STAR-DELTA

09/02/2008 5:13 AM

DEAR FRIENDS,

CONSIDER THE LOAD OF A SCIM IS LESS. WHICH CONNECTION CONSUME LESS POWER? STAR OR DELTA.

Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Guru
United Kingdom - Member - Indeterminate Engineering Fields - Control Engineering - New Member

Join Date: Jan 2007
Location: In the bothy, 7 chains down the line from Dodman's Lane level crossing, in the nation formerly known as Great Britain. Kettle's on.
Posts: 32175
Good Answers: 839
#1

Re: STAR-DELTA

09/02/2008 6:05 AM
__________________
"Did you get my e-mail?" - "The biggest problem in communication is the illusion that it has taken place" - George Bernard Shaw, 1856
Reply Score 1 for Good Answer
Guru

Join Date: Nov 2006
Posts: 729
Good Answers: 2
#2

Re: STAR-DELTA

09/02/2008 11:19 PM

Star

__________________
To avoid crticism do nothing,say nothing,be nothing
Reply
Guru
United States - Member - New Member Engineering Fields - Power Engineering - New Member

Join Date: Sep 2006
Location: California, USA, where the Godless live next door to God.
Posts: 4665
Good Answers: 804
#3
In reply to #2

Re: STAR-DELTA

09/03/2008 3:16 PM

What???

The answer is, it is a non-issue. The different windings are intended for different voltages (assuming IEC motors). For example, it is designed to provide 100kW at 400V when connected in Star, or 100kW at 230V when connected in Delta. If you have 230V and connect the motor in Star, it will consume 1/3 of the power, but it will deliver only 1/3 of its rated torque. Speed will remain the same because the number of poles has not changed, therefor the motor kW output capacity is reduced to33kW. If your load has not become 1/3 of what it was, you will stall the motor!

So is it going to save energy? Sure, in the same was as turning it off will, because essentially it will no longer function as a motor.

__________________
** All I every really wanted to be, was... A LUMBERJACK!.**
Reply
Power-User

Join Date: Sep 2008
Location: Jakarta, Indonesia
Posts: 104
#5
In reply to #3

Re: STAR-DELTA

09/08/2008 6:31 AM

absolutely agree.....

rated motor in nameplate is based on manufacture standart. commonly, there are 37 kw,45kw,60kw,75kw,90kw,100kw, 110kw,132kw.

first we must know how many Hydraulic Horse Power(HHP) of our load (our friend in mechanical department must be more expert than us). after that we convert to Brake Horse Power (BHP).after we found, for example 97KW.then we find available motor standart KW in market.then we choose 100 KW motor.

second, we must give power for that motor . we must give at least 100 KW from our LV MCC.

third, motor winding have impedance and current that flow in that impedance is constant.(see the picture below). the different is if we wire the motor with different connection (wye or delta). it will make current that flow from our MCC is different too. we need more bigger current from our LV MCC when motor is in delta connection than motor is in wye connection. that caused motor in wye connection less of power.so motor will stall.

Reply
Commentator

Join Date: Sep 2008
Location: India
Posts: 91
Good Answers: 6
#4

Re: STAR-DELTA

09/07/2008 7:33 PM

Hello guest,

Star connection will consume less power. The current in each winding will be 1/1.732 times in star as compared to delta. So if the required torque is less, running the motor in star will save energy.

Reply
Reply to Forum Thread 5 comments

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Copy to Clipboard

Users who posted comments:

elect-ok (1); JRaef (1); Lspraba (1); nesubra (1); PWSlack (1)

Previous in Forum: power rating ac motors 1phase vs 3phase   Next in Forum: how to control electric motor with control ammeter

Advertisement