We are installing a 1250 KVA diesel generator set. Is it possible that this genset would be water cooled by means of a cooling tower? My concern here is that we may have a start=up problem considering that the cooling tower will derive power also from this genset.
Australia - Member - New Member Hobbies - Target Shooting - New Member Popular Science - Weaponology - New Member
Re: Water Cooled Genset
08/22/2008 1:17 AM
Kumskip,
This a common practice.
The cooling system for this (towers and pumps) for this purpose are generally run by thermostat and don't start up until after the load has been picked up.
Just make sure that the pump and fan motors for this are included in you power requirements or you might get bitten as you approach Generator capacity.
Regards,
Sapper
It's all about the Boom! - MythBusters
Engineering Fields - Piping Design Engineering - New Member Technical Fields - Architecture - New Member
Re: Water Cooled Gen set
08/23/2008 12:10 AM
you can provide a timer activated switch form the gen set Breaker panel and connect your cooling water pumps and cooling tower to generator breakers panel and set the timer in such way that timer will activate the cooling water pumps and cooling towers with in 30 seconds of generator breakers are closed this was what i do whenever i opt for water cooled generator sets. it is working in all the installations i have installed the gen sets.
crm
Run silent run deep
08/23/2008 12:49 AM
CRM,
I have seen this done both ways and they work equally as well.
The delay allows the load to step in instead of one step.
Regards,
Sapper
08/23/2008 1:11 AM
Sapper
Thanks for the comment