and Trip signals: Low and high level alarm signals are generated from one for the transmitters output through software switches. However very Low and very high level trip signals (software switches) from both the transmitters output and also from the averaged/compensated signals are considered through an 'OR' gate. Signals from transmitters are also checked for the healthiness of the respective transmitters before connecting to the 'OR' gate.

Following are the Trip/Alarm Signals generated.

11.1 Transmitter deviation Alarm.

11.2 Drum level – Low Level Alarm

11.3 Drum level – High Level Alarm

11.4 Drum level – Very Low Level Trip

11.5 Drum level – Very High Level Trip

12.0 Hard Wired hooter

Following Trip/Alarm Signals are also hardwired to the Hooter, which is to be

mounted externally in control room.

12.1 Drum level – Very Low Level Trip

12.2 Drum level – Very High Level Trip

Register to Reply
Active Contributor

Join Date: May 2008
Posts: 14
#5
In reply to #4

Re: 3 element boiler drum level control

06/02/2008 4:22 AM

Hi Rajant,

The theoretical aspects u have given is too good, pl let me know the how much compensated steam flow added with the corrected signal generated in the drum level controller. COnsidering one example tel me.

Register to Reply
Guru
United States - Member - New Member Engineering Fields - Mechanical Engineering - New Member Popular Science - Weaponology - New Member Hobbies - Target Shooting - New Member Safety - ESD - New Member Technical Fields - Education - New Member

Join Date: Mar 2007
Location: Texas
Posts: 635
Good Answers: 20
#6

Re: 3 element boiler drum level control

06/02/2008 8:52 AM

RUN!

-A-

__________________
question everything
Register to Reply
Register to Reply 6 comments