Automation Washing Station

06/25/2008 7:32 AM

i am doing one project "automating washing station" . i am using drives to run the motor and pump, a pressure transmiter , one pressure switch ,plc and controller.

my idea is i am setting pressure setpoint to 20 bar and run the pump , if the pressure reached setpoint the pump will automatically stoped. On testing when the pressure reached 20 bar i manually stop the motor , but the pressure is no maintained (the outlet valve is allready closed). And on pump side have one nonreturn valve. why it happen like that . any one please help . if my idea is not good one please tell me other way to do this project.

__________________
Mohammed Hilal
Register to Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Guru
United Kingdom - Member - Indeterminate Engineering Fields - Control Engineering - New Member

Join Date: Jan 2007
Location: In the bothy, 7 chains down the line from Dodman's Lane level crossing, in the nation formerly known as Great Britain. Kettle's on.
Posts: 32175
Good Answers: 839
#1

Re: please help me in this

06/25/2008 8:12 AM

So the pressure is not being maintained when the pump stops?

Congratulations. There is a leak somewhere. The system is losing fluid and the pressure dropping off is a symptom of that phenomenon.

__________________
"Did you get my e-mail?" - "The biggest problem in communication is the illusion that it has taken place" - George Bernard Shaw, 1856
Register to Reply Score 1 for Off Topic
Member

Join Date: Apr 2008
Location: sharjha
Posts: 9
#7
In reply to #1

Re: please help me in this

06/30/2008 12:38 AM

thanks for ur wise answer.

__________________
Mohammed Hilal
Register to Reply
Power-User
United States - Member - American by birth,southern by the grace of GOD Popular Science - Weaponology - you can't carry that! Technical Fields - Technical Writing - why can't I use a pencil? Hobbies - Target Shooting - New Member

Join Date: Jan 2008
Posts: 203
Good Answers: 2
#2

Re: please help me in this

06/25/2008 8:15 AM

I would install a pressure tank in the line down from the pump this will give you some capacity and keep the pressure constant in the line. I t will also keep the pump from starting and stopping frequently. This is a start.

__________________
The more complex the mind, the greater the need for the simplicity of play... If you think you can or think you can't you'll always be right
Register to Reply Off Topic (Score 5)
Guru
Popular Science - Weaponology - New Member United Kingdom - Member - New Member

Join Date: May 2007
Location: Harlow England
Posts: 16512
Good Answers: 670
#3

Re: Automation Washing Station

06/25/2008 9:16 AM

i can't see why you want to have the output closed, the pump stopped and maintain pressure.

If you want to wash then presumably you want jets of water...well run the pump!...
When you want the jets to stop..... simply ...stop the pump. You can have a pressure relief valve if you wish.

Del

__________________
health warning: These posts may contain traces of nut.
Register to Reply
Guru
Hobbies - Fishing - Old Salt Hobbies - CNC - New Member United States - US - Statue of Liberty - New Member

Join Date: Mar 2007
Location: Rosedale, Maryland USA
Posts: 5197
Good Answers: 266
#4

Re: Automation Washing Station

06/25/2008 1:13 PM

Check valve at output of pump most pumps will not hold pressure.

__________________
Life is not a journey to the grave with the intention of arriving in a pretty, pristine body but rather to come sliding in sideways, all used up and exclaiming, "Wow, what a ride!"
Register to Reply
Active Contributor

Join Date: Apr 2008
Location: Bangalore,India
Posts: 19
Good Answers: 1
#5

Re: Automation Washing Station

06/26/2008 1:49 AM

Sir,

Please check whether input from pressure switch setting is correct. In PLC [ladder diagram] please check the interlock of pressure switch and motor. The motor must switch off when the pressure is 20 bar. If possible use analog inputs for pressure switch. Please check online the PLC diagram and also when pressure switch reaches 20 bar the input must become 1.

__________________
Never never never give up
Register to Reply
Active Contributor

Join Date: Jun 2008
Posts: 16
#6

Re: Automation Washing Station

06/26/2008 10:17 AM

fundamentally, your initial test should not work even if you don't have a leak in the system. liquid is imcompressible. this is how the hydraulic system works. you must apply a force (no matter how small it is that required) to maintain the pressure in the constant volume system. therefore, as soon as you stop the motor, without any leaks, the small change in temperature alone is enough for the pressure to drop. on the other hand, if the temperature has not change yet, all it takes is a displacement of a few drops of water or the collapse of the air bubbles.

first, you should know that 20 bar (300#) is a lot of pressure. i am quite certain that you can take a lot of paint off with that pressure. but then, i don't know much about automatic washing station. also, be sure to check your design and calculate the total volume of the system and, then verify with your local jurisdiction for pressure vessel requirement that it is not required the installation of a pressure relief or a thermal relief of some sort.

in general, if you are trying to use the line pressure (sensing by the pressure tx) to regulate the drives to speed up or slow down the motor, it may and may not work for the following reasons. the liquid is imcompressible, meaning you cannot maintain a fixed pressure at 300# if there is no user. keep in mind, that double the speed of the motor (which will double the speed of the pump) will quadruple the power and the work done by the drive/motor/pump is directly proportional to the volume throughput. therefore, you may not have enough resolution and response on the drives to maintain the constant header pressure at low usage.

the pressure switch can be used as an auto shut-off to stop the pump under high pressure or you can use it as a auto start to start the pump under low pressure but you should not use one pressure switch with its deadband to autostart and autostop the pump due to reliability and safety.

Register to Reply Score 1 for Good Answer
Member

Join Date: Apr 2008
Location: sharjha
Posts: 9
#8
In reply to #6

Re: Automation Washing Station

06/30/2008 12:51 AM

if there is a drop in pressure the pump must starts. according to u one drop of water leak will decrese the pressure. if there is no leake did the pressure be constant.

__________________
Mohammed Hilal
Register to Reply
Active Contributor

Join Date: Jun 2008
Posts: 16
#9

Re: Automation Washing Station

07/02/2008 9:56 AM

you are talking about an ideal condition of isothermal compression, which you could never achieve, realistically. plus, the idea is to be able to deliver the wash water while the pressure remain constant.

If you settle for a little lower pressure, like less than 150psi (10bar), the cheappest and easiest way to accomplish this task, variable flow at constant head pressure, is to add a pressurized tank and an air compressor, which always comes with its own pressure set switch. the compressed air will maintain the water pressure. if you must deliver water at higher pressure, this set up is not economic because the air compressor will be costly due to multi-stages and intercooler.

with this configuration, both of the water pump and the air compressor are running intermittently, on demand only. and the fluctuation in the demand for wash water is not a concern.

Register to Reply
Register to Reply 9 comments

"Almost" Good Answers: