Selecting a 220-kV Cable for Connection to Ground

08/18/2008 9:43 AM

220/33kV 140MVA YY Transformer starpoint is to be connected to ground. Can some one please suggest the size of neutral cable to be selected.

thanks

Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.
Guru
United Kingdom - Member - Indeterminate Engineering Fields - Control Engineering - New Member

Join Date: Jan 2007
Location: In the bothy, 7 chains down the line from Dodman's Lane level crossing, in the nation formerly known as Great Britain. Kettle's on.
Posts: 32175
Good Answers: 839
#1

Re: 220kV cable for connection of neutral

08/18/2008 9:50 AM

For an unbalanced load, the neutral conductor needs to be the same size as the phase conductors.

__________________
"Did you get my e-mail?" - "The biggest problem in communication is the illusion that it has taken place" - George Bernard Shaw, 1856
Reply
Anonymous Poster
#2
In reply to #1

Re: 220kV cable for connection of neutral

08/18/2008 9:58 AM

Thank you.

Further, the primary conductor selected is 1c 630 Sqmm Cu 220kV XLPE cables.

Do we necessarily maintain the same voltage level for neutral conductor?

That means, can we select same cable for connection with primary neutral also?

Reply
Guru
United Kingdom - Member - Indeterminate Engineering Fields - Control Engineering - New Member

Join Date: Jan 2007
Location: In the bothy, 7 chains down the line from Dodman's Lane level crossing, in the nation formerly known as Great Britain. Kettle's on.
Posts: 32175
Good Answers: 839
#3
In reply to #2

Re: 220kV cable for connection of neutral

08/18/2008 10:34 AM

These matters are best addressed by referring to the end Client's specifications.

__________________
"Did you get my e-mail?" - "The biggest problem in communication is the illusion that it has taken place" - George Bernard Shaw, 1856
Reply
Guru

Join Date: Dec 2005
Posts: 1602
Good Answers: 19
#4
In reply to #3

Re: 220kV cable for connection of neutral

08/18/2008 12:13 PM

AND local codes.

(Sorry, I thought this was 220V not 220 kV. Local Codes probably are silent. But check with local utility requirements or practice.)

__________________
Eventually, one needs to realize that it is far less important to be the smartest person in the room than it is to sit next to that person and make friends.
Reply
Participant

Join Date: Aug 2008
Posts: 1
#5

Re: Selecting a 220-kV Cable for Connection to Ground

08/18/2008 12:35 PM

generally we are using a copper strips to connect to the ground.an earthin plate is extended to the transformer neutral point.

Reply
Guru
New Zealand - Member - Interested in everything- see my Profile please APIX Pilot Plant Design Project - Member - Member Engineering Fields - Electrical Engineering - Member Engineering Fields - Power Engineering - Member Engineering Fields - Civil Engineering - Member Hobbies - Musician - Autoharp and Harmonica Hobbies - Hunting - Member Hobbies - Fishing - Member

Join Date: Nov 2007
Location: Christchurch, (The Garden City), South Island, New Zealand
Posts: 4395
Good Answers: 230
#6

Primary & Secondary windings not normally both star connected to ground

08/18/2008 7:27 PM

Hello "Guest".

It would be a very unusual installation where a 220kV/33kV transformer is required to have both windings running star connected to ground.

It is normal for the Primary winding: in this case the 220kV winding, to be Delta connected.

The reason for this is simple:

If both Primary and Secondary windings are Star connected, it becomes possible for Neutral ground faults on the Secondary, to interfere with protection and fault discrimination relays at the supplying end of the transmission line feeding the 220kV Primary winding.

That is the main reason for never connecting both Primary and Secondary in Star form.

By connecting both neutral points to ground, at the same location, gives problems, because of electrical non-isolation.

Can you please advise the Installation Location/Country where you have seen the YY with both neutrals earthed?

Reply here, with

Kind Regards....

__________________
"The number of inventions increases faster than the need for them at the time" - SparkY
Reply
Anonymous Poster
#8
In reply to #6

Re: Primary & Secondary windings not normally both star connected to ground

08/19/2008 2:27 AM

Hello

Thank you for your replies.

Meanwhile, I must correct, the vector group is YNynO(d), the primary neutral is solidly grounded, the secondry neutral is grounded through neutral reactor and the tertiary (stablising) winding is delta solidly grounded.

rgds

Reply
Guru
New Zealand - Member - Interested in everything- see my Profile please APIX Pilot Plant Design Project - Member - Member Engineering Fields - Electrical Engineering - Member Engineering Fields - Power Engineering - Member Engineering Fields - Civil Engineering - Member Hobbies - Musician - Autoharp and Harmonica Hobbies - Hunting - Member Hobbies - Fishing - Member

Join Date: Nov 2007
Location: Christchurch, (The Garden City), South Island, New Zealand
Posts: 4395
Good Answers: 230
#9
In reply to #8

Re: Primary & Secondary windings not normally both star connected to ground

08/19/2008 3:26 AM

Hello again "Guest",

That is a "horse of a very different colour".

Kind Regards....

__________________
"The number of inventions increases faster than the need for them at the time" - SparkY
Reply
Guru
Canada - Member - If there is a way to screw someting up, there is someone to do so! Safety - Hazmat - New Member

Join Date: Mar 2007
Location: Iqaluit, NU. Canada
Posts: 1854
Good Answers: 140
#7

Re: Selecting a 220-kV Cable for Connection to Ground

08/18/2008 10:19 PM

Actually Spark, a wyw/wye with grounded star points is becoming a preferred method of connecting transformers for many utilities across Canada and I'm sure the US as well.

Yes... its an autotransformer. Yes by the Canadian code it is illegal to use an autotransformer (other then in a reduced voltage starter) inside of a building as a power transformer, but the utilities love them.

They save money on conductor cost as they only have the one neutral and it does not effect their protection systems or coordination. Many utilities Have active conversion programs to change over their distributions.

Though... this is not being done, that I know of, on systems with the voltages mentioned in this thread.

__________________
Joe Contractor to Electrical Inspector, "What do you mean you are going to make me follow the code?".
Reply
Anonymous Poster
#10

Re: Selecting a 220-kV Cable for Connection to Ground

06/06/2010 6:30 AM

220/33 kv 140MVA YY Transformer starpoint is to be connected to ground throug Neutral Gorunding Reactor not by Cable

Reply Off Topic (Score 5)
Anonymous Poster
#11

Re: Selecting a 220-kV Cable for Connection to Ground

08/09/2010 8:50 PM

The conductor size shall be calculated based on Earth Fault current of the system.

First of all, Check the earth fault current(? KA) and calculate the grounding conductor size. IEEE80 shows the calculation method.

The "Neutral cable you said" is not neutral cable. It is grounding conductor that is connected to neutral terminal. The grounding points of the TR are 4 points, Primary, Secondary, tertiary and Transformer body and shall be connected to earthing(Grounding) system.

The conductor type will be Copper Tape or Inslated conductor.