110 Outlet with Green Circle & Red Triangle on The Bottom

08/14/2008 7:48 PM

I only do low voltage in Florida. Well I unpluged a device from this recpitical then tryed to remember which outlet to plug it back into. Some know it all said that the bottom outlet with the red triangle on the left side, and the green circle on the right side is 220. The top outlet was regular 110. Tell the girl anything ? I think he's full of bologna.

Is he right?

__________________
New sport. Horse butt diving. My getaway from wire city.
Register to Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.
Guru
New Zealand - Member - Interested in everything- see my Profile please APIX Pilot Plant Design Project - Member - Member Engineering Fields - Electrical Engineering - Member Engineering Fields - Power Engineering - Member Engineering Fields - Civil Engineering - Member Hobbies - Musician - Autoharp and Harmonica Hobbies - Hunting - Member Hobbies - Fishing - Member

Join Date: Nov 2007
Location: Christchurch, (The Garden City), South Island, New Zealand
Posts: 4395
Good Answers: 230
#1

Re: 110 outlet with Green circle & red triangle on the bottom

08/14/2008 7:51 PM

Hello lockitup

You forgot to place a picture of the receptacle.

Reply here, with the picture, and

Kind Regards....

__________________
"The number of inventions increases faster than the need for them at the time" - SparkY
Register to Reply
Guru
United States - Member - Charter Member Engineering Fields - Instrumentation Engineering - Charter Member

Join Date: Mar 2008
Location: The People's Republic of Massachusetts
Posts: 1946
Good Answers: 73
#2

Re: 110 outlet with Green circle & red triangle on the bottom

08/14/2008 8:40 PM

Well, um, err, this is perhaps the strangest post I ever saw. The girl is a he, with colored circles and triangles, and luncheon meat thrown in to boot.

A picture would really clear things up. So would a volt meter.

__________________
I go into every human encounter expecting to be framed for a crime I didn't commit. Dilbert, 2013
Register to Reply
Power-User
Hobbies - HAM Radio - New Member United States - Member - New Member Hobbies - Hunting - New Member

Join Date: Jun 2008
Posts: 440
Good Answers: 7
#3
In reply to #2

Re: 110 outlet with Green circle & red triangle on the bottom

08/14/2008 9:23 PM

It is a hospital grade and filtered outlet--We sometimes use them on "clean power" for automation and the color discourages angle grinders from being plugged into them. I think audiophiles use them for stereo equipment, but the voltage shouldn't be out of the ordinary.

__________________
Those who believe in telekinetics, raise my hand --Kurt Vonnegut Jr.
Register to Reply
Guru
United States - Member - Charter Member Engineering Fields - Instrumentation Engineering - Charter Member

Join Date: Mar 2008
Location: The People's Republic of Massachusetts
Posts: 1946
Good Answers: 73
#4
In reply to #3

Re: 110 outlet with Green circle & red triangle on the bottom

08/14/2008 9:38 PM

Perhaps you could educate me here. Are not 110 volt and 220 volt plug configurations different?

__________________
I go into every human encounter expecting to be framed for a crime I didn't commit. Dilbert, 2013
Register to Reply
Power-User
Hobbies - HAM Radio - New Member United States - Member - New Member Hobbies - Hunting - New Member

Join Date: Jun 2008
Posts: 440
Good Answers: 7
#5
In reply to #4

Re: 110 outlet with Green circle & red triangle on the bottom

08/14/2008 9:59 PM

If wired right, absolutely. You should never have to make that decision. Markings or color on them may suggest usage, but the voltage shouldn't be in question. Different voltage and amperage rating usually won't interchange. This can be referenced at a suppliers site--try Leviton or Tripp lite and it will show a variety or plug bodies and cord caps and outlets and ratings for phase, voltage and amperage.

Here's one:

http://www.leviton.com/OA_HTML/xxlcfbuibeCSrdSrchResults.jsp?cg=&kw=cord+cap+ratings&bo=and&nkw=&st=kw&dr=20&cpg=0&upc=&ccnum=&allats=&oneats=&exphr=&isAdvSrch=false&tbon=T

__________________
Those who believe in telekinetics, raise my hand --Kurt Vonnegut Jr.
Register to Reply
Guru
Hobbies - RC Aircraft - New Member Hobbies - Automotive Performance - New Member Hobbies - DIY Welding - New Member

Join Date: Jul 2007
Location: Fort Lauderdale Florida
Posts: 5708
Good Answers: 123
#6
In reply to #4

Re: 110 outlet with Green circle & red triangle on the bottom

08/14/2008 10:09 PM

did you forget this one?

What would happen if I connected my 110v dishwasher to 220v by accident?

From what I have seen in the last 30 years, NEMA has designed plugs and receptacles so that if it fits, it is correct. I have 120 volt items in 15 amp and 20 amp. You can plug the 15 into the 20 receptacle, but not the 20 into the 15.

Someone on this site sent me a list of outlet configurations around the world. Perhaps they would post it again.

I have seen and used the green dot hospital grade. They are overpriced. The same quality can be had in an industrial grade. Does anyone know what the difference between hospital grade and industrial grade?

I have also seen orange isolated ground receptacles listed, but never used.

__________________
Bob
Register to Reply
Guru
United Kingdom - Member - Indeterminate Engineering Fields - Control Engineering - New Member

Join Date: Jan 2007
Location: In the bothy, 7 chains down the line from Dodman's Lane level crossing, in the nation formerly known as Great Britain. Kettle's on.
Posts: 32175
Good Answers: 839
#11
In reply to #6

Re: 110 outlet with Green circle & red triangle on the bottom

08/15/2008 8:23 AM

<...Someone on this site sent me a list of outlet configurations around the world....>

There is also an illustrated article on this subject in Wikipedia.

__________________
"Did you get my e-mail?" - "The biggest problem in communication is the illusion that it has taken place" - George Bernard Shaw, 1856
Register to Reply
Commentator

Join Date: Jun 2008
Location: Brick, NJ
Posts: 71
Good Answers: 8
#12
In reply to #6

Re: 110 outlet with Green circle & red triangle on the bottom

08/15/2008 11:22 PM

I'm not sure what the difference between hospital grade and industrial grade are but when I was an electrician in the Navy in the early 80's hospital grade was used exclusively. I have used the orange isolated ground outlets but not since 1987 in the very early PC days.

As far as the plug and receptical configurations being correct if they fit, never assume that. You are counting on the person that wired the receptical to have used the right part. If in doubt, measure the voltage first. Plugging a 220 V device into 110 V probably won't damage the device immediately, but the reverse is rarely true.

__________________
Do this. Don't do that. Can't you redesign?
Register to Reply
Guru
United States - US - Statue of Liberty - New Member Hobbies - Fishing - New Member

Join Date: Nov 2007
Location: Gone to Alabama with my banjo on my knee...
Posts: 5595
Good Answers: 20
#16
In reply to #6

Re: 110 outlet with Green circle & red triangle on the bottom

08/16/2008 9:29 AM

"...the difference between hospital grade and industrial grade..."

I think the other respondents have answered most everything else, including the fact that whoever wired in the pictured circuit learned electricity from the Rube Goldberg school (although in the lower left corner of the upper pic you'll see a pretty substantial ground connection - presuming it actually goes to Earth somewhere...).

Therefore, I will wax erudite on the quoted phrase (above) only - "hospital grade" electrical (switches as well as) outlets have gold-plated contacts to avoid a spark across the gap when contact is made/interrupted due to the usually oxygen-rich atmosphere. Also occasionally flammable vapors...

__________________
Veni, vidi, video - I came, I saw, I got it on film.
Register to Reply
Active Contributor

Join Date: Mar 2008
Location: Orange, CA
Posts: 20
#31
In reply to #6

Re: 110 outlet with Green circle & red triangle on the bottom

08/18/2008 11:19 AM

Great link!!!

After checking it out I have a question?

Why are their holes on the flat blades of the US style plugs?

Thank You in advance...

__________________
George
Register to Reply Off Topic (Score 5)
Anonymous Poster
#32
In reply to #31

Re: 110 outlet with Green circle & red triangle on the bottom

08/18/2008 11:31 AM

I give up, Why?

Register to Reply Off Topic (Score 5)
Active Contributor

Join Date: Mar 2008
Location: Orange, CA
Posts: 20
#34
In reply to #32

Re: 110 outlet with Green circle & red triangle on the bottom

08/18/2008 11:43 AM

I do NOT know, that is why I'm asking!!!

__________________
George
Register to Reply Off Topic (Score 5)
Anonymous Poster
#38
In reply to #34

Re: 110 outlet with Green circle & red triangle on the bottom

08/18/2008 12:03 PM

Oh!

I always thought the hole is there to engage a spring configuration or similar protrusion in the blade receptable that is meant to bring the plug home, make a solid connection, and prevent the plug from pulling out unintended. (I've sometimes asked myself why plug-grip by outlets is so reliable.)

Or make it easier to start the plug into the receptacle

Or both.

One day I'll smash a receptacle with hammer and learn the answer, or not, first hand.

Register to Reply Off Topic (Score 5)
Guru
Panama - Member - New Member Hobbies - CNC - New Member Engineering Fields - Marine Engineering - New Member Engineering Fields - Retired Engineers / Mentors - New Member

Join Date: Dec 2006
Location: Panama
Posts: 4273
Good Answers: 213
#39
In reply to #34

Re: 110 outlet with Green circle & red triangle on the bottom

08/18/2008 1:33 PM

There was a thread addressing this a few months back. As I remember rightly, NO ONE KNOWS, but everyone has an opinion...

Register to Reply Off Topic (Score 5)
Guru
United States - Member - Charter Member Engineering Fields - Instrumentation Engineering - Charter Member

Join Date: Mar 2008
Location: The People's Republic of Massachusetts
Posts: 1946
Good Answers: 73
#33
In reply to #31

Re: 110 outlet with Green circle & red triangle on the bottom

08/18/2008 11:39 AM

The blades inside the female receptacle are springy and have a dimple. This helps to hold the plug fast, requiring a small effort to unplug.

__________________
I go into every human encounter expecting to be framed for a crime I didn't commit. Dilbert, 2013
Register to Reply
Active Contributor

Join Date: Mar 2008
Location: Orange, CA
Posts: 20
#35
In reply to #33

Re: 110 outlet with Green circle & red triangle on the bottom

08/18/2008 11:44 AM

Thnak You

__________________
George
Register to Reply
Anonymous Poster
#41
In reply to #35

Re: 110 outlet with Green circle & red triangle on the bottom

08/18/2008 2:47 PM

Not so fast with the thanks there! How can a dimple hold a hole?

Register to Reply
Guru
United States - Member - Charter Member Engineering Fields - Instrumentation Engineering - Charter Member

Join Date: Mar 2008
Location: The People's Republic of Massachusetts
Posts: 1946
Good Answers: 73
#44
In reply to #41

Re: 110 outlet with Green circle & red triangle on the bottom

08/18/2008 3:27 PM

It would be the male side of a dimple, or, perhaps, better called a nipple.

__________________
I go into every human encounter expecting to be framed for a crime I didn't commit. Dilbert, 2013
Register to Reply
Guru
United States - US - Statue of Liberty - New Member Hobbies - Fishing - New Member

Join Date: Nov 2007
Location: Gone to Alabama with my banjo on my knee...
Posts: 5595
Good Answers: 20
#45
In reply to #44

Re: 110 outlet with Green circle & red triangle on the bottom

08/18/2008 3:42 PM

So...this is why...males have nipples? I've often wondered...

__________________
Veni, vidi, video - I came, I saw, I got it on film.
Register to Reply Off Topic (Score 5)
Guru
United States - Member - Charter Member Engineering Fields - Instrumentation Engineering - Charter Member

Join Date: Mar 2008
Location: The People's Republic of Massachusetts
Posts: 1946
Good Answers: 73
#48
In reply to #45

Re: 110 outlet with Green circle & red triangle on the bottom

08/18/2008 8:39 PM

No, no, no, in this case it's the female receptacle that has the nipples, (pregnant with the male dimples).

__________________
I go into every human encounter expecting to be framed for a crime I didn't commit. Dilbert, 2013
Register to Reply
Power-User
Hobbies - HAM Radio - New Member United States - Member - New Member Hobbies - Hunting - New Member

Join Date: Jun 2008
Posts: 440
Good Answers: 7
#49
In reply to #48

Re: 110 outlet with Green circle & red triangle on the bottom

08/18/2008 8:59 PM

HHHHHHAAAAAAAAAAAAAAAAAAHHHAAAAAAAAAAAAAAA!

I thought they(the holes) were solderies so that if the plug transformer in picture wouldn't fit into a 120V socket that was wired for polyphase 480V---just goop enough solder on them and size your wire to carry "DUH" load.

Nipples!

__________________
Those who believe in telekinetics, raise my hand --Kurt Vonnegut Jr.
Register to Reply
Guru
United States - US - Statue of Liberty - New Member Hobbies - Fishing - New Member

Join Date: Nov 2007
Location: Gone to Alabama with my banjo on my knee...
Posts: 5595
Good Answers: 20
#52
In reply to #48

Re: 110 outlet with Green circle & red triangle on the bottom

08/19/2008 6:15 AM

Spoken like a true dimpled Lothario!

__________________
Veni, vidi, video - I came, I saw, I got it on film.
Register to Reply Off Topic (Score 5)
Anonymous Poster
#63
In reply to #44

Re: 110 outlet with Green circle & red triangle on the bottom

08/21/2008 3:32 AM

Oh...like a baby in bottle... a Grabber Baby'n Bottle?

Register to Reply
Guru
New Zealand - Member - Interested in everything- see my Profile please APIX Pilot Plant Design Project - Member - Member Engineering Fields - Electrical Engineering - Member Engineering Fields - Power Engineering - Member Engineering Fields - Civil Engineering - Member Hobbies - Musician - Autoharp and Harmonica Hobbies - Hunting - Member Hobbies - Fishing - Member

Join Date: Nov 2007
Location: Christchurch, (The Garden City), South Island, New Zealand
Posts: 4395
Good Answers: 230
#64
In reply to #63

Re: 110 outlet with Green circle & red triangle on the bottom

08/21/2008 4:16 AM

Kind Regards....

__________________
"The number of inventions increases faster than the need for them at the time" - SparkY
Register to Reply
Anonymous Poster
#40
In reply to #33

Re: 110 outlet with Green circle & red triangle on the bottom

08/18/2008 2:42 PM

That's your opinion?

Register to Reply Off Topic (Score 5)
Anonymous Poster
#43
In reply to #31

Re: 110 outlet with Green circle & red triangle on the bottom

08/18/2008 2:56 PM

May be, for every few dozen blades with holes in them, enough metal is "saved" to make the few-dozen-and-first blade. Just one person's opinion, though.

Hmm! I wonder what the commodity value of all the blade holes in the US would turn out to be? Wikepedia?

Register to Reply Off Topic (Score 5)
Anonymous Poster
#26
In reply to #3

Re: 110 outlet with Green circle & red triangle on the bottom

08/17/2008 11:09 PM

So the patients with pacemakers can go with a song in their heart?

Register to Reply
Participant

Join Date: Aug 2008
Location: Ft.Lauderdale, Florida
Posts: 3
#7

Re: 110 outlet with Green circle & red triangle on the bottom

08/14/2008 10:39 PM

Oh wow. Thanks everybody. I do have a pic.When i pluged the cord

in, the whole side of the recipitical pushed in sideways, then no power. only then i tryed the volt meter. Maintance couldn"t find the breaker. Gee, and its not even Friday yet.

__________________
New sport. Horse butt diving. My getaway from wire city.
Register to Reply
Guru
New Zealand - Member - Interested in everything- see my Profile please APIX Pilot Plant Design Project - Member - Member Engineering Fields - Electrical Engineering - Member Engineering Fields - Power Engineering - Member Engineering Fields - Civil Engineering - Member Hobbies - Musician - Autoharp and Harmonica Hobbies - Hunting - Member Hobbies - Fishing - Member

Join Date: Nov 2007
Location: Christchurch, (The Garden City), South Island, New Zealand
Posts: 4395
Good Answers: 230
#8
In reply to #7

Re: 110 outlet with Green circle & red triangle on the bottom

08/14/2008 10:52 PM

Hello lockitup

That wiring looks as if it was done by Heath Robinson.

The screws on that front plate are very rusty, too.

Probably the box interior is damaged.

Kind Regards....

__________________
"The number of inventions increases faster than the need for them at the time" - SparkY
Register to Reply
Power-User
Hobbies - HAM Radio - New Member United States - Member - New Member Hobbies - Hunting - New Member

Join Date: Jun 2008
Posts: 440
Good Answers: 7
#9
In reply to #8

Re: 110 outlet with Green circle & red triangle on the bottom

08/14/2008 11:00 PM

I hate to agree with anyone, but this time, Spark I will with you--The plastic enclosure with the plastic screws and the splash guarded outlet cover may be suited for the location----But the wire nuts????? No way. What and where is this contraption and what is supposed to do?? Help can be found right here--These guys jump at the chance, just ask!!

__________________
Those who believe in telekinetics, raise my hand --Kurt Vonnegut Jr.
Register to Reply
Guru
Hobbies - RC Aircraft - New Member Hobbies - Automotive Performance - New Member Hobbies - DIY Welding - New Member

Join Date: Jul 2007
Location: Fort Lauderdale Florida
Posts: 5708
Good Answers: 123
#10
In reply to #9

Re: 110 outlet with Green circle & red triangle on the bottom

08/14/2008 11:33 PM

Thank you Sparky.

My guess is that this is a power supply for a remote radio site or radio repeater. I think the wires on the wall are antenna wires.

__________________
Bob
Register to Reply
Anonymous Poster
#13

Re: 110 Outlet with Green Circle & Red Triangle on The Bottom

08/16/2008 6:40 AM

The double duplex receptacle(s) are for powering the low voltage equipment in the enclosure. Low voltage installers are notorious for butcher work like this. The markings on the receptacles indicate that they are isolated ground, data-grade receptacles. However, used in this application, it looks like the installer just used these because they were just laying around and handy to be installed. As far as the equipment, the devices at top left are for analog video transmission and PTZ data transmission for a CCTV camera (75 ohm coax) over twisted pair cable (passive baluns). It looks like a small step down transformer for camera power in the lower right side of the picture using pigtail connections. This is the reason for the wire nuts.

I have installed low voltage for 20 years. Unfortunately this type of shotty work is the norm. Hope this helps.

Register to Reply
Anonymous Poster
#14

Re: 110 Outlet with Green Circle & Red Triangle on The Bottom

08/16/2008 8:15 AM

PLease educate yourself on electricity. You may not have to worry about plugging things back in based on your question. Electricity kills be it 24V or 120V. Be Careful you only have one life to live.

Register to Reply
Active Contributor
Popular Science - Weaponology - New Member

Join Date: Jan 2008
Location: Lakewood, CO.
Posts: 19
#15

Re: 110 Outlet with Green Circle & Red Triangle on The Bottom

08/16/2008 9:18 AM

It sounds to me like it is an isolated grounded outlet. I think that is a spec or code for hospital locations.

Indydog

Register to Reply
Power-User

Join Date: Mar 2006
Location: Valdosta, GA
Posts: 361
Good Answers: 8
#17

Re: 110 Outlet with Green Circle & Red Triangle on The Bottom

08/16/2008 5:28 PM

Usually the outlets in a double gang box are all wired the same. The duplex outlets are usually tied together top and bottom. That said, the outlets may be untied by breaking out the connecting piece, thus allowing each outlet to be wired seperately. The red triangle would suggest to me to be the "hot" side of the outlet while the green circle should be ground or neutral. There again, there are no guarantees. It does indeed look as though there is an isolated ground. I doubt very seriously that there is any 220 Volt power available here. However, as I have stated, there is no guarantee. The receptacles certainly are capable of accepting 220 volt plugs. Usually though, the neutral side of the receptacle is not tied to ground except in the distribution panel in normal house wiring which this obviously isn't and certainly wouldn't be tied to ground in the USA if it were 220 volt. The know it all may know something we don't. The only safe course of action is to get the power restored and check the voltage with a volt meter. Please, for safety sake, check and make sure your ground is actually grounded.

Regards,

Keywalker

__________________
Always use protection.
Register to Reply
Power-User
Hobbies - HAM Radio - New Member United States - Member - New Member Hobbies - Hunting - New Member

Join Date: Jun 2008
Posts: 440
Good Answers: 7
#18
In reply to #17

Re: 110 Outlet with Green Circle & Red Triangle on The Bottom

08/16/2008 6:07 PM

If wired properly, one should not be able to confuse voltage/amperage ratings when using plugs and receptacles. If you can, it must be very old or wired improperly.

www.systemconnection.com/downloads/PDFs/NEMAPlugReceptacleConfigurations.pdf

__________________
Those who believe in telekinetics, raise my hand --Kurt Vonnegut Jr.
Register to Reply
Guru

Join Date: Mar 2008
Location: Atlanta, Georgia
Posts: 749
Good Answers: 13
#19
In reply to #18

Re: 110 Outlet with Green Circle & Red Triangle on The Bottom

08/16/2008 10:25 PM

Hospital grade receptacles are red and because of cost are only used in rooms where oxygen or flammable gases may be in use as stated above.

Guest has correctly identified the other equipment around the receptacles. There could be as many as four separate 20 amp circuits at 120 volts A.C. in that box or four, because of the possible use of "T" polarized plugs, 240 volt circuits considering each half of those duplex receptacles can be separated and wired individually.

When I lived in England folks used to regularly go nuts because of the radically different load distinctions and plugs. Take a device from one place and try to plug it in somewhere else and it would not fit. Of course that is more necessary because starting at 220 volts you are potentially playing around with considerable more energy. Nonetheless, I and all my friends always thought it was a pain in the ass although I was even then many years ago a competent electrician who recognized why it was that way .

The use of those receptacles with the "T" polarization as one of two possibilities is just plain stupid because it introduces an unknown where there should not be one. The parallel Edison plug should always be an indicator of 120 volts.

When I mess around with that sort of stuff I find it easiest to carry in my pocket a test plug that indicates polarity and neutral or ground if not yet up to the new standards. They even make a plug that has a grounding button on it to check GFCI protected circuits.

j.

Register to Reply
Guru
Hobbies - RC Aircraft - New Member Hobbies - Automotive Performance - New Member Hobbies - DIY Welding - New Member

Join Date: Jul 2007
Location: Fort Lauderdale Florida
Posts: 5708
Good Answers: 123
#20
In reply to #19

Re: 110 Outlet with Green Circle & Red Triangle on The Bottom

08/16/2008 11:28 PM

I have been using HBL5266C from Hubbell. I get good usage out of them, but wanted to the to improve on them. I bought the same thing from Hubbell, but hospital grade, and they were $ 4.00 more. They got crushed just as bad as the 5266Cs did. Other than the green dots, I could see no difference between them. .

__________________
Bob
Register to Reply
Guru

Join Date: Mar 2008
Location: Atlanta, Georgia
Posts: 749
Good Answers: 13
#21
In reply to #20

Re: 110 Outlet with Green Circle & Red Triangle on The Bottom

08/16/2008 11:44 PM

Install anything but hospital grade in a hospital where specs and code indicate and see how fast the inspector will jump all over you.

The four dollars extra covers the gold plating which prevents arcing, hence prevents fires and explosions in potentially dangerous atmospheres.

j.

Register to Reply
Guru
Hobbies - RC Aircraft - New Member Hobbies - Automotive Performance - New Member Hobbies - DIY Welding - New Member

Join Date: Jul 2007
Location: Fort Lauderdale Florida
Posts: 5708
Good Answers: 123
#22
In reply to #21

Re: 110 Outlet with Green Circle & Red Triangle on The Bottom

08/17/2008 12:18 AM

I do face a bit of arking and erosion of the plugs because the loads on them are not turned off when plugging in or removing the plug. But I don't feel that I would be violating any code by going from non hospital to hospital grades as long as the wiring is up to codes. It does not compromise quality, only adds to it.

__________________
Bob
Register to Reply
Guru

Join Date: Mar 2008
Location: Atlanta, Georgia
Posts: 749
Good Answers: 13
#23
In reply to #22

Re: 110 Outlet with Green Circle & Red Triangle on The Bottom

08/17/2008 10:00 AM

You don't say just what you are working on but that aside if you install anything but hospital grade in a hospital environment where hospital grade is specified it would not be polite to tell you here what ought to be done to you.

j.

Register to Reply
Guru
Hobbies - RC Aircraft - New Member Hobbies - Automotive Performance - New Member Hobbies - DIY Welding - New Member

Join Date: Jul 2007
Location: Fort Lauderdale Florida
Posts: 5708
Good Answers: 123
#24
In reply to #23

Re: 110 Outlet with Green Circle & Red Triangle on The Bottom

08/17/2008 12:29 PM

I'll grant you no special privileges now. Wait in line like the rest of the people that hate me.

The trucks I deal with have

1) Onboard air compressors to maintain sufficient air pressure to allow the trucks to release the parking brake immediately.

2) Onboard battery chargers to assure the truck will start as quick as possible.

3) Onboard engine heaters to assure the trucks have full power right away, and will not damage heads from wide open throttle operation when cold.

The power consumption for these combined devices is very close to the 20 amp rating of the connection. The trucks have an automatic plug ejector that breaks the electrical connection before pushing the plug out. But I still get some arking marks on the flat pins of the plug after time.

I have gone to 12 gauge overhead reels combined with short 10 gauge jumper links in case the auto eject fails (again).

Check with my wife about scheduling a time for my --- kicking. She thinks there may be an opening in November due to a cancellation.

__________________
Bob
Register to Reply
Anonymous Poster
#28
In reply to #24

Re: 110 Outlet with Green Circle & Red Triangle on The Bottom

08/18/2008 12:53 AM

Well Bob it was very murky just what you were talking about.

Now you are talking about trucks, obviously with air brakes that set when air pressure gets low.

You are talking about electric start vehicles.

You seem to be talking about diesels.

You could be talking about ambulances but that business about overhead reels is murky. Are the trucks plugged up to an external A.C. supply to keep batteries under charge when the engines are off?

Do the automatic plug ejectors disconnect the truck when brakes come off ready to run. Do the jumper links pull the plug when the truck moves away if the automatic fails?

What is this about receptacles getting crushed?

Sorry to upset you. My intention was to warn anybody who might substitute for hospital grade in a hospital environment as to how serious such could be.

j.

Register to Reply
Guru
Hobbies - RC Aircraft - New Member Hobbies - Automotive Performance - New Member Hobbies - DIY Welding - New Member

Join Date: Jul 2007
Location: Fort Lauderdale Florida
Posts: 5708
Good Answers: 123
#58
In reply to #28

Re: 110 Outlet with Green Circle & Red Triangle on The Bottom

08/19/2008 9:08 PM

Sorry for the delayed response. I had a previously scheduled appointment to get my --- kicked.

The trucks are large airport fire trucks. We keep the on board battery charger, air compressor and engine heater connected when ever the trucks are parked in the station. There is an overhead reel to keep wires off the ground. (trip hazard) At the end of the cord from the reel is a female connector that had a tiny circuit board built into it that verifies correct wiring all the way back to the breaker. When all is correct the internal LED glows blue. If anything is incorrect, the LED turns red. I can't remember the name of the manufacturer right now, (I'm home now) but will post the name when I return to work tomorrow. The light also assures the driver of the truck that the cord is live.

Plugged into the illuminated cord connector is a Hubble 20 amp 120 volt plug, with 10 gauge wire and a matching 20 amp 120 volt Hubble connector that plugs into the truck. This wire is too short to reach the ground if left plugged into the truck alone. this is the jumper link I was referring to.

The truck is equipped with an automatic disconnect 120 volt 20 amp plug recessed into the side of the truck right next to the driver's door. This device is manufactured by a company called Auto Eject. Very common in the emergency vehicle field. The Auto Eject has a strong spring pushing against a plastic pin that hits the female connector when connecting the cord. As you push in the cord end into the truck's Auto Eject plug the plastic pin is pushed into the back of the Auto Eject until it latches. At that point the spring pressure is stored and the 120 volt cord is electrically connected to the truck.

When the truck's starter is energized, the same signal is sent to the solenoid mounted inside the Auto Eject. The solenoid pulls back the latch holding the compressed spring, allowing the spring pressure to push out the 120 volt cord, and connector.

If everything went correct, the truck drives away with the overhead cord line hanging next to the truck.

But if the cord is too long, and lays on the ground, the back tires on this 45,000, 69,000 or 90,000 pound truck drives over the cord connector.

Or if the Auto Eject fails to push out the connector, the truck will pull the short cord away from the long cord attached overhead reel, and hang harmlessly from the side of the truck as it drives away. The Hubble connectors that I have been using will deform if driven over a few times. There are armored connectors sold. I tried them once. when driven over, the metal edge crushed into the live wire and blew the circuit breaker. That was the end of the trial.

Hope I have made the mud a little clearer. Fear not about upsetting me . I have a great respect for the advances that have been made in the electrical codes, and NEMA. As for the Hospital grade, I was just trying to find a better plug than the current Hubble ones.

__________________
Bob
Register to Reply
Guru

Join Date: Mar 2008
Location: Atlanta, Georgia
Posts: 749
Good Answers: 13
#59
In reply to #58

Re: 110 Outlet with Green Circle & Red Triangle on The Bottom

08/19/2008 11:26 PM

Thanks. That's interesting. Never knew there were plug ejecting male sockets. Why don't you shorten that cord even more so it can't get run over?

I never dreamed a fire truck had more than a big pump, tank, and a bunch of hose.

j.

Register to Reply
Guru
Hobbies - RC Aircraft - New Member Hobbies - Automotive Performance - New Member Hobbies - DIY Welding - New Member

Join Date: Jul 2007
Location: Fort Lauderdale Florida
Posts: 5708
Good Answers: 123
#62
In reply to #59

Re: 110 Outlet with Green Circle & Red Triangle on The Bottom

08/20/2008 11:45 AM

Why don't you shorten that cord even more so it can't get run over?

Because the parking spot of the trucks may move, the cord is on a reel. Because some people think they are doing good They leave 2-3 feet of slack in the cord. That allows it to get run over.

The illuminated safety connectors are made by Ericson part # 1612-CMGL 20 A. Pass and Seymour also makes a similar one #1PGK-4. Never tried it yet, but it looks good.

__________________
Bob
Register to Reply
Power-User

Join Date: Mar 2006
Location: Valdosta, GA
Posts: 361
Good Answers: 8
#65
In reply to #62

Re: 110 Outlet with Green Circle & Red Triangle on The Bottom

08/21/2008 11:43 AM

What comes to mind is spring loading the reel so that it takes up the slack automatically. A bit off topic but hey, it came to mind.

__________________
Always use protection.
Register to Reply Off Topic (Score 5)
Commentator

Join Date: Jun 2008
Location: Brick, NJ
Posts: 71
Good Answers: 8
#66
In reply to #65

Re: 110 Outlet with Green Circle & Red Triangle on The Bottom

08/21/2008 12:30 PM

It may already be spring loaded. We had a similar application for a spring loaded reel to wire a prox on a freight elevator. These reels allow you to pay them out slowly and then they will stay at that length. You then give it a quick pull and then they retract. Like a vacuum cleaner cord. What we did was open up the reel and remove the mechanism that holds the reel from retracting and this kept a constant tension on the reel. You could do this on the truck reels as well. A lot of reels come with an adjustable rubber ball that keeps the cord from retracting too far. Adjust this ball to allow the proper amount of cord payed out so that it stays off the floor, but will always automatically retract.

__________________
Do this. Don't do that. Can't you redesign?
Register to Reply Off Topic (Score 5)
Guru
Hobbies - RC Aircraft - New Member Hobbies - Automotive Performance - New Member Hobbies - DIY Welding - New Member

Join Date: Jul 2007
Location: Fort Lauderdale Florida
Posts: 5708
Good Answers: 123
#67
In reply to #66

Re: 110 Outlet with Green Circle & Red Triangle on The Bottom

08/21/2008 3:00 PM

All of the reels were installed on the roof in the wrong direction except one. That means that only one reel has the cable guide that is used to catch the ball. The one that has the stop has a ball and it works well. The other reels are as you described, latch wise. When the reels were allowed to retract the end was 20 feet off the ground. We had to on loop some wire so we would not have to fish the end with stacked broom handles. Any other ideas please?

__________________
Bob
Register to Reply Off Topic (Score 5)
Guru
United States - US - Statue of Liberty - New Member Hobbies - Fishing - New Member

Join Date: Nov 2007
Location: Gone to Alabama with my banjo on my knee...
Posts: 5595
Good Answers: 20
#68
In reply to #67

Re: 110 Outlet with Green Circle & Red Triangle on The Bottom

08/21/2008 4:22 PM

Is it too late to reinstall the ones that were put up backwards?

__________________
Veni, vidi, video - I came, I saw, I got it on film.
Register to Reply Off Topic (Score 5)
Guru
Hobbies - RC Aircraft - New Member Hobbies - Automotive Performance - New Member Hobbies - DIY Welding - New Member

Join Date: Jul 2007
Location: Fort Lauderdale Florida
Posts: 5708
Good Answers: 123
#69
In reply to #68

Re: 110 Outlet with Green Circle & Red Triangle on The Bottom

08/21/2008 7:46 PM

The mounting brackets and guide arm are one piece. The reels were designed to be mounted to a wall. The rocket scientists that installed them mounted them to the braces that support the long runs of electric conduit. The roof is about 20 feet from the ground, and would require moving the reels another three feet to the roof and rewiring to reach the electrical junction boxes that would be three feet away now.

A lot of work for the building maintenance crew for a small amount of gain. I just replace the plug whenever it gets out of round, and will not spring out of the plug in receptacle. I would not would not put it that high on my "to do list".

Thank you for your concern though.

__________________
Bob
Register to Reply Off Topic (Score 5)
Guru
United States - US - Statue of Liberty - New Member Hobbies - Fishing - New Member

Join Date: Nov 2007
Location: Gone to Alabama with my banjo on my knee...
Posts: 5595
Good Answers: 20
#70
In reply to #69

Re: 110 Outlet with Green Circle & Red Triangle on The Bottom

08/22/2008 6:18 AM

"...The rocket scientists that installed them..."

See, that's your problem - you should've had electricians (reel ones...) install them!

__________________
Veni, vidi, video - I came, I saw, I got it on film.
Register to Reply Off Topic (Score 5)
Guru
Hobbies - RC Aircraft - New Member Hobbies - Automotive Performance - New Member Hobbies - DIY Welding - New Member

Join Date: Jul 2007
Location: Fort Lauderdale Florida
Posts: 5708
Good Answers: 123
#71
In reply to #70

Re: 110 Outlet with Green Circle & Red Triangle on The Bottom

08/22/2008 7:17 AM

As in "Even electrician can do"

__________________
Bob
Register to Reply Off Topic (Score 5)
Guru
United States - US - Statue of Liberty - New Member Hobbies - Fishing - New Member

Join Date: Nov 2007
Location: Gone to Alabama with my banjo on my knee...
Posts: 5595
Good Answers: 20
#30
In reply to #24

Re: 110 Outlet with Green Circle & Red Triangle on The Bottom

08/18/2008 9:30 AM

WHAT?!? A cancellation? Who'd back out on something like that? Might as well give up one's place in line for an audience with the Pope!

__________________
Veni, vidi, video - I came, I saw, I got it on film.
Register to Reply Off Topic (Score 5)
Guru

Join Date: Jul 2008
Location: SoCal USA
Posts: 556
Good Answers: 23
#25
In reply to #19

Re: 110 Outlet with Green Circle & Red Triangle on The Bottom

08/17/2008 9:27 PM

Slight correction. Plugs that are backed up by the emergency generator are red.

Hospital grade plugs and receptacles are white or clear (for easy inspection), and marked with a green dot.

Hospital grade or not, the workmanship of the original installers apparently is not.

__________________
I do not 'know it all', but i will admit that I would like to. CJM
Register to Reply
Anonymous Poster
#27
In reply to #25

Re: 110 Outlet with Green Circle & Red Triangle on The Bottom

08/18/2008 12:31 AM

Mia Culpa CJ.

You are right. The green dot is hospital grade.

j.

Register to Reply
Power-User
United Kingdom - Member - New Member Engineering Fields - Transportation Engineering - New Member Technical Fields - Marketing/Advertising - New Member Hobbies - Target Shooting - New Member

Join Date: Sep 2007
Location: South coast of England
Posts: 411
Good Answers: 36
#51
In reply to #19

Re: 110 Outlet with Green Circle & Red Triangle on The Bottom

08/19/2008 5:01 AM

Did you live in England a long time ago? the system you describe is long obsolete. All domestic and light commercial installations now use the same socket size for all loads up to 13A. The actual supply may be rated up to 32A feeding many sockets in parallel. A fuse is fitted in each plug to protect the appliance and its cable. Different fuse ratings are used for different loads.

Register to Reply
Guru

Join Date: Mar 2008
Location: Atlanta, Georgia
Posts: 749
Good Answers: 13
#55
In reply to #51

Re: 110 Outlet with Green Circle & Red Triangle on The Bottom

08/19/2008 7:12 PM

Thank you Chankley.

Yes, it was long ago.

Now, I will bet, instead of carrying around in one's pocket a handfull of plugs, folks carry around a handful of fuses.

j.

Register to Reply
Power-User
United Kingdom - Member - New Member Engineering Fields - Transportation Engineering - New Member Technical Fields - Marketing/Advertising - New Member Hobbies - Target Shooting - New Member

Join Date: Sep 2007
Location: South coast of England
Posts: 411
Good Answers: 36
#61
In reply to #55

Re: 110 Outlet with Green Circle & Red Triangle on The Bottom

08/20/2008 4:58 AM

All new equipment has to be supplied with a plug fitted (usually moulded) which should already have the correct fuse. Unfortunately the average user just sticks in a 13A fuse for everything. I used to have boxes full of 13A fuses that had been removed in order to fit the correct value.

Register to Reply
Anonymous Poster
#29

Re: 110 Outlet with Green Circle & Red Triangle on The Bottom

08/18/2008 6:10 AM

Probably want you to eat some baloney.

I don't know but my sense would be that it's green-go and yellow-caution, as relates to the two sides of each receptable. Perhaps pertaining to plug polarization; and/or to wiring color coding inside? The key would be to understand the circle and triangle significance, if any. It definitely looks like a 110, though.

Register to Reply
Commentator

Join Date: Jun 2008
Posts: 80
Good Answers: 5
#36

Re: 110 Outlet with Green Circle & Red Triangle on The Bottom

08/18/2008 11:47 AM

1) The green dot is hospital grade

2) The orange triangle is isolated ground. I think that is the extra ground that comes out of the box and is connected to the bare ground wire at the corner of the room.

With the set up you have there is NO WAY you should have anything other than 120 (nominal) Volts AC. Tell that idiot who told you there are different voltages to get a brain before he kills someone. A 240 VAC plug will not fit into the receptacle shown in the picture.

Register to Reply
Guru

Join Date: Mar 2008
Location: Atlanta, Georgia
Posts: 749
Good Answers: 13
#37
In reply to #36

Re: 110 Outlet with Green Circle & Red Triangle on The Bottom

08/18/2008 12:01 PM

Goodho,

I would be cautious about that. Those receptacles will accept a "T" type flat blade plug instead of the parallel flat blade Edison plug. I have seen 220 volt equipment with the "T" plug so obviously, on occasion, somebody wires those receptacles for 220.

j.

Register to Reply Off Topic (Score 5)
Commentator

Join Date: Jun 2008
Location: Brick, NJ
Posts: 71
Good Answers: 8
#42
In reply to #37

Re: 110 Outlet with Green Circle & Red Triangle on The Bottom

08/18/2008 2:55 PM

While it is true that 220 V equipment can have a T type blade on one side, the other side is horizontal on 220 V. That would be a NEMA 6-20R type 220 V 20 A plug. The one pictured is a NEMA 5-20R type which is 120 V 20 A.

__________________
Do this. Don't do that. Can't you redesign?
Register to Reply Off Topic (Score 5)
Power-User

Join Date: Mar 2006
Location: Valdosta, GA
Posts: 361
Good Answers: 8
#46
In reply to #36

Re: 110 Outlet with Green Circle & Red Triangle on The Bottom

08/18/2008 7:44 PM

We have 220 receptacles at Chick-Fil-A that are configured like the one in the picture. Don't tell anyone that it is not possible for the plug to be 220 volt. Are you trying to kill them? The only safe route is to check with a meter!

__________________
Always use protection.
Register to Reply
Active Contributor
Popular Science - Weaponology - New Member

Join Date: Jan 2008
Location: Lakewood, CO.
Posts: 19
#47
In reply to #46

Re: 110 Outlet with Green Circle & Red Triangle on The Bottom

08/18/2008 7:55 PM

It is an isolated ground 20 amp receptacle, that is hospital grade.

Register to Reply
Guru
Hobbies - RC Aircraft - New Member Hobbies - Automotive Performance - New Member Hobbies - DIY Welding - New Member

Join Date: Jul 2007
Location: Fort Lauderdale Florida
Posts: 5708
Good Answers: 123
#50
In reply to #46

Re: 110 Outlet with Green Circle & Red Triangle on The Bottom

08/19/2008 1:43 AM

As andrew ward said, the vertical and horizontal pins are reversed between 20amp 120 and 20 amp 240. It looks confusing, but NEMA has it worked out well and is fairly safe. Any one could use any outlet, and wire it to any voltage he wanted, that is why we always check.

Try this. If the power is off, (check to be sure) use an ohm meter to test between the ground pin receptacle and each of the other flat pin receptacles.If one of the readings is 0, or very close to 0, It must be 120 volts. Correct?

__________________
Bob
Register to Reply
Commentator

Join Date: Jun 2008
Posts: 80
Good Answers: 5
#53
In reply to #46

Re: 110 Outlet with Green Circle & Red Triangle on The Bottom

08/19/2008 6:12 PM

Let me restate my words "There is no way a NEMA compliant, correctly terminated, and properly applied 240VAC plug will fit into the receptacle shown in the picture." The receptacle shown is a duplex straight blade 125V, 20 Amp NEMA #5-20R that is both Hospital Grade and has provisions for an isolated ground. Unless modifications are performed, which will void the UL listing, the NEMA # 6-15P, 6-20P, or for that matter any of the NEMA #6 (250V or as some people call them 220V) plug designs will not fit into that receptacle. The ungrounded conductor blade for 120 V plugs would have to be rotated 90 degrees in order to fit. In response to a comment earlier, there are no correctly configured 240V receptacles like this. Not at chick-fil-a or anyplace else. This is like an ad for the NEC, and why I am happy to be a licensed electrician. I was a journeyman for many years then I took my Master's test and passed the first time. That is why the code is national, so I can go to florida, california, vermont, etc. and the rules stay pretty much the same. Each municipality can accept or amend the code when the new revision is issued.

My best advice is learn the electrical code. If you do not have a working knowledge of that book you might think you are an electrician, but you are not. You are just out there biting wire.

Register to Reply
Guru

Join Date: Mar 2008
Location: Atlanta, Georgia
Posts: 749
Good Answers: 13
#54
In reply to #53

Re: 110 Outlet with Green Circle & Red Triangle on The Bottom

08/19/2008 7:08 PM

Goodho,

I have no doubt you cite the good book correctly. Nonetheless there is still plenty of stuff circulating that does not heed the book.

I have seen, without a grounding pin, plugs that would fit the "T" formation of those outlets.

Are they legal? Probably not, but caution is good advice although in this particular instance I saw no need to think, and therefore would not have checked, that there was 220 present.

Perhaps I would have done otherwise if someone had told me it might be present.

j.

Register to Reply
Power-User
Hobbies - HAM Radio - New Member United States - Member - New Member Hobbies - Hunting - New Member

Join Date: Jun 2008
Posts: 440
Good Answers: 7
#56
In reply to #54

Re: 110 Outlet with Green Circle & Red Triangle on The Bottom

08/19/2008 8:05 PM

Things that are out of code are the exception, not the rule. Caution is a constant of course, whether driving on the freeway or manipulating conductors. Apply the code and change it where it isn't. Simple.

__________________
Those who believe in telekinetics, raise my hand --Kurt Vonnegut Jr.
Register to Reply
Guru

Join Date: Mar 2008
Location: Atlanta, Georgia
Posts: 749
Good Answers: 13
#57
In reply to #56

Re: 110 Outlet with Green Circle & Red Triangle on The Bottom

08/19/2008 9:05 PM

Simple only seems so.

I have had occasion to look in the attics of multi-family dwellings here in Atlanta that were built under license and allegedly inspected for adherence to code.

In those attics I often saw sheaves, ten or fifteen runs, of Romex running rafter to rafter just drooping between. They each are supposed to be supported and stapled in place at intervals.

Periodically, especially in summer where those attics must get very hot, 150 f. would not surprise me, there are fires in those buildings that start in the attics.

The code is a wonderful thing for safety.

Want to bet economics triumphs?

j.

Register to Reply
Power-User
Hobbies - HAM Radio - New Member United States - Member - New Member Hobbies - Hunting - New Member

Join Date: Jun 2008
Posts: 440
Good Answers: 7
#60
In reply to #57

Re: 110 Outlet with Green Circle & Red Triangle on The Bottom

08/20/2008 1:00 AM

I have seen thousands of bad examples--But we trudge on and diligently apply the code if we believe in what we do. Over time I think it will make a difference.

There was a thread about safety precautions and equipment that get bypassed while working on energized 480V systems. OLE, I started to answer like it was something to talk about--It's not. It got me thinking. Have a license, follow the code and practice it, period. I don't revere the bad examples as bullets we are skilled enough to dodge without getting bit. They are just bad.

Set good examples and don't qualify junk as electrical work. If I crawled into an attic that was going to possibly burst into flames do to high temperatures and wiring practices that are substandard--What should I do? I would buy a smoke detector for them at the very least(I know I just blew this way out of proportion, but it is just making a point).

__________________
Those who believe in telekinetics, raise my hand --Kurt Vonnegut Jr.
Register to Reply
Power-User

Join Date: Mar 2006
Location: Valdosta, GA
Posts: 361
Good Answers: 8
#72
In reply to #46

Re: 110 Outlet with Green Circle & Red Triangle on The Bottom

08/23/2008 5:24 PM

I stand corrected. I took another look at the plug at Chick-Fil-A I made referrence to. It is indeed configured with the "T" on the right side not the left as pictured above. Even though it is less likely to be "@240 volt" in the picture now than before in my mind, I stand by my position that it is better to test than assume. You know what "assume" sometimes does don't you?

__________________
Always use protection.
Register to Reply
Guru
Hobbies - Musician - Tube Amps Only Please!

Join Date: Apr 2009
Location: Los Angeles, California USA
Posts: 553
Good Answers: 1
#73

Re: 110 Outlet with Green Circle & Red Triangle on The Bottom

11/06/2009 10:27 PM

Just use a multimeter and test it. 110v should be 120v.

__________________
Regards, Maveric Manic - 'Knowledge is Power and Wisdom is knowing how to use it'
Register to Reply