Anonymous Poster

Caculation for Breaker Capacity Selection for Transformer Incoming and Outgoing

07/16/2008 2:38 AM

I would like to know how to calculate and select Breakers Capacity/rating for the PowerTransformer in coming and Out going.

Transformer details HV 66 KV;LV 11 KV;HV 43.7 Amps,LV262.5 Amps;Impedence 7.17%,Frequency 50Hz.

Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.
Guru

Join Date: Jun 2007
Location: chennai,India
Posts: 592
Good Answers: 19
#1

Re: Caculation for Breaker Capacity Selection for Transformer Incoming and Outgoing

07/16/2008 9:19 AM

What is the fault level?

What is the rating of the transformer?

Already full load current of transformer on primary side and secondary side is available you may have to select the switch gear which can arry the required current and with stand the fault level.Other considerations like temperature,outdoor/indoor ,Vaccuam/SF6 also to be taken into .

__________________
Ramesh,Freelance Electrical/automation Consultant
Reply
Anonymous Poster
#4
In reply to #1

Re: Caculation for Breaker Capacity Selection for Transformer Incoming and Outgoing

07/02/2010 3:49 AM

Calculation for Breaker capacity selection

Reply
Anonymous Poster
#2

Re: Caculation for Breaker Capacity Selection for Transformer Incoming and Outgoing

07/20/2008 3:57 PM

main points to be known for choosing breaker for incoming and outgoing of transformer are Breaker making and breaking capacity level. for making capacity u all ready given current values usesame only and for breaking capacity find fault current

fault level=1.1*V(line voltage)/(1.7*Z)

where z=impedence of transformer

breaking capacity of transformer should be greater than fault level

Reply
Associate

Join Date: Jul 2008
Posts: 37
#3

Re: Caculation for Breaker Capacity Selection for Transformer Incoming and Outgoing

07/20/2008 11:30 PM

hi

for that it is very important to have knowledge of rating of transformer and fault level at various point in the system, nomally highest fault level at the terminal of transformer is calculted by Fault MVA = Rating of trans./ % impedance

and from that fault current too,

for 66 kv system you could have SF6 breaker outdoor and for 11 kv, vaccum breaker indoor.

whereas all other parameters of the breakere of 66 and 11 kv are standardised by companies,

regards

divyesh patel

Reply