Calculating Earth Strip Size

08/16/2008 5:39 PM

1.how to calculate earth strip size to be used for grid earthing,because we are using 50x8 GI strip for earthing

2.how to calculate copper cable size used for connecting 500 kv transformer neutral to NGR

Register to Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Guru
Popular Science - Weaponology - bwire Hobbies - Car Customizing - New Member

Join Date: Dec 2007
Location: Upper Mid-west USA
Posts: 7498
Good Answers: 97
#1

Re: CALCULATION FOR EARTH STRIP SIZE

08/16/2008 7:20 PM

Your state or country authority is the source for this info.

__________________
If death came with a warning there would be a whole lot less of it.
Register to Reply Score 1 for Good Answer
Guru
New Zealand - Member - Interested in everything- see my Profile please APIX Pilot Plant Design Project - Member - Member Engineering Fields - Electrical Engineering - Member Engineering Fields - Power Engineering - Member Engineering Fields - Civil Engineering - Member Hobbies - Musician - Autoharp and Harmonica Hobbies - Hunting - Member Hobbies - Fishing - Member

Join Date: Nov 2007
Location: Christchurch, (The Garden City), South Island, New Zealand
Posts: 4395
Good Answers: 230
#2
In reply to #1

Re: CALCULATION FOR EARTH STRIP SIZE

08/16/2008 7:28 PM

Hello bwire

from me

There are far too many Topic Starters, who are trying to get their homework assignments done for them.

That is the best way not to learn.

Kind Regards....

__________________
"The number of inventions increases faster than the need for them at the time" - SparkY
Register to Reply Off Topic (Score 5)
Guru
Popular Science - Weaponology - bwire Hobbies - Car Customizing - New Member

Join Date: Dec 2007
Location: Upper Mid-west USA
Posts: 7498
Good Answers: 97
#3
In reply to #2

Re: CALCULATION FOR EARTH STRIP SIZE

08/16/2008 11:58 PM

Ubetcha!

__________________
If death came with a warning there would be a whole lot less of it.
Register to Reply Off Topic (Score 5)
Anonymous Poster
#4

Re: Calculating Earth Strip Size

08/18/2008 3:49 PM

Unless you are experienced in the field of grounding, which I believe you are not based on your questions, it is best left to someone who is.

Generally a soil conductivity test is performed first for the area intended to be used to place the ground mat. If the conductivity proves to be too low for the amount of available area for the mat, it may require amending the soil to increase its conductivity.

Once soil conductivity is determined, ground mat configuration can be calculated based on fault current available.

Register to Reply
Anonymous Poster
#5
In reply to #4

Re: Calculating Earth Strip Size

08/18/2008 9:22 PM

If you know the answer of the above question. Then give a correct answer with complete formula of earthing.beacuse soil resistivity is first thing and after soil resistivity what we do.

Register to Reply
Guru
Engineering Fields - Control Engineering - New Member China - Member - New Member

Join Date: Sep 2006
Location: CHINA
Posts: 2945
Good Answers: 14
#6
In reply to #5

Re: Calculating Earth Strip Size

08/18/2008 11:08 PM

you can measure this soil resistance with a high resistance meter. the way of the test can be found in the cr4. I remember I posted some of it.

Register to Reply
Associate

Join Date: Oct 2007
Posts: 48
Good Answers: 1
#7

Re: Calculating Earth Strip Size

08/24/2008 1:26 PM

Hello Raj : You can try to solve/calculate this by yourself using IEEE 80 ( substation grounding ) or I could try to help in some of the steps .

1st : what do you mean by 'earth strip size' ? do you mean area ( square meters ) of earth grid ?

2nd : what is 50 x 8 GI ? 3rd : is this a transformer substation ? and can you describe the single line diagram ?

Register to Reply
Anonymous Poster
#8
In reply to #7

Re: Calculating Earth Strip Size

11/20/2008 8:15 AM

If you use GI strips for earth grid then the Cross sectional area of the conductor A

A=I*sq root of time/K

k=80 FOR GI strips

I= The fault current

t= Duration of fault current

So if system fault level is 65 ka for 1 sec

Then cross sectional area will be 65000*1/80 =812 sq mm

So the cross sctional area of the earth strip will primarily depend on the system fault level whereas the soil resistivity decides the total length of the strips required,

Again when we get 812 sq mm strips from the formula we have to add suitable corrosion allowance to get the actual cross sectional area of the earth strip.Here soil resistivity is important as lower the resistivity more will be the corrosion allowance.

Register to Reply Score 1 for Good Answer
Associate

Join Date: Oct 2007
Posts: 48
Good Answers: 1
#9
In reply to #8

Re: Calculating Earth Strip Size

11/20/2008 3:31 PM

Hi Raj : Your calcs for size of "earthing conductor" is fine but it has nothing to do with sizing the "earth grid" and its conductors( all of which are presumably direct buried in good low resistivity soil).What you have calculated is okay for above-ground ( earth soil) conductors that are used to connect electrical equipment to earth. Also, you haved assumed all of the fault current, 65kA, to be flowing thru this earth conductor 'A'.

1st: this sounds like a 3 phase max fault current at some point? Since I don't have your single line diagram, I will try to guess one : you mention 500kV transformer : I'll assume 500kV primary delta/25kV secondary wye, resistance neutral ground(NGR)/200MVA/Z=12%. This gives a 3phase max fault, on secondary side of 38kA ! So, your transformer is somewhere in this category or magnitude.

2nd: Now this 38kA ( or your 65kA) is NOT the fault current that one uses for the earth grid sizing and its underground conductors! You have to use the available " earth fault current ( line-to-ground)" on the primary side, coming from the utility or power company towards your substation transformer! Usually, this would be around 3kA to 8kA ( much less).

3rd: Maybe you are the utility? Okay, in that case, you could use the fault current on the secondary side but it would not be the 3phase fault; it would be the line-to-ground fault current(which is the only current that could flow into your earth grid) and in your case the NGR is limiting it to some small value like 300A ? So, even if you are the utility, you would NOT size the earth grid based on the secondary side line-to-ground fault current( too small), but rather based on the primary side line-to-ground fault current. What is this current? You have to calculate it! It certainly will not be 65kA or 38kA but will be more like 3kA or 6kA ? ( you must find this out).

4th: Now, assuming that the earth fault current, on the primary side, that can possibly flow into the earth grid is, say, 5.8kA, you can proceed with the earth grid sizing based upon IEEE80 ! You need to know the resistivity of the soil. Let's assume that it is average of 200 ohm-meters.

5th: Next, typically, all underground conductors in North America are copper-stranded #4/0 awg ( 120 mm sq).

6th: Next, typically, all substation earth grids have a 150 mm thick top layer of crushed stone and/or concrete.

7th: Typically, our ( Canada) electrical safety code requires the following to be met :(for 0.5 sec fault) E(step) < 3105 volts; E(touch) < 885 volts; and GPR < 5000 volts.

8th: A typical earth grid will have a grid pattern of conductors, as well as some earth rods ( 19 mm dia copper-clad steel, 3 meters long, buried vertically).

9th: The most influential parameters in a low-resistance and safe ( to humans) grid are the resistivity and the area covered by the grid.

10th: Let's assume : fault duration = 0.5 sec; grid depth = 0.75 meters; grid conductor spacing = 2.4 meters ( both directions); Area of grid = 100m x 100m; # of ground rods = 60 .

11th: Based on IEEE80 equations : Rg( grid) = 0.645 ohms ; GPR = Ig x Rg = 5768 A x 0.645 ohms = 3722 volts ; Es = 3014 volts; and Et = 148 volts

These all meet the code safety requirements; I had to go thru several parametric iterations to get these optimum results.

Next time, with your permission, we'll look at the NGR conductor sizing.

Cheers, Ovide.

Register to Reply Score 1 for Good Answer
Anonymous Poster
#10
In reply to #8

Re: Calculating Earth Strip Size

12/30/2008 4:35 AM

may be thi method is applicable for electrical equipments if we are going to earth the process equipments like vessels , tank etc how the size of strip can be calculated?

please suggest.

Register to Reply Off Topic (Score 5)
Anonymous Poster
#11
In reply to #8

Re: Calculating Earth Strip Size

05/30/2009 2:34 AM

Dear sir thanx for your vital information will u plz confirm me what is the value of K for copper strip. thanx raja sen

Register to Reply
Anonymous Poster
#13
In reply to #11

Re: Calculating Earth Strip Size

01/24/2010 12:30 AM

material constant k for copper is 205 for current rating 1 sec..

and k for copper is 118 for current rating 3 sec..

these values are for bare conductors..

Regards..

Shridhar Patel

(India)

Register to Reply
Anonymous Poster
#14
In reply to #13

Re: Calculating Earth Strip Size

02/17/2010 12:46 AM

Really good info, can u plz provide the K value for Aluminum & Galvanized iron. Plz provide the info. Best Regards Mayank

Email Removed - CR4 Admin

Register to Reply
Anonymous Poster
#15
In reply to #14

Re: Calculating Earth Strip Size

07/23/2010 5:39 AM

k factor of aluminium is:

for 1 sec current ratinginA/mm2= 126

for 3 sec current ratinginA/mm2= 73

k factor for steel

for 1 sec current ratinginA/mm2= 80

for 3 sec current ratinginA/mm2= 46

Register to Reply
Anonymous Poster
#16
In reply to #8

Re: Calculating Earth Strip Size

12/08/2010 2:41 AM

thanks for your answers. please help how the no of electrodes and length of GI strip can be evaluated?

Register to Reply
Guru
United Kingdom - Member - Indeterminate Engineering Fields - Control Engineering - New Member

Join Date: Jan 2007
Location: In the bothy, 7 chains down the line from Dodman's Lane level crossing, in the nation formerly known as Great Britain. Kettle's on.
Posts: 32175
Good Answers: 839
#18
In reply to #16

Re: Calculating Earth Strip Size

07/08/2024 7:48 AM

Does it go BANG?

That would be one way to <...evaluate...> it.

__________________
"Did you get my e-mail?" - "The biggest problem in communication is the illusion that it has taken place" - George Bernard Shaw, 1856
Register to Reply
Anonymous Poster
#12

Re: Calculating Earth Strip Size

01/08/2010 10:27 AM

how to calculate copper or GI strip size for various loads.

Pl send details

Thanks & Regards,

Anurag

Email Removed. CR4 Admin

Register to Reply Off Topic (Score 5)
Guru
United Kingdom - Member - Indeterminate Engineering Fields - Control Engineering - New Member

Join Date: Jan 2007
Location: In the bothy, 7 chains down the line from Dodman's Lane level crossing, in the nation formerly known as Great Britain. Kettle's on.
Posts: 32175
Good Answers: 839
#17
In reply to #12

Re: Calculating Earth Strip Size

07/08/2024 7:46 AM

Declined.

Use the protocols in British Standard 7671 if the installation is in the UK.

__________________
"Did you get my e-mail?" - "The biggest problem in communication is the illusion that it has taken place" - George Bernard Shaw, 1856
Register to Reply
Register to Reply 18 comments

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Copy to Clipboard

Users who posted comments:

Anonymous Poster (9); bwire (2); cnpower (1); ovide brudo (2); PWSlack (2); Sparkstation (1)