Earthed Cables vs. Unearthed Cables

08/21/2008 2:49 AM

Dear All

pl provide the difference between earthed and unearthed cables...?

Regards

K.Maharaja

Register to Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.

Good Answers:

These comments received enough positive votes to make them "good answers".

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Guru
New Zealand - Member - Interested in everything- see my Profile please APIX Pilot Plant Design Project - Member - Member Engineering Fields - Electrical Engineering - Member Engineering Fields - Power Engineering - Member Engineering Fields - Civil Engineering - Member Hobbies - Musician - Autoharp and Harmonica Hobbies - Hunting - Member Hobbies - Fishing - Member

Join Date: Nov 2007
Location: Christchurch, (The Garden City), South Island, New Zealand
Posts: 4395
Good Answers: 230
#1

Re: what is the difference between earthed and unearthed cables?

08/21/2008 3:37 AM

Hello kmaharaja_86

I emailed you the information last week.

However, here it is, once more, just for you.

Earthed cables are earthed.

Unearthed Cables are not earthed.

Please save that very important data to your own computer, as in time you may forget, and then you can refer to your own repository of knowledge, in your computer, without having to ask the same question, once again.

Kind Regards....

__________________
"The number of inventions increases faster than the need for them at the time" - SparkY
Register to Reply Score 1 for Good Answer
Anonymous Poster
#7
In reply to #1

Re: what is the difference between earthed and unearthed cables?

09/02/2008 7:40 AM

Hello,

A cable is considered to be earthed if is armoured. The Cable will be having different cores, with a PVC Insulation and armour is Steel either circular shape or flat sahpe. The wires will be connected to the respective circuits. The armour will be earthed through the Gland and body earthing.

An unearthed cable is unarmoured in which there will be any earthing for the cables.

Regards,

N.Suresh

Register to Reply
Commentator
Engineering Fields - Power Engineering - Projects Engineer

Join Date: Aug 2008
Location: Tanzania- East Africa
Posts: 71
#2

Re: what is the difference between earthed and unearthed cables?

08/21/2008 9:38 AM

a single phase cable earthed will have 3 wires one for phase the other for neutral and the third one for earthing. un earthed will not have the third wire

A 3 phase cable earthed will have 4 or five wires . 3 for the phases one for the neutral and the fifth or the armouring for earth .

i would suggest you to dig out such basic information from a electrical text book.

__________________
A wise person will understand more from a Foolish question than what a Fool will understand from a Wise Answer
Register to Reply
2
Guru
Safety - ESD - New Member India - Member - New Member Engineering Fields - Energy Engineering - New Member

Join Date: May 2007
Location: Pune , India
Posts: 875
Good Answers: 42
#3

Re: what is the difference between earthed and unearthed cables?

08/21/2008 11:11 AM

Hi K. Maharaja,

In HT electrical distribution,the systm can be earthed or un earthed.

This same subject was discussed for a thread that came up in CR4 on 04/01/2008 . Please read my reply which is quoted below and please read all the other replies . It is always better to check the previous threads on the same subject before putting up a new thread.

"The selection of earthed/unearthed cable will depend on your system. If your distribution system is earthed then you have to use cable manufactured for earthed system. (which the manufacturer specifies). If the system is unearthed then you need to use cable manufactured for un earthed system.The unearthed system requires high insulation level"

"

For earthed and un earthed XLPE cables, the IS 7098 part2 1985 does not give any difference in specification. The insulation level for cable for unearthed system has to be more. In simple statement the manufacturers states that 11 KV earthed cable is suitable for use in 6.6 KV unearthed system.The process of manufacture of cable is same. The size of cable will depend on current rating and voltage level.

what IS specifies and I quote below:

" b) Voltage Grade (Uo/U)

1) Earthed System - 1.9/3.3 kV, 3.8/6.6 kV, 6.35/11 kV, 12.7/22 kV and 19/33 kV.

2) Unearthed System - 3.3/3.3 kV and 11/11 kV.

Note 1 - Cables of 6.35/11 kV grade (earthed system) are suitable for use on 6.6/6.6 kV (unearthed system) also "

Hope this will clear your doubts

Register to Reply Good Answer (Score 2)
Anonymous Poster
#8
In reply to #3

Re: what is the difference between earthed and unearthed cables?

10/29/2008 4:05 AM

Hi Maharaja,

The answers given relating to the use of cables for earthed or unearthed systems are very pertinent and good.

regds

Gnanasambandam

email ID ; vgs.nadi@gmail.com

Register to Reply
Anonymous Poster
#9
In reply to #3

Re: what is the difference between earthed and unearthed cables?

10/28/2009 12:52 AM

Very good answer.Hope your concept is very clear

Register to Reply
Guru
New Zealand - Member - Kiwi Popular Science - Weaponology - New Member Engineering Fields - Power Engineering - New Member Engineering Fields - Electrical Engineering - New Member

Join Date: Sep 2006
Location: Auckland, New Zealand
Posts: 8777
Good Answers: 376
#4

Re: Earthed Cables vs. Unearthed Cables

08/21/2008 3:40 PM

Since your question is rather vague, do you mean the difference between earth-screened cables and standard unearthed cables?

Earth-screened cables are like standard cables but incorporate a braided or stranded metallic screen (commonly copper) around it (very similar to a coaxial TV aerial cable). This screen is (generally) connected to ground as a protective measure to provide additional electrical and touch-safe protection to the cables.

Try a google search.

__________________
jack of all trades
Register to Reply
Power-User

Join Date: Apr 2007
Posts: 414
Good Answers: 19
#5

Re: Earthed Cables vs. Unearthed Cables

08/22/2008 1:16 AM

I think you mean, "screened cables". Each conductor inside a high-voltage screened cable has an earthed screen, usually metallized gauze or conductive polymer, surrounding the insulation. This equalizes electrical stress on the cable insulation.

The need to equalize electrical stresses inside the cable became apparent in the 1930's, when high-voltage distribution cables began to fail for no apparent reason. The cause of these failures was determined to be the concentration of electric stress that exceeded the dielectric strength of the insulation. Covering the insulation of each conductor in the cable with an earthed screen eliminated those localized electric stresses and solved that particular problem.

Register to Reply Score 1 for Good Answer
Participant

Join Date: Jul 2008
Posts: 4
#6
In reply to #5

Re: Earthed Cables vs. Unearthed Cables

08/22/2008 2:05 AM

Dear friend

Thank you.

Register to Reply Off Topic (Score 5)
Register to Reply 9 comments

Good Answers:

These comments received enough positive votes to make them "good answers".

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Copy to Clipboard

Users who posted comments:

Anonymous Poster (3); bubbapebi (1); jack of all trades (1); kmaharaja_86 (1); SAK (1); Sparkstation (1); V.I.Abraham (1)