Over drying plant and instrument air?

08/24/2008 10:59 PM

As a process engineer working with utilities, I am always looking in optimization.

The facility I work in utilizes 4 desiccant dryers with varying product air temp dew points ranging from -110 to -70 degrees F.

I would like to establish "common practice" for a maximum tolerable air temperature dew point so that regeneration cycles can be based on dryer performance and not necessarily time. Where I work, the lowest recordable ambient temperature was -8 degrees F.

Thank you much!

-David

Register to Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.
Guru
United Kingdom - Member - Indeterminate Engineering Fields - Control Engineering - New Member

Join Date: Jan 2007
Location: In the bothy, 7 chains down the line from Dodman's Lane level crossing, in the nation formerly known as Great Britain. Kettle's on.
Posts: 32175
Good Answers: 839
#1

Re: Over drying plant and instrument air?

08/26/2008 3:28 AM

A global photographic materials manufacturer operated at -40degC dewpoint at its UK factory.

__________________
"Did you get my e-mail?" - "The biggest problem in communication is the illusion that it has taken place" - George Bernard Shaw, 1856
Register to Reply
Guru

Join Date: Dec 2007
Posts: 588
Good Answers: 13
#2

Re: Over drying plant and instrument air?

08/27/2008 9:42 AM

ok, so go back and calculate the dew point of compressed air. If you dry your air to -10 dew point at the meter, you will make water in your headed as sone as the outside temp gets to 35 F and it'll freeze at 32 F. The hygrometers are not set to measure water content under pressure.

The estimated dew point temp you need is about -50F, so the added security of -100F is worth it. One frozen line would cost you your job, is it worth saving $1000/year versus shutting down a unit?

Register to Reply