Anonymous Poster

Reciprocating Compressor

08/28/2008 5:31 AM

We are running 4 cylinder two stage compressor ,and its FAD is 45 m3/min (Actual), and 69.4m3/min (reated) ,i.e its Volumeric efficiency is about 65 % .

How efficiency can be improved? On what factor we should give attention?

Reply
User-tagged by 1 user
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.

Good Answers:

These comments received enough positive votes to make them "good answers".

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Guru
United Kingdom - Member - Indeterminate Engineering Fields - Control Engineering - New Member

Join Date: Jan 2007
Location: In the bothy, 7 chains down the line from Dodman's Lane level crossing, in the nation formerly known as Great Britain. Kettle's on.
Posts: 32175
Good Answers: 839
#1

Re: RECIPROCATING COMPRESSOR

08/28/2008 5:45 AM

Reduce the downstream pipe system back-pressure.

__________________
"Did you get my e-mail?" - "The biggest problem in communication is the illusion that it has taken place" - George Bernard Shaw, 1856
Reply
Guru
New Zealand - Member - Interested in everything- see my Profile please APIX Pilot Plant Design Project - Member - Member Engineering Fields - Electrical Engineering - Member Engineering Fields - Power Engineering - Member Engineering Fields - Civil Engineering - Member Hobbies - Musician - Autoharp and Harmonica Hobbies - Hunting - Member Hobbies - Fishing - Member

Join Date: Nov 2007
Location: Christchurch, (The Garden City), South Island, New Zealand
Posts: 4395
Good Answers: 230
#2

Re: RECIPROCATING COMPRESSOR

08/28/2008 6:10 AM

Hello "Guest",

In addition to the remedy as suggested by PWSlack above, you could install an interstage cooler.

If you already have an interstage cooler installed, and it is natural air convection cooled, look at replacing it with a water-cooled interstage cooler.

I do note you do not give us the ambient air temperature, along with the temperature of the compressed air as it arrives at the receiver tank, plus the actual power requirement (Electrical) and volume of air compressed, the compressed air pressure reading, plus the altitude of the compressor location, all of which have a considerable bearing on your compressor and its efficiency.

Thus it is impossible to calculate properly the efficiency of your 2-stage compressor, at present, and any figures presented would therefore, just be guesses.

Kind Regards....

__________________
"The number of inventions increases faster than the need for them at the time" - SparkY
Reply
Anonymous Poster
#3

Re: RECIPROCATING COMPRESSOR

08/28/2008 6:20 AM

our compressor has both intercooler and after cooler (water Cooling)

i have conducted volumetric efficiency test by pump up capacity method ,which requries filling the reciever by compressed air and noting down the time requried to fill the reciever at rated pressure .

by using the formula efficiency has been calculated.

as per my knowledge efficiency can be improved by -

removing the fouling of intercooler.

if requried then changing the piston ring

controlling leakages.

apart from these i would like to know is there any other improvement method.

thanks.

Reply
Power-User

Join Date: Mar 2007
Location: Newburgh, IN
Posts: 283
Good Answers: 10
#4
In reply to #3

Re: RECIPROCATING COMPRESSOR

08/28/2008 9:37 AM

Cool the Intake air to 32 deg.f. and your efficiency would increase, plus you would get rid of a lot of water in the system.

However, it might be as expensive as adding another compressor setup.

__________________
Bud Trinkel
Reply
Anonymous Poster
#6
In reply to #3

Re: RECIPROCATING COMPRESSOR

08/28/2008 8:21 PM

Don't forgot your valves!!!!

Valve slip means reversed gas flow through the valves before they have had time to seat at the end of the piston stroke. Obviously, this volume loss can occur through both intake and discharge valves. Minimum slippage occurs in a responsive valve; one that has minimum inertia so that the moving element can easily be controlled by air flow. Slippage is usually much less through intake valves than through discharge valves. In the latter, differential pressure across the valve increases rapidly as the piston reaches dead center, so that if the valve does not respond instantaneously, high pressure gas naturally returns through the valve before it seats.


Also - Piston ring leakage!!!!!!!!!

Reply
2
Power-User
Engineering Fields - Mechanical Engineering - New Member Technical Fields - Technical Writing - New Member

Join Date: May 2007
Location: Parallel 45
Posts: 226
Good Answers: 21
#5

Re: Reciprocating Compressor

08/28/2008 9:51 AM

The volumetric efficiency depends on the clearance, the compressor ratio and the isentropic exponent K of the gas being compressed. As the clearance and compressor ratio increase the volumetric efficiency decreases.

Hope this help

__________________
Look over to the next challenge
Reply Good Answer (Score 2)
Power-User
Engineering Fields - Mechanical Engineering - New Member Technical Fields - Technical Writing - New Member

Join Date: May 2007
Location: Parallel 45
Posts: 226
Good Answers: 21
#7

Re: Reciprocating Compressor

08/29/2008 2:54 AM

In my last post I did not mention about compresion systems problems ( valves, piston rings, rider rings, packing, etc ). Assume this cheks are performed and we spoke in principle about volumetric efficiency improving.

__________________
Look over to the next challenge
Reply Score 1 for Good Answer
Guru

Join Date: Dec 2007
Posts: 588
Good Answers: 13
#8

Re: Reciprocating Compressor

08/31/2008 11:53 PM

why do you even care about volumetric efficency, its not a waste of energy (or so small it doesn't matter to engineers). Increasing VE will mean a higher throughput and higher energy.

The VE on a machine is a function of the cylinder clearance, the gas properties and ratios. You have very little if any controls over these variables. You CAN COMPENSATE for a low VE by increasing suction poress or decreasing temp. You can change vales on the suction stage that will lower pressure drop which is the same as increasing the suction pressure.

Reply
Reply to Forum Thread 8 comments

Good Answers:

These comments received enough positive votes to make them "good answers".

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Copy to Clipboard

Users who posted comments:

Anonymous Poster (2); BudT (1); PWSlack (1); Sparkstation (1); user-deleted-1104 (2); vicini (1)