Water Ingress Into Reinforced Concrete Structure

09/03/2008 3:43 AM

Dear CR4

The organization I work for conduct research in various harmful and highly dangerous bacteria and viruses. We have an "effluent plant" where these are collected and sterilized before disposal into the municipal storm water system. The facility is constructed more than 10m undergraound, surrounded by "evaporation" earth dams for collection of all water (including contaminants) that may be carried out on foot et cetera. During heavy rains, the plant was flooded, and while pumping out the water, it was noticed that the water level at one of the evaporation dams was correspondingly dropping (this happens to be the largest of the evaporation dams). Common sense dictates that the reinforced concrete wall might be leaking (with sealed scaffolding holes one culprit), but the volume of the water indicates something far more than this. We need some long term solution to this problem (the facility is over 30 years old, and shows no simptoms of movement or disturbance) as the viruses and bacteria are catastrophic should they escape through the storm water system before sterilization. Basically no one seem to know where this flooding came from. Any suggestions and solution to this problem?

Regards

Mag

Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.

Good Answers:

These comments received enough positive votes to make them "good answers".
3
Guru
New Zealand - Member - Interested in everything- see my Profile please APIX Pilot Plant Design Project - Member - Member Engineering Fields - Electrical Engineering - Member Engineering Fields - Power Engineering - Member Engineering Fields - Civil Engineering - Member Hobbies - Musician - Autoharp and Harmonica Hobbies - Hunting - Member Hobbies - Fishing - Member

Join Date: Nov 2007
Location: Christchurch, (The Garden City), South Island, New Zealand
Posts: 4395
Good Answers: 230
#1

Re: Water ingress into reinforced concrete structure

09/03/2008 5:07 AM

Hello "Guest".

It is well known that the safe lifespan for concrete in such a facility as you describe is 20 years or less.

This is because the very concrete itself absorbs viruses and bacteria, which lurk below the surface awaiting the time they can exit and re-commence their intended work.

Even flame-throwing of the concrete surface does not remove the viruses/bacteria which have thus penetrated into the concrete pores.

This is the main reason many operating hospitals have to abandon a reinforced concrete structure after around 20 years, build a new hospital building, and convert the old building to offices etc.

You have not advised your location or country.

If you are in UK: Urgently contact http://www.dh.gov.uk/en/ContactUs/ContactDetailsList/DH_072330

If you are in US: Urgently contact http://www.bt.cdc.gov/emcontact/

Whatever your location it is vital that no person enter the facility, unless the full installation has been inspected and cleared by the experts.

It may well be that the complete facility is sealed off and incinerated - that would be my advice.

Disregard any endeavour to locate water leaks, get out and ensure safety of all, including those in the surrounding area.

The experts you call in, will certainly Quarantine the facilities, and dependent on what was being worked on, may extend the quarantine area, in some cases for at least 100kM.

Kind Regards....

__________________
"The number of inventions increases faster than the need for them at the time" - SparkY
Reply Good Answer (Score 3)
Anonymous Poster
#7
In reply to #1

Re: Water ingress into reinforced concrete structure

09/05/2008 6:08 AM

Dear Sparkstation

Thanks for your feedback. All regulatory systems are in place, hence the need for some action. We are weighting various options at the moment. The viruses and bacteria are basically harmless to humans but can be catastrophic for the livestock industry (we are working with animal borne diseases), and the facility is a quarantine in itself. I started in this position on July 01, 2008, so I would say I am fairly new in this position.

Kind regards

Mag

Reply
Guru

Join Date: Nov 2007
Location: Sherwood Park, Alberta, Canada
Posts: 1212
Good Answers: 74
#2

Re: Water ingress into reinforced concrete structure

09/03/2008 1:01 PM

Dear Mag,

I completely agree with the advice given by Sparkstation. I urge you to act immediately. To do otherwise would be criminal negligence.

Best regards,

__________________
Bruce
Reply
Guru
United States - US - Statue of Liberty - New Member Hobbies - Fishing - New Member

Join Date: Nov 2007
Location: Gone to Alabama with my banjo on my knee...
Posts: 5595
Good Answers: 20
#3

Re: Water Ingress Into Reinforced Concrete Structure

09/04/2008 11:31 AM

Pores in the concrete, seeping expansion joints, stress cracks, all could be the source of the leakage. I concur the safety factor overrides all other considerations. I can't think that you'd be engaged in this kind of research without ongoing oversight by some regulatory agency or other. Make sure they are involved in finding the solution from the beginning - you do NOT want to be accused of a cover-up!

__________________
Veni, vidi, video - I came, I saw, I got it on film.
Reply
Guru
Hobbies - RC Aircraft - New Member Hobbies - Automotive Performance - New Member Hobbies - DIY Welding - New Member

Join Date: Jul 2007
Location: Fort Lauderdale Florida
Posts: 5708
Good Answers: 123
#4
In reply to #3

Re: Water Ingress Into Reinforced Concrete Structure

09/04/2008 11:36 AM

Do you think this post is for real? How would you be able to be in charge of maintenance of a facility like this and not know of safety regulations? How could a facility of this type not be under constant inspections by someone? And why "Guest"

__________________
Bob
Reply
Guru
United States - US - Statue of Liberty - New Member Hobbies - Fishing - New Member

Join Date: Nov 2007
Location: Gone to Alabama with my banjo on my knee...
Posts: 5595
Good Answers: 20
#5
In reply to #4

Re: Water Ingress Into Reinforced Concrete Structure

09/04/2008 12:35 PM

If the answer to your first question is "yes", then the obvious answer to the last one is "anonymity". The answer to the second one is "I have NO idea, unless it's the result of one of those bogus diplomas we discussed in an earlier thread". And the remaining answer is "not likely, unless the anti-science faction of the current administration abdicated all sense of propriety". If the answer to your first question is "no", then all bets are off on the rest. Except the third one, that's still possible...

__________________
Veni, vidi, video - I came, I saw, I got it on film.
Reply
Power-User
Australia - Member - New Member Engineering Fields - Mechanical Engineering - New Member Engineering Fields - Marine Engineering - New Member

Join Date: Sep 2006
Posts: 451
Good Answers: 16
#6
In reply to #5

Re: Water Ingress Into Reinforced Concrete Structure

09/05/2008 12:02 AM

If it is half as real/possible as it sounds we should be able to follow the next chapter in our news papers. Unless big brother decides it would be better for us not to know.

They wouldn't do that would they?

BAB

__________________
Make it so.
Reply
Guru
United States - US - Statue of Liberty - New Member Hobbies - Fishing - New Member

Join Date: Nov 2007
Location: Gone to Alabama with my banjo on my knee...
Posts: 5595
Good Answers: 20
#9
In reply to #6

Re: Water Ingress Into Reinforced Concrete Structure

09/05/2008 9:52 AM

"They wouldn't do that would they?"

Naaah...not the government...they're of the people, by the people, and for the people, right?

__________________
Veni, vidi, video - I came, I saw, I got it on film.
Reply Off Topic (Score 5)
Anonymous Poster
#8

Re: Water Ingress Into Reinforced Concrete Structure

09/05/2008 7:44 AM

Few days back in Bihar state in India there was serious situation of bursting of one of the big dam in northern part of Bihar where the river Kosi flows.It lead to diversion of the river water,many villages were flooded, millions lost their homes, property of millions of Dollars worth was lost, standing corps were damaged,many people lost their lives. Relief operation are going on but it brought misery to many poor people.

So this can happen anywhere if dams gets bursted due to corrosion of RCC in dam's structure.

Suresh Sharma.

Reply
Guru

Join Date: Dec 2006
Location: Germany 49° 26' N, 7° 46' O
Posts: 1950
Good Answers: 109
#10

Re: Water Ingress Into Reinforced Concrete Structure

09/05/2008 10:24 AM

Hi,

ultraviolet light (if intense) is eating away any organic life. So if contamination is on the surface, you may try this.

If to go deeper - this seems to be the biggest problem, then take hydrogen-peroxide.

(UV light is producing H202 from water).

If in direct contact a concentration of 3% is enough, but in your situation I would stay with commercial quality 35% - to be stabilised - ! This material can decompose by many catalysts and then boil, evaporate, detonate with organics etc.

So you really need a specialist who is familiar with this.

This has a big advantage: it will find the same leaks as the leaking water. This is not really expensive and easy to handle with minimum safety efforts.

Chlorine may do the same disinfection but much more difficult to apply!

If you have done the first disinfection and you are convinced that everything is safe then it is advisable to flush with a water-fluoresceine solution. (I suppose that the fluoresceine is not surviving in the peroxide - to be tested).

With this you can detect for many kilometers downstream where the contaminated solution is coming to the surface again!

If you get tiny amounts of the reddish powder on your skin and add some water or look at you eyes you will see green color for days!

If you take a spectrometer tuned to this green color you may see it 1000km downstream.

Subsequent additional action suggested at sites where the water shows up again!

RHABE

Reply
Guru

Join Date: Dec 2007
Location: California
Posts: 2363
Good Answers: 63
#13
In reply to #10

Re: Water Ingress Into Reinforced Concrete Structure

09/11/2008 12:56 PM

Umm reinforced concrete. Iron+ H2O2=corrosion, and concrete is permeable. So H2O2 would probably kill some of the biologicals residing in the pores, but it may well rapidly accelerate degradation of the structural integrity of the facility. also, you do not usually get much H2O2 production fro UV light tranmission into water, the reactive agent in water drived from the interaction with UV light is tyically OH radicals. Again chlorine is worse as concrete is more permeable to gases, chlorine attacks and degrades the cementtitious materials and the reinforcing steel.

It is likely the water issues is either from a crack/fissure in the concrete or some other opening, as concrete tends to be relatively low permeability in the range of 10-8 cm/s +/- an order of magnitude. Other openings might include drainage systems that are being infiltrated, as all drainage systems pipes tend to leak and infiltrate/exfiltrate subsurface waters. Are there any types of floor drains or such. also, any pipe structures penetrating concrete can pipe pipe water in along the void space between the concrete and the pipe, check the seals (if used) along all concrete pipe penetrations (or any system penetraions of the concrete for that matter). The water must infiltrate/exfiltrate the facility fairly rapidly if it is readily correlated to the surface water depths in a overlying basin. Obviously, as concrete is permeable to water, if you have sufficient head across the concrete, you will move sufficient water through to get moisture on the walls and drainage down to the floor where it collects, but this is a highly attenuated flow that tends to show response on the inside well after water pressures have developed on the outside.

Reply
Power-User

Join Date: Feb 2008
Location: Northeast Ohio, USA
Posts: 267
Good Answers: 9
#11

Re: Water Ingress Into Reinforced Concrete Structure

09/05/2008 10:55 AM

Thirty year old tanks may be hard to repair and/or water proof. However, there are systems taht are designed to completely coat the inside oif copncrete tanks with a material that dries to a plastic film coating that is impervious to attack by water and some more aggressive liquids. The problem as I see it with these coatings is that they require that you empty the tank and dry it before application. That could pose several problems, not the least of which may be compromising the structural integrity of the tank. At the depth you indicate and with the saturated soil around the tank, there is the distinct possibility that the walls may collapse when the tank is de-watered.

If the leaks are small, there is a foam agent that is sold in cartridges that are the same size as a standard caulking compound and may be dispensed with the same type of "gubns" that are used for caulking. This compound will expand when it comes in contact with water and we use it to seal cracks and holes in precast concrete tanks. Again, the tank must be de-watered at least to the level of the leak and the integrity of the concrete wall may be suspect.

I would suggest that you try a Google search for your needs and see what you get.

Good luck.

__________________
All that is necessary for the triumph of evil is for good men to do nothing. - Edmund Burke
Reply
Active Contributor

Join Date: May 2007
Location: Bangalore in india
Posts: 24
#12

Re: Water Ingress Into Reinforced Concrete Structure

09/08/2008 3:52 AM

if what i have understood is correct the structure is 30year old and water is seeping out then please check for the wall joint ie place where vertical wall and floor joins the other culprit can be weak wall when the internal pressure increased due to flood the wall might have given way for if this problem has started recently there is no scope for one to think of air pockets in wall or floor.

the remidy for this is chip the joint superficially apply cementetious waterproof compound mixed with cement in thin format and follow it with thick slurry and resurface the plaster after that if you dont get the vaccum sound then give tow coats of pu or polyurea coating.

eventually you get to hear vaccum sound then try to open that and replaster the surface as indicated about and then after giving one base coat of epoxy fix pre impregnated frg cloth 5 mesh size and top coat it with exposy this will reseumably be a permenant solution

raghunath

Reply
Active Contributor

Join Date: May 2007
Location: Bangalore in india
Posts: 24
#14

Re: Water Ingress Into Reinforced Concrete Structure

09/13/2008 6:42 AM

hi

There has been reference to microbes etc this can be cleared using phosporic acid and detergent combination and once that is done there is anti microbial plaster and also coating which can be used this is specifically designed to resist the ingress of microbes

i can help you procure these products in case you are intrested.

raghunath protectsystems

Reply
Guru
New Zealand - Member - Interested in everything- see my Profile please APIX Pilot Plant Design Project - Member - Member Engineering Fields - Electrical Engineering - Member Engineering Fields - Power Engineering - Member Engineering Fields - Civil Engineering - Member Hobbies - Musician - Autoharp and Harmonica Hobbies - Hunting - Member Hobbies - Fishing - Member

Join Date: Nov 2007
Location: Christchurch, (The Garden City), South Island, New Zealand
Posts: 4395
Good Answers: 230
#15
In reply to #14

Re: Water Ingress Into Reinforced Concrete Structure

09/14/2008 4:15 AM

Hello protectsystems2004

Phosphoric acid actually eats into concrete, so that is not a good idea.

The major problem at this installation appears to be both flooding plus extremely dangerous viruses & bacteria.

The viruses and bacteria will by now have permeated right into the concrete, and without destroying the concrete, they cannot be removed.

Please read my earlier post.

I would be very concerned if your above advice was taken.

Kind Regards....

__________________
"The number of inventions increases faster than the need for them at the time" - SparkY
Reply
Active Contributor

Join Date: May 2007
Location: Bangalore in india
Posts: 24
#16
In reply to #15

Re: Water Ingress Into Reinforced Concrete Structure

09/14/2008 11:49 PM

hi

i suggested to use it with detergent 15% of phosporic acid and 25% detergent combi on trial and error method will solve your problem also the permiation time for the combi gives you 2 min you can dilute the coat using water within 2 min so that it wont enter the surface deep down. try this product made by chemline from usa if u want i can outsource it for u r u can take it directly u can talk to one john hennigson if its k u can refer my name r u can talk directly

Reply
Guru

Join Date: Dec 2007
Location: California
Posts: 2363
Good Answers: 63
#18
In reply to #16

Re: Water Ingress Into Reinforced Concrete Structure

09/15/2008 5:17 PM

The phosphoric acid will react with the calcium and magnesium to form a strong crystalline structure that will accelerate re-ifection of the structure, as phosphate is a primary micronutrient for all life. Add a little nitrate and you would have a bloom on your hands. Additionally ther eis a disposal issue, since phosphates disposal is restricted.

Reply
Guru
New Zealand - Member - Interested in everything- see my Profile please APIX Pilot Plant Design Project - Member - Member Engineering Fields - Electrical Engineering - Member Engineering Fields - Power Engineering - Member Engineering Fields - Civil Engineering - Member Hobbies - Musician - Autoharp and Harmonica Hobbies - Hunting - Member Hobbies - Fishing - Member

Join Date: Nov 2007
Location: Christchurch, (The Garden City), South Island, New Zealand
Posts: 4395
Good Answers: 230
#17

Re: Water Ingress Into Reinforced Concrete Structure

09/15/2008 3:26 AM

Hello "Guest",

The whole topic as originally posted appears to be hypothetical, at least I hope it is.

The reason I state that, is that no installation of the type you describe would have been built in the manner you state.

Either that, or if there is a real installation as you have described, the reason for it being built 10 metres underground, and poorly designed, and even worse, poorly constructed, makes me think that the organisation you say you work for is in the business of germ warfare, and intends to use that against others.

If you are genuine, the installation is a real situation, and you can actually leave the installation, do so, and blow the whistle on the activity without delay.

Perhaps you are in the Military, or contracted to them, but if at all possible, advise others of the location, so proper remedial action may be taken.

Kind Regards....

__________________
"The number of inventions increases faster than the need for them at the time" - SparkY
Reply
Active Contributor

Join Date: Jul 2008
Posts: 20
#19

Re: Water Ingress Into Reinforced Concrete Structure

10/12/2008 7:56 AM

hello;are you saying you have holes to put up your scaffolding?which might be causing leaks?if you can't replace the wall its self,have you thought of cutting out the holes and pouring supports in place for the scaffolding,so this can be sealed-and left in place? plenty of rust proof material out there that will support this,hope this helps,is so please answer and let me know.

Reply
Reply to Forum Thread 19 comments

Good Answers:

These comments received enough positive votes to make them "good answers".
Copy to Clipboard

Users who posted comments:

Anonymous Poster (2); ba/ael (1); blackhorse (1); BlueAussieBoy (1); bob c (1); EnviroMan (3); protectsystems2004 (3); RCE (2); RHABE (1); Sparkstation (3); The Commoner (1)

Previous in Forum: fixing structural glazers   Next in Forum: leve or dam

Advertisement