Anonymous Poster

acand dc ampere rating in the contact

07/30/2008 3:43 AM

contactor's contact current rating for ac current and dc current is same or defferent

Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.

Good Answers:

These comments received enough positive votes to make them "good answers".

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
2
Guru
United Kingdom - Member - Indeterminate Engineering Fields - Control Engineering - New Member

Join Date: Jan 2007
Location: In the bothy, 7 chains down the line from Dodman's Lane level crossing, in the nation formerly known as Great Britain. Kettle's on.
Posts: 32175
Good Answers: 839
#1

Re: acand dc ampere rating in the contact

07/30/2008 5:51 AM

Different.

__________________
"Did you get my e-mail?" - "The biggest problem in communication is the illusion that it has taken place" - George Bernard Shaw, 1856
Reply Good Answer (Score 2)
3
Guru
Canada - Member - If there is a way to screw someting up, there is someone to do so! Safety - Hazmat - New Member

Join Date: Mar 2007
Location: Iqaluit, NU. Canada
Posts: 1854
Good Answers: 140
#2

Re: acand dc ampere rating in the contact

07/30/2008 7:51 AM

Different...

A contactor rated for both AC and DC will have a DC rating lower then its AC rating.

The reason for this is the current that must be interrupted with a DC source is always at the maximum level, as defined by I=E/R, because the voltage level from the DC source is constant. This is contrary to the current level that must be interrupted with an AC source because of its changing voltage.

__________________
Joe Contractor to Electrical Inspector, "What do you mean you are going to make me follow the code?".
Reply Good Answer (Score 3)
Guru
Technical Fields - Architecture - New Member Popular Science - Weaponology - New Member Engineering Fields - Control Engineering - New Member Engineering Fields - Electrical Engineering - New Member Engineering Fields - Electromechanical Engineering - New Member Hobbies - Fishing - New Member Hobbies - Target Shooting - New Member Hobbies - Hunting - New Member

Join Date: Dec 2005
Location: Clemson, South Carolina
Posts: 1722
Good Answers: 18
#3

Re: acand dc ampere rating in the contact

07/30/2008 8:43 AM

I concur with PWSlack and North of 60.

__________________
We have met the enemy and he is us . . . Walt Kelly
Reply
Commentator

Join Date: Jun 2008
Posts: 80
Good Answers: 5
#4

Re: acand dc ampere rating in the contact

08/01/2008 1:44 PM

I agree with PW Slack and North of 60. I looked at the Eaton site real fast and I did not see any dual rated contactors, this does not mean they do not exist by any means. Eaton makes each type and placed side-by-side it would be easy to show the differences. The DC is much more heavy duty. I would probably not recommend a field type derating of an AC contactor for DC use, unless it was an emergency and the correct part was on its way. Even then you should proceed very carefully. This is where people who do not know and understand electrical engineering make recommendations and these same people are usually not there if there are negative consequences. If you are an engineer make sure your manager understands that use of components out of there normal application is not recommended. If you think of the contactor like you would a breaker it becomes easier. A circuit breaker will wait for the natural zero in AC current until it opens. Our graduate instructor showed us stroboscopic images and the poles open individually in positive sequence rotational order. This is why it so hard to interrupt a DC fault. If you look at a dual rated Circuit Breaker it will be something like 100A AC and 30 or 40 A DC. I did not look to verify those numbers but the DC is always significantly less. The chances are the contactor will wear out faster too. For large AC power breakers ABB now has a program that will close the breaker at the natural zero to help with contact wear.

I hope this helps

Bill

Reply Score 1 for Good Answer
Guru
United States - Member - New Member Engineering Fields - Power Engineering - New Member

Join Date: Sep 2006
Location: California, USA, where the Godless live next door to God.
Posts: 4665
Good Answers: 804
#5
In reply to #4

Re: acand dc ampere rating in the contact

08/01/2008 2:38 PM

"A circuit breaker will wait for the natural zero in AC current until it opens."

No, not really true. Circuit breakers do not have any such intelligence and even if you could come up with a way, the reaction time of any electro-mechanical device is so incredibly slow by comparison that this is virtually impossible. The breaker doesn't wait, it just tries to open when t is tripped.

I think maybe you are confusing this with the fact that in AC, as you start to open a set of contacts, the current flowing through them is by nature crossing zero 120 times per second. This aids in extinguishing the arc created as the current tries to continue to flow across the air gap until the dielectric strength of the air between the contacts reaches a sufficient level.

But with DC, that arc maintains itself for a lot longer because there is no zero-cross to help, so the contacts heat up exponentially higher and thus the contact material vaporizes at a much higher rate. To compensate, the DC contact material must have more surface area or mass to dissipate the heat than an AC contact for a given amp rating. Either that or, for a given contact size, the maximum DC current rating must be significantly lower.

There is also a very significant difference in the voltage rating of the contacts for the same reason. DC needs a much higher dielectric than AC to extinguish that arc, so the contacts themselves need to separate by a higher distance. That is the reason why most manufacturers will have different versions of their contactors for AC and DC.

__________________
** All I every really wanted to be, was... A LUMBERJACK!.**
Reply Score 1 for Good Answer
Commentator

Join Date: Jun 2008
Posts: 80
Good Answers: 5
#6
In reply to #4

Re: acand dc ampere rating in the contact

08/11/2008 2:04 PM

I am sorry if I implied that circuit breakers have a thought process. The actual opening , when given an open demand, will occur at the natural zero of the current. Springs will give it their best try but they are not enough to open the contacts. This is not an opinion this is a fact. Yes there will be an arc because the opening does not happen instantaneously. I would suggest to my friend that he view some high speed photography of three phase AC power circuit breakers opening if he does not believe me.

Reply Off Topic (Score 5)
Reply to Forum Thread 6 comments

Good Answers:

These comments received enough positive votes to make them "good answers".

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Copy to Clipboard

Users who posted comments:

Bill (1); Goodho (2); JRaef (1); North of 60 (1); PWSlack (1)