In a Cable trench with Power & Control Cables what shall be elevation of Control Cables and what shall be for power cables?. Will the Power Cables in the bottom elevation and the control cables in the top elevation.
N.Suresh
Re: Cable Trench
06/12/2008 9:52 AM
What does the Client's Engineering Standards say on the subject?
It might be easier to put the 'heavier' cables on the bottom. These will probably be the first to go in and also those least likely to incur changes and additions.
Re: Cable Trench
06/13/2008 2:07 AM
Hi,
As you have rightly pointed out the higher sized power cable wiil be in the bottom and requires least maintanance wheras the control cable on the top may become faulty which needs replacement periodically.
N.Suresh
N.Suresh
Safety - ESD - Inspect all things, keep the good things safe! New Zealand - Member - PalmerstonNorth -hub of the Manawatu.
Re: Cable Trench
06/13/2008 1:19 PM
Do you plan to lay it flat or can you fit it onto a vertical cable tray if the trench is wide enough and lined with concrete?
Observe-Plan-Execute-Monitor-Control
Re: Cable Trench
06/16/2008 12:25 AM
Hi,
In a trench cable shall be laid horizontally. This normal practise. The verical tray shall be laid on the walls in a cable tray if the trench section is less. ie. On both the there shall be trays vertcally arranged with a walking spece between them.
The flat formant inside a trench will be for EHT Power Cables with support structures grouted on the floor. After necessary snaking considering the bending radii of the cable the it will be vertcaly laid with a support structure tio terminate in the respective equipement.
If you hav enay further doubt please revert.
N.Suresh