Steam turbine condenser vacuum problem

08/06/2008 9:47 AM

Hi, I'm new here. I'm working in one of the power plants in Malaysia and would like to get your comments & opinions regarding to vacuum rpoblem as stated above. For your information, our combined cycle plant is a combination of 13D ABB/Alstom open cycle gas turbine and MHI steam turbine. Maximum block gross output is approx. 250 MW where 90 MW of steam turbine is included. Condenser vacuum approx at -925 mbar. Condenser inlet temperature is 29-30 deg C but currently it observed about 31 deg C. Cooling medium is a sea water with 2 CW pumps in service. Problem is observed when condenser vacuum suddenly decreased to -896 mbar from -924 mbar at steady load. Normally, we will increase the motive steam pressure of air ejector to 16 mbar or sometimes to 20 mbar in order to ensure the condenser vacuum can be sustained at -924 mbar. After few hours the air ejector can be put on auto sequence with 14 mbar of motive steam pressure.

For your information, HP/LP bypass valves/ inlet and outlet motorised valves are fully closed. Cannot put in service due to the oil unit problem. It is long outstanding defect.Previously, two air ejectors were put in service in order to sustain the condenser vacuum. Currently, it also observed the sea water outfall temperature increase to 40 deg C. Based on DOE requirement, the outfall should not more than 40 deg C. I do not know either high outfall temperature is related to the condenser vacuum problem.

Thank you

Register to Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.
Guru
United Kingdom - Member - Indeterminate Engineering Fields - Control Engineering - New Member

Join Date: Jan 2007
Location: In the bothy, 7 chains down the line from Dodman's Lane level crossing, in the nation formerly known as Great Britain. Kettle's on.
Posts: 32175
Good Answers: 839
#1

Re: Steam turbine condenser vacuum problem

08/06/2008 10:28 AM

The boiling temperature and pressure of water are intimately linked.

It sounds as though some sort of inward leak is causing the loss of condenser vacuum, and the higher temperature is a symptom of the lower vacuum and indicating the leak.

__________________
"Did you get my e-mail?" - "The biggest problem in communication is the illusion that it has taken place" - George Bernard Shaw, 1856
Register to Reply
Anonymous Poster
#2

Re: Steam turbine condenser vacuum problem

08/07/2008 7:35 AM

Check your crossover valve used for back washing. It may be leaking by or have something stuck in it.

Register to Reply
Anonymous Poster
#3

Re: Steam turbine condenser vacuum problem

08/07/2008 8:56 AM

Check for condenser leaks which develop with increasing temperature.

What method are you using for oxygen control: hydrozine injection?

Register to Reply
Member

Join Date: Feb 2008
Posts: 8
#6
In reply to #3

Re: Steam turbine condenser vacuum problem

08/08/2008 12:24 PM

Basically the only way to remove dissolve oxygen is by using deaerator. According to EPRI guide for feedwater treatment, hydrozine disallowed in order to prevent FAC. We have on-line DO2 which located at condenser extraction pump outlet, deaerator inlet, deaerator outlet, HP BFP and LP BFP. Based on my observation the DO2 is normal.

Register to Reply
Power-User

Join Date: May 2007
Location: Los Angeles area, California, USA
Posts: 202
Good Answers: 9
#4

Re: Steam turbine condenser vacuum problem

08/07/2008 12:32 PM

I do not know either high outfall temperature is related to the condenser vacuum problem.

Global warming......cross over critical point.

Directly related.

MR. GUY

__________________
If you are looking for a positive answer..it's YUP......
Register to Reply
Guru
Popular Science - Evolution - New Member

Join Date: Jul 2006
Location: India-Chennai.
Posts: 722
Good Answers: 30
#5
In reply to #4

Re: Steam turbine condenser vacuum problem

08/07/2008 1:46 PM

I recall similar experience we faced on Sulzer turbine during mid nineties.

Fluctuating condenser pressure/vacuum.

Air was getting into through gland. Actual culprit was a simple 'steam trap' at glad steam circuit. The malfunction of this trap was allowing condensate intermittently into gland. This irregular supply of steam to gland led air on and often to turbine and intern to condenser.

__________________
A picture worth thousand words: needless to say if it is animated.
Register to Reply
Member

Join Date: Feb 2008
Posts: 8
#7
In reply to #5

Re: Steam turbine condenser vacuum problem

09/01/2008 1:58 AM

Dear Yesyen, it happened when load reduced to minimum i.e 70 MW of steam turbine gross output. Gland steam pressure approx. 0.22 bar. FYI, the gland steam pressure throttled manually by throttling the bypass manual isolating valve. CV unable to put in service.

Register to Reply
Anonymous Poster
#8

Re: Steam turbine condenser vacuum problem

09/23/2008 2:55 PM

Dear friend,

You are mentioning about the condeser problem. As per the information provided by you there is a rise in outlet temperaure for increase in inlet temperature.

Please check the following items.

1. Check the condeser cooling water flow.

2. Check your cooling water inlet take off point. Is it nearer to any industrial waste out let point.

3. Provide fin type arrangement with cooling fan provision at the condenser inlet pipe line to reduce inlet temperature such that you can limit your outlet temp as well you can increase the load.

4. Check vacuum tightness effectively.

5. Check your boiler feed water chemistry for effective evacuation of dissolved oxygen in feed water.

With regards,

SAM

Register to Reply
Member

Join Date: Feb 2008
Posts: 8
#9
In reply to #8

Re: Steam turbine condenser vacuum problem

01/11/2009 10:06 AM

Thank you Guest,

We have on-line DO2 reading and our chemist/ lab department also will do the grab sampling in order to get the DO2. The problem is the accuracy of reading itself. Sometimes reading recorded by grab sampling is more higher than the on-line reading. So, quite difficult for us to accept it due to one of the factor of air ingress is high DO2 reading. Limit is <10ppb.

Our combined cycle plant just coming back from major overhaul but the problem on condenser vacuum still persist. Currently, one steam air ejector in service but the motive steam pressure is 16.5 bar where slightly above the setting pressure, 14.0bar.

Before we managed to put one main ejector in service, both steam ejectors were in service on auto with motive steam pressure at 14.0 bar. Observed condenser outlet pressure improved to 1.2/0.9 bar (press gg is located before the outlet motorized valve). The TTD is 7.6 deg C for both condenser w/boxes. LP turbine exhaust temperature roughly at 43 deg C compared to 47 deg C before major overhaul.

Register to Reply
Member

Join Date: Feb 2008
Posts: 8
#10

Re: Steam turbine condenser vacuum problem

05/07/2009 1:47 AM

Our plant just installed with PI system. Based on the trend, it showed the high outfall temperature and low condenser vacuum happened just before the sea water tide level increased to maximum. Then the outfall and condenser vacuum will be back to normal operating reading when the tide level at maximum.I do not know if the hot water from the outfall flowing back to the intake lagoon of cooling water pump which caused the condenser inlet temperature increased. As far I'm concerned, sea water extracting by cooling water pump into condenser quite deep in the water.

Register to Reply
Participant

Join Date: Jul 2011
Posts: 1
#13
In reply to #10

Re: Steam turbine condenser vacuum problem

07/09/2011 2:58 AM

boleh jadi bro ada back flow from outfall to CW intake if ur condenser inlet temp also high. Global warming pun ye juga tapi lu boleh check CW intake screen da penuh kupang kot. CW flow tak cantik pun boleh kacau vacuum during tide changing. SJAE steam supply lu x payah increase press kalau nozzle n defuser masih baik, too high press boleh senak lu punya SJAE.. performance drop bro. Air ingress lu boleh tau dgn result DO2. Paling mudah nk buat leak check pakai freon gas, pasang detector kat SJAE exhaust pastu lu sembur la gas tu kat yg mncurigakan. Condenser cleanliness factor kn jaga bro, ball cleaning system kena jalan bro.

Register to Reply
Anonymous Poster
#11

Re: Steam turbine condenser vacuum problem

04/22/2010 8:42 PM

You can check the following items for your problem

1.Check your sea water intake temperature

2.check your sea water supply line to your ST whether it is provided with filteration equipment.This may be choked.

3.Any air ingression through any valves which connected in the vaccumm system.Check your sealing water pressure.

4.If you suspect any leak from the steam side then your condensate temp will raise.

5.check the primming of your sea water line.Some air lock also will reduce the cooling and it will detoriate the vaccumm.

Register to Reply
Anonymous Poster
#12

Re: Steam turbine condenser vacuum problem

06/03/2010 2:47 AM

your vacuum readings should be in bar(g) or Bar(a)?

Register to Reply
Associate

Join Date: Oct 2013
Posts: 29
#14

Re: Steam turbine condenser vacuum problem

11/24/2013 3:58 AM

There might be a leakage on your bypass on your HP/LP valve.