Load Calculation

08/18/2008 2:15 AM

What is the formula to calculate laod between two phases while the system is three phase four wires. We can say a air-conditioner of 24000 BTUH is connected on 2 phases having phase to phase 220V but the system is 3phase 4 wires.

Register to Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Guru
Canada - Member - If there is a way to screw someting up, there is someone to do so! Safety - Hazmat - New Member

Join Date: Mar 2007
Location: Iqaluit, NU. Canada
Posts: 1854
Good Answers: 140
#1

Re: Load calculation

08/18/2008 7:53 AM

There is no calculation other then the standard one for a single phase load. If a load is across to phase conductors in a three phase 4 wire system, it is a "single phase" load and not a two phase load.

__________________
Joe Contractor to Electrical Inspector, "What do you mean you are going to make me follow the code?".
Register to Reply Score 1 for Good Answer
Guru
Engineering Fields - Control Engineering - New Member China - Member - New Member

Join Date: Sep 2006
Location: CHINA
Posts: 2945
Good Answers: 14
#2

Re: Load Calculation

08/19/2008 4:19 AM

Guess,

Before answer your question. you hve to know what is phase voltage and wht is line voltage!

if you airconditioner is rate of 220v, you will distroy it when you connect it to two phase! no matter what yours is 3ph 4 wires or 3ph 5 wires.

Register to Reply
Member

Join Date: Jul 2008
Location: Accra, Ghana
Posts: 5
#3

Re: Load Calculation

08/19/2008 10:02 AM

First you have to know the power rating of your country. Is it 115V or 220V? These are just examples of the various avaialble to diffierent countries. If it is 115 then connecting on the two phases would give you something in the range of 230V and connecting a phase and the neutral would give you a 115V.

If it is a 220V system then connecting a phase and a neutral would give you the required 220V but if you connect across two phases then the voltage would be 390V.

Mind you there are also different arrangement of the 3 phase. It can be WYE or DELTA arranged and this would also have some impact on the individual phases you connect to.

So you need to further get some details on the properties of the power supply from your service provider.

Register to Reply
Active Contributor

Join Date: Aug 2008
Posts: 19
#4
In reply to #3

Re: Load Calculation

08/19/2008 10:39 AM

The supply voltage here in Saudia are phase to phase 220V and phase to neutral 127V, as the airconditioners are mostly of 220V so here the airconditioners are being connected between two phases to get 220V.

Now My concern is that an airconditioner of 18000 BTUH while connecting on 220 V accros the two phases it is taking around 13 Amps, while 18000 BTUH is equal 5.25KW. where as by calculation of a single phase the ampare are quite different (high), that I want to know.

Register to Reply
Member

Join Date: Jul 2008
Location: Accra, Ghana
Posts: 5
#5
In reply to #4

Re: Load Calculation

08/19/2008 11:45 AM

Ok For both instances the current is defined as follows;

Ib = P(Watts)/V (where V =127V) for single phase and

Ib = P(Watts)/(SQRT{3}*V where V = 220V for the three phase.

You may go ahead then and consider using the power factors and efficiencies if they are available.

SQRT is the Square Root.

Register to Reply
Active Contributor

Join Date: Jun 2008
Location: New Jersey, USA
Posts: 22
#6
In reply to #5

Re: Load Calculation

08/19/2008 12:49 PM

Try this:

18,000 BTUH = 5.27KW

Line Current ==> 5.27kW/220V = 23.9A

Phase Current ==> 23.9A/1.73 = 13.9A

Register to Reply
Anonymous Poster
#7

Re: Load Calculation

08/19/2008 4:46 PM

TAKE CARE!!!!! commonly when it is 220v it is between phase and neutral wire:There are 380v between two phases!!!!!!!!!!!!

Register to Reply
Anonymous Poster
#8

Re: Load Calculation

08/20/2008 4:32 AM

USE 1.414 INSTEAD OF 1.732 TO CALCULATE THE LOAD

Register to Reply
Anonymous Poster
#9

Re: Load Calculation

08/20/2008 4:46 AM

SORRY USE 1.414 INSTED OF 1.732 AND CALCULATE THE PHASE CURRENT BY DEVIDING THE ANSWER BY 1.732.

Hope that will answer your query

Register to Reply
Guru

Join Date: Jul 2008
Location: Mallorca, Spain
Posts: 567
Good Answers: 15
#10

Re: Load Calculation

08/30/2008 8:36 AM

Hi Manzoor,

As north of 60 says you are just need single phase calculations for this airco, however look on the specification plate for the current draw of your unit. Does that agree with the calculated figure of 24A? I agree with the calculation that 18000btuh = 5.25kW thus you must draw 24Amps at 220V. If you draw less then you are not getting 18000 cooling. (or you are getting something for nothing!)

Is something wrong with the gassing of the unit for example?

regards

chas

__________________
En la casa del herrero, cuchillos de palo!
Register to Reply
Guru
United Kingdom - Member - Indeterminate Engineering Fields - Control Engineering - New Member

Join Date: Jan 2007
Location: In the bothy, 7 chains down the line from Dodman's Lane level crossing, in the nation formerly known as Great Britain. Kettle's on.
Posts: 32175
Good Answers: 839
#11

Re: Load Calculation

08/16/2023 5:22 AM

It should be possible to look this up in the Operation and Maintenance Manual that came with the equipment.

If not, then there should be a rating plate somewhere on the equipment.

If not, then the manufacturer's telephone number must be easily accessible.

John 11:35.

__________________
"Did you get my e-mail?" - "The biggest problem in communication is the illusion that it has taken place" - George Bernard Shaw, 1856
Register to Reply
Guru

Join Date: Oct 2012
Location: 100 miles North from the World Center
Posts: 879
Good Answers: 42
#12

Re: Load Calculation

08/25/2023 6:55 AM

If the air-conditioning is built for 3 phases of 220 V phase-to-phase and if the supply source is 3*220 V, then, for 18000 BTUH [5.274 kW] the current will be 5.274*1000/220/sqrt(3)=13.84 A per phase.

If the air-conditioning is built for single phase 220 V the current will be 5.274/220=23.97 A

In my opinion, a power factor of 0.85 usually can be employed so the actual current may be 23.97/0.85=28.2 A

__________________
Julius
Register to Reply
Register to Reply 12 comments

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!