Capacitor Banks

07/04/2008 9:16 AM

Hye all,

Need your help to clarify my problem on the capacitor bank. currently in my substation we have 2 caps but was segregated by bus tie. unfortunately we are having transformer problem thus required to closed the bus tie and depend on one transformer only. during the energization of the capacitor banks, it breaker wont close because the interlock from the bus tie. the interlock just like allow only one caps bank to be energize. my question is, is there any problem if the caps bank energize more than needed. for your info my cap banks are in auto mode and for 6.6kV switchgear. Please advsie.

__________________
-tom-
Register to Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.
Guru
New Zealand - Member - Interested in everything- see my Profile please APIX Pilot Plant Design Project - Member - Member Engineering Fields - Electrical Engineering - Member Engineering Fields - Power Engineering - Member Engineering Fields - Civil Engineering - Member Hobbies - Musician - Autoharp and Harmonica Hobbies - Hunting - Member Hobbies - Fishing - Member

Join Date: Nov 2007
Location: Christchurch, (The Garden City), South Island, New Zealand
Posts: 4395
Good Answers: 230
#1

Re: Capacitor Banks

07/05/2008 2:44 AM

Hello TomHaRa

The interlock circuitry is there for safety reasons.

It may be possible to bypass the interlock arrangement, but without knowing the present system equipment, complete with protection relays and how they are interconnected, it is best to leave it well alone.

The reasons for not interfering are:

  1. Damage to equipment
  2. damage to persons,
  3. Possible invalidation of any Insurance Policy, if something went wrong.

Best to get the transformer problem sorted out, and get the plant back to normal, as soon as possible.

Kind Regards....

__________________
"The number of inventions increases faster than the need for them at the time" - SparkY
Register to Reply
Member

Join Date: Jul 2008
Location: Malaysia
Posts: 7
#2
In reply to #1

Re: Capacitor Banks

07/05/2008 8:37 AM

Thanks Sparkstation,

unfortunately we need to run the cap bank since the transformer problem takes time to be sorted out. currently we are in progress in startup our plant and a few HV motor are in place. now the PF is 0.74 lagging and what is the causes if we over energize the cap bank. is it the "lagging" term means that the kVar is in +ve magnitude while "leading" the kVar will be in -ve magnitude. Please correct me if i'm wrong. thus if possible, need your help to guide me to the relevent site for my reading.

Really appreciate for your responds.

__________________
-tom-
Register to Reply
Guru
Canada - Member - Specialized in power electronics

Join Date: Feb 2008
Location: Montreal, Canada.
Posts: 1372
Good Answers: 80
#3

Re: Capacitor Banks

07/06/2008 11:16 AM

If you get a PF of 0.74 with one bank, you should not go leading with two banks on line. In general, it is not good to be leading but it is usually safe up to 0.98.

The main problem you might have if the banks are nearby each others is large current transients when switching. This is because the bank that is already on line will feed the one being switched on. Since capacitors have a very high current sourcing (and absorbing) capacity. The cable impedance will limit the peak current. The peak current is greatly minimized if the banks are equipped with de-tuning reactors.

Before trying it, I would talk to the bank manufacturer and figure out why they had this interlock. The interlock need might still be valid and should not be bypassed. It is better to be safe than sorry.

__________________
Experienced is earned, common sense is taught, both are rare essentials of life.