320v leg on 480v 3ph.

08/13/2008 10:58 AM

Whilst troubleshooting a 3ph. 10hp motor I discovered one 320vac (measured to ground) leg on a 3ph. 480vac circuit. Does anyone know the reason for this ? All the 480v systems I've dealt with in the past were 240v per leg to ground 480v between phases . Thanks .

Register to Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Guru
United Kingdom - Member - Indeterminate Engineering Fields - Control Engineering - New Member

Join Date: Jan 2007
Location: In the bothy, 7 chains down the line from Dodman's Lane level crossing, in the nation formerly known as Great Britain. Kettle's on.
Posts: 32175
Good Answers: 839
#1

Re: 320v leg on 480v 3ph.

08/13/2008 11:58 AM

What is the voltage of the other two phases?

If one of the other two phases were much lower, it would indicate a heavy neutral current from a single phase load on that phase.

__________________
"Did you get my e-mail?" - "The biggest problem in communication is the illusion that it has taken place" - George Bernard Shaw, 1856
Register to Reply
Associate

Join Date: Aug 2008
Location: Rochester , NY
Posts: 35
#2
In reply to #1

Re: 320v leg on 480v 3ph.

08/13/2008 12:58 PM

PW , thanks for the response . The other 2 legs have 240vac to ground on them

Register to Reply
Power-User

Join Date: Jun 2008
Location: Olive Branch, Ms. USA
Posts: 124
#3

Re: 320v leg on 480v 3ph.

08/13/2008 1:17 PM

Your using a delta high- leg system. This is usually the "B" phase or T-2

__________________
Tell 'em what they need to hear; not what they want to hear!
Register to Reply
Power-User

Join Date: Jun 2007
Posts: 141
Good Answers: 2
#4

Re: 320v leg on 480v 3ph.

08/13/2008 4:05 PM

I got a couple of guesses. First, it does not sound like a 3 phase 4wire wye, otherwise you would be measuring somewhere around 277V from phase to ground. It sounds like a center tapped delta, but on a 480V system the high leg would read around 416V. It may be that the phase you were measuring was the residual voltage from an open leg being back fed by the motor.

Register to Reply Score 1 for Good Answer
Guru
Canada - Member - If there is a way to screw someting up, there is someone to do so! Safety - Hazmat - New Member

Join Date: Mar 2007
Location: Iqaluit, NU. Canada
Posts: 1854
Good Answers: 140
#5
In reply to #4

Re: 320v leg on 480v 3ph.

08/13/2008 9:28 PM

Ya I agree... you get a point.

__________________
Joe Contractor to Electrical Inspector, "What do you mean you are going to make me follow the code?".
Register to Reply
Anonymous Poster
#6

Re: 320v leg on 480v 3ph.

08/13/2008 11:04 PM

Was the motor single phasing, A+B or A+C or B+C?

Register to Reply
Power-User

Join Date: Dec 2007
Location: Chicago, IL, USSA
Posts: 141
Good Answers: 3
#7

Re: 320v leg on 480v 3ph.

08/14/2008 11:36 AM

You should measure the voltage between all 3 phases A-B; B-C; C-A if you read 480v between all phases then it is because of where the transformer secondary upstream is grounded (or possibly floating). If you do not read 480v between all phases then it could indicate an overloaded phase with too much current flowing thru it to the Neutral or another phase.

Register to Reply
Associate

Join Date: Aug 2008
Location: Rochester , NY
Posts: 35
#8

Re: 320v leg on 480v 3ph.

08/16/2008 11:54 PM

Thanks everyone for the replies ! I did a little more research on this and this is what I found . Between any 2 phases I read 472 vac . Phase A to ground = 250vac , phase B to ground = 257 vac and phase C to ground 316 vac . The current is the same on all three phases , around 7-1/2 amps. I hope this will shed some light for some of you more experienced pros out there because this is making no sense to me . Going camping tomorrow so I'll check back next week sometime . Thanks again for all the help !

Register to Reply
Guru
Canada - Member - If there is a way to screw someting up, there is someone to do so! Safety - Hazmat - New Member

Join Date: Mar 2007
Location: Iqaluit, NU. Canada
Posts: 1854
Good Answers: 140
#9
In reply to #8

Re: 320v leg on 480v 3ph.

08/17/2008 3:28 PM

As of yet, you have not mentioned a neutral. If you have a neutral, what are the line to neutral voltage readings?

You need to understand what type of winding, either delta or wye, it is that is supplying the 480 volt system and where that system is grounded.

If you do not see a neutral and if you do not have any line to neutral loads, which gives you 277v which is normally used for lighting loads, your neutral may just have been left at the transformer and not brought any farther.

There has to be a neutral at the transformer, other wise it would be a corner grounded system or not grounded at all. If it was not grounded, the line to ground voltage should be zero and if it was corner grounded, 1 of the phases should show zero volts to ground.

__________________
Joe Contractor to Electrical Inspector, "What do you mean you are going to make me follow the code?".
Register to Reply
Power-User

Join Date: Jun 2007
Posts: 141
Good Answers: 2
#10
In reply to #8

Re: 320v leg on 480v 3ph.

08/18/2008 10:32 AM

As North of 60 pointed out, more info is needed on your distribution system. From what you stated here, is sounds like a 3 phase 3 wire system that is not grounded or improperly grounded. The readings look like something you would see from a floating ground with the exception that they seem to remain constant.

Register to Reply
Register to Reply 10 comments

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Copy to Clipboard

Users who posted comments:

5BANJO5 (2); Anonymous Poster (1); Apps Man (1); Lendog (2); North of 60 (2); noshorts (1); PWSlack (1)