07/08/2008 9:37 PM

Gentlemen/women......I need to protect a 1.5 hp horizontal centrifugal pump used for pumping water with elevation increase of approx 400 ft. Supply has about 40 psi but is sometimes interrupted causing dry pump burnout. Have pressure switch on output but water head generates pressure. What is best meithod/device for run dry protection....any help appreciated.

Register to Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.
Power-User

Join Date: Aug 2007
Location: Bhopal India
Posts: 234
Good Answers: 5
#1

Re: pump protection

07/08/2008 11:33 PM

A combination of pressure switch and flow switch in the suction line.

It is bit more complicated, but you can use CT based relays which sense the drop in current and trip the motor.

Cheers.

__________________
He must be very ignorant as he answers all the questions he is asked. Voltaire
Register to Reply
Guru
New Zealand - Member - Interested in everything- see my Profile please APIX Pilot Plant Design Project - Member - Member Engineering Fields - Electrical Engineering - Member Engineering Fields - Power Engineering - Member Engineering Fields - Civil Engineering - Member Hobbies - Musician - Autoharp and Harmonica Hobbies - Hunting - Member Hobbies - Fishing - Member

Join Date: Nov 2007
Location: Christchurch, (The Garden City), South Island, New Zealand
Posts: 4395
Good Answers: 230
#2

Re: pump protection

07/08/2008 11:48 PM

Hello sparkyspark

Your 400 foot elevation increase is going to require approximately 185 lbs per square inch pressure just to get the flow to the outlet at the top.

Remember to add the pressure required at the outlet, plus the loss in the suction pipe to the pump from your water supply, plus the loss in the outlet pipe from the pump, plus the pump loss.

With a 1.5HP pump, there is not going to be a big quantity of water actually moved, as most of the motor effort will be absorbed by the various losses.

For this type of installation, once pump size/motor size/pipe size has been determined, it is sometimes better to add to chaterpilar's system with an electrode sensor in the supply pipe, just before the pump.

No water = motor shutdown, and alarm sent, if required.

If you are supplying a header tank at the top of the outlet pipe, the simplest auto control is a ball float valve, which shuts the pump off with the increase in pressure as sensed at the pump outlet.

When the tank level falls, the ball float drops, valve opens, pressure switch at pump outlet senses pressure drop, and switches the pump motor on.

Trust that assists you.

Kind Regards....

__________________
"The number of inventions increases faster than the need for them at the time" - SparkY
Register to Reply
Guru
United Kingdom - Member - Indeterminate Engineering Fields - Control Engineering - New Member

Join Date: Jan 2007
Location: In the bothy, 7 chains down the line from Dodman's Lane level crossing, in the nation formerly known as Great Britain. Kettle's on.
Posts: 32175
Good Answers: 839
#3

Re: pump protection

07/09/2008 3:07 AM

There are devices that measure the phase angle between the voltage and the current of a motor. If these go out-of-phase by more than a pre-set amount, a changeover contact operates. The contact can be used to interrupt the starter circuit, and trip the motor out. One of these has been used quite satisfactorily to indicate a switch-off point for a pump in an industrial water treatment plant. It's a neat solution where nothing can be installed in the process line.

Another way is to put a pressure switch on the pump inlet line. If the pressure falls below, say, 20psi (user adjustable) then the switch could be used to switch off the pump.

__________________
"Did you get my e-mail?" - "The biggest problem in communication is the illusion that it has taken place" - George Bernard Shaw, 1856
Register to Reply
Participant

Join Date: Jul 2008
Posts: 2
#4

Re: pump protection

07/10/2008 2:54 AM

this pump has been operating using the breaker as a switch with a high pressure limit in line. I suppose a flow switch with a delay might be the answer. Isn't it possible or likely that a low pressure switch would cause bounce/nuisance stops once a starter is installed? Trying to find a conventional proven solution instead of reinventing the wheel.

Register to Reply
Power-User

Join Date: Dec 2005
Location: Willenhall, UK
Posts: 159
#5

Re: pump protection

07/10/2008 5:01 AM

I normally fit a pressure switch on the supply side or a dp switch across the pump for this application

__________________
A day without a smile is a day lost
Register to Reply
Anonymous Poster
#6

Re: pump protection

07/10/2008 5:58 AM

Hi There,

There are pump control units you can buy which automatically shut the pump down when the unit senses cavitation or interruption of the water supply, there is not much use in fitting a pressure switch on the intake or supply side of the system because it is under suction. I bought a unit in Australia for $95.00 AUD & it will automatically turn the pump on & off as a tap or hose is turned on & shut down if there is no water supply to the intake side of the pump.

Have look at www.cheapapumps.com.au

Register to Reply
Anonymous Poster
#7

Re: pump protection

07/10/2008 7:01 AM

I am presently using the Pumptech plus pump motor protector by Franklin Electric. Works great! http://www.wwpp.us/pumptec/pumptec-plus.shtml?gclid=CMSK_IiVtZQCFRghnAodcgS6Ug

Register to Reply
Associate

Join Date: Jan 2007
Location: Raleigh, N.C.
Posts: 49
Good Answers: 1
#8

Re: pump protection

07/10/2008 8:54 AM

A company called Load Controls Inc has several inexpensive devices, which I've used in various applications. These are easily integrated into your pumps control circuit.

www.loadcontrols.com

__________________
"You can fool some of the people all of the time and you can even fool all the people some of the time, but you can never fool all the people all of the time." Abe Lincoln
Register to Reply
Register to Reply 8 comments