Synchronizing

07/31/2008 5:18 AM

What does it mean to synchronize two alternators in a simplest form.

Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Guru
United Kingdom - Member - Indeterminate Engineering Fields - Control Engineering - New Member

Join Date: Jan 2007
Location: In the bothy, 7 chains down the line from Dodman's Lane level crossing, in the nation formerly known as Great Britain. Kettle's on.
Posts: 32175
Good Answers: 839
#1

Re: Synchronizing

07/31/2008 6:07 AM

It means that the phase angle between the output waveforms is zero degrees.

__________________
"Did you get my e-mail?" - "The biggest problem in communication is the illusion that it has taken place" - George Bernard Shaw, 1856
Reply
Guru
Technical Fields - Architecture - New Member Popular Science - Weaponology - New Member Engineering Fields - Control Engineering - New Member Engineering Fields - Electrical Engineering - New Member Engineering Fields - Electromechanical Engineering - New Member Hobbies - Fishing - New Member Hobbies - Target Shooting - New Member Hobbies - Hunting - New Member

Join Date: Dec 2005
Location: Clemson, South Carolina
Posts: 1722
Good Answers: 18
#2

Re: Synchronizing

07/31/2008 2:22 PM

PW's right about the phase angle, and the voltages must be the same also.

__________________
We have met the enemy and he is us . . . Walt Kelly
Reply
Power-User
Australia - Member - New Member Engineering Fields - Mechanical Engineering - New Member Engineering Fields - Marine Engineering - New Member

Join Date: Sep 2006
Posts: 451
Good Answers: 16
#3
In reply to #2

Re: Synchronizing

08/01/2008 12:06 AM

It means lots of excitement and expense if you get it wrong.

Generators and their drives can be ripped from their beds and with them the engineers that were also in their beds.

Getting synchronisation right is very important for ones personal comfort.

BAB.

__________________
Make it so.
Reply
Power-User

Join Date: Dec 2005
Location: Willenhall, UK
Posts: 159
#4

Re: Synchronizing

08/01/2008 3:58 AM

To synchronise you must match voltage, frequency and phase angle at the same time. You normally have the machine that is coming on to the bus speeding up towards the correct phase angle so it will accept the load as breaker closes.

__________________
A day without a smile is a day lost
Reply
Member

Join Date: Jul 2008
Posts: 7
#5
In reply to #4

Re: Synchronizing

08/02/2008 3:59 AM

Peterd,

You are right! You need a master control with synchroscope, phase monitor etc.. This is usually used for paralleling two generators.

Reply
Associate

Join Date: Jun 2008
Posts: 25
#6

Re: Synchronizing

08/02/2008 7:15 AM

For synchronizing, phease sequence ,frequency and voltage of both the alternator should be same. Once the parameters matches ,then you can go for synchronising. There are different methods like all dark and all faint lamps etc.

Reply
Participant

Join Date: Aug 2008
Posts: 1
#7

Re: Synchronizing

08/03/2008 12:56 AM

I agreed your point i.e voltage, frequency and phase angles should match. if different capacities and aging ( one machine is 10 years old and one machine is new ) - what is the solution for syschronizing ?

Regds

A.Ravindra Reddy

Reply
Power-User

Join Date: Dec 2005
Location: Willenhall, UK
Posts: 159
#8
In reply to #7

Re: Synchronizing

08/04/2008 3:47 AM

Age of machine has nothing to do with it. Preferably the prime mover and/or the generator voltage regulator should have drooping characteristic for sysnchronising but not necessarily - depends on several things

__________________
A day without a smile is a day lost
Reply
Participant

Join Date: Aug 2008
Location: Luanda, Angola
Posts: 3
#9

Re: Synchronizing

08/04/2008 11:29 PM

Synchronizing two or more generators is to bring them in parallel operation in order to feed a certain electrical load. To be possible to put ac generators in parallel (to make them work together) as a prerequisite a) tension output of generators must have the same frequency (speed control by fuel or water injection at the generator's driver) b) output tension must match (excitation control at the generators) c) when phase angles between the equivalent phases of different generators are null, generators can be put in parallel by closing generator breakers.

These are the prerequisites for an ideal synchronization. The real world is somewhat different:

1 - Synchronize two generators without load (when the electrical load that must be feed exceeds the output of only one generator, so generators must be synchronized prior to close the breaker to feed the load)

2- Synchronize one generator with other generators that are just feeding a network.

In case 1, synchronization is made as described with two minor differences:

a) closing breaker order is given before phase angles are matching in order to compensate the closing time of the breaker;

b) output tension of both generators do not totally match, to be possible to have same reactive power maintaining generators electrically locked after synchronization.

In case 2 the new generator to be brought in parallel is synchronized

a) with a slightly higher frequency than the net (to take same load as soon as is breaker is closed;

b) with a tension slightly higher to feed same reactive power to the network

c) with a slight negative phase angle at the moment of breaker closing order.

These parameters (frequency, tension and phase angle) can be adjusted with an automatic synchronizing device and according with time response of the automatic speed/load control, the inertial momentum of the machine and time response of the automatic voltage regulator and breaker time to close. All these settings are more accurately established as the generators are more powerful and can impact all electrical system.

After synchronizing generators, how they will share the load that is another matter. Active and reactive power share can be manually controlled via fuel or water injection at the generator driver (diesel, gas or hydro turbine) and excitation at the generator excitation coils respectively, but usually all share activity, is automatically controlled by an automatic speed/load control device that controls the generator driver and the automatic voltage regulator device (excitation control) and their characteristic response curves. Settings of these devices must be more accurately established when generators with different prime movers like diesel and hydro with quite different time responses to changing load.

So type of prime mover, total rotating mass and age of prime mover related with time response to sudden variation of load can be important on choosing the right settings of automatic control devices in order to maintain generators synchronized but are of almost no importance to synchronize them.

__________________
"One does not, by knowing all the fundamental laws, obtain an understanding of anything much. Nature seems to be so designed that most important things in the real world appear to be kind of complicated accidental result of a lot of laws" R. Feynman
Reply Score 1 for Good Answer
Reply to Forum Thread 9 comments

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Copy to Clipboard

Users who posted comments:

acer (1); Bill (1); BlueAussieBoy (1); Japcs (1); peterd (2); PWSlack (1); raviavuthu (1); takle (1)

Previous in Forum: why need transformer   Next in Forum: cable selection

Advertisement